Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY
This section describes how to read and validate a 2 channel digital input.
This example uses the following libraries: SafeConversion library
SafeDataValidation library
|
S_ADCToVoltageOrCurrent, S_VoltageToDI and S_DebounceDI POUs are included in the code template generated by MultiTool Creator.
|
The following image is an architecture example for a 2 channel DI validation.
SafeConversion library version 1.1.0.0 or newer.SafeConversion library version 1.1.0.0 or newer.
SafeConversion library version 1.0.1.2SafeConversion library version 1.0.1.2.
When the following example is used with non-safety I/O, the I/O variables are generated in Inputs program instead of S_Inputs. |
The following example shows the validation of 2 safety related DIs done by Switch1 and Switch2 DI inputs defined in MultiTool Creator.
Safe PRG:
|
|
Init method:
|
IF NOT initDone THEN ValidateSwitchDI.Init( S_i_InvertedCh2:=TRUE , S_i_DiagnosticDelay:=30 , S_i_SafeOutputState:=FALSE , i_pEventCode:=ADR(S_Inputs.o_EventCode_Switch1) , i_pEventCodeCh2:=ADR(S_Inputs.o_EventCode_Switch2) );
initDone:=TRUE; END_IF
|
S_ValidateDI (FB)
S_VoltageToDI (FB)