S_ADCToVoltageOrCurrent (FB)

Description

This function block is used to convert control unit AD converter value to current (µA) or voltage (mV). The function block can be used when analog sensors (0-5V, 0-10V or 0-22mA) are connected to control unit’s AI pin. Cat. 2 type AI pin is also supported.

 

Initialization

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

A parameter error is diagnosed if:

  • Init method is not called before the main FB call OR

  • i_pEventCode = 0 OR

  • S_i_OutputMaximum <= 0 OR

  • S_i_OutputHighLimit  > S_i_OutputMaximum OR

  • S_i_OutputLowLimit >= S_i_OutputHighLimit  OR

  • S_i_OutputLowLimit < 0

 

S_i_Cat2MonitoringCh is set to TRUE only to current input pin's redundant-channel.

 

Initialization parameters

Parameter

Type

Unit

Range

Description

S_i_OutputMaximum

ENUM

mV /µA

EPEC_HW. VALUE_AT_ AD_MAXIMUM

mV/µA value at AD maximum

S_i_OutputHighLimit

SAFEDINT

mV / µA

>0

Limit value for status o_Status.OutputTooHigh

S_i_OutputLowLimit

SAFEDINT

mV /µA

>=0

Limit value for status o_Status.OutputTooLow  

S_i_DiagnosticDelay

SAFEUINT

ms

-

Delay time for output high/low diagnostics

S_i_Cat2MonitoringCh

SAFEBOOL

-

-

Is this channel a CAT2 monitoring channel.

i_pEventCode

POINTER TO EventCode

-

≠0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

Operation

When i_Enable is TRUE, the function block converts the input ADC value (i_ADCValue) to voltage (mV) or current (µA) value.

The input pin type can be either voltage or current.

If Cat. 2 monitoring channel is not in use the equation 3 can be used to calculate output value.

 


 
                  

 

S_o_Output minimum is however limited to 0.

If Cat. 2 monitoring channel is in use then output current can be calculated with equation 4

 

 

, where G_CAT2_OUTPUT_MAX is theoretical maximum current.

 

If the calculated output value is lower than S_i_OutputLowLimit or higher than S_i_OutputHighLimit for longer () than given diagnostic delay time, the corresponding error output is set.

 

A parameter error is diagnosed if AD input value exceeds defined maximum value G_ADC_MAXIMUM_VALUE.

  The output S_o_Output is set to safe value (0) if any error occurs, also o_Status.OutputValid is set false and the corresponding event ID is set to EventCode.

Limitations

Cat. 2 monitoring channel can be used only with current input pin.

 

Inputs

Input variable name

Data type

Range

Description

i_Enable

BOOL

TRUE / FALSE

Enable calculation

i_ADCValue

DWORD

0 - G_ADC_MAXIMUM_VALUE

AD converter value to be scaled

Outputs

Output variable name

Data type

Unit

Range

Description

S_o_Output

SAFEDINT

mV / µA

-

Calculated voltage or current value

o_Status

Status

-

-

Status of output value. See Status structure.

 

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

S_o_Output value

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

i_Enable TRUE

AND

init parameter error AND

 i_pEventCode valid

0

FALSE

ParameterError

ADC_TO_VOLTAGE OR_CURRENT  

PARAMETER_ERROR

i_Enable TRUE

AND

init parameter error AND
i_pEventCode NULL

0

FALSE

ParameterError

-

-

i_Enable rises

AND

 init parameters ok AND

S_i_OutputLowLimit <= S_o_Output <= S_i_OutputHighLimit

calculated value

TRUE

-

NO_FUNC

NO_ERROR

i_Enable TRUE

AND

 parameters ok

AND

S_o_Output > S_i_OutputHighLimit

0

FALSE

OutputHigh

ADC_TO_VOLTAGE OR_CURRENT

OUTPUT_TOO_HIGH

i_Enable TRUE

AND

 parameters ok

AND

S_o_Output < S_i_OutputLowLimit

0

FALSE

OutputLow

ADC_TO_VOLTAGE OR_CURRENT

OUTPUT_TOO_LOW

 

Example code

MultiTool Creator generated code includes this function block, when the input is selected to use.

 

Location of the POU instance depends on the application: Non-safe inputs are handled in non-safe context, safe inputs are handled in safe context. The example code applies to both.

 

Definitions:

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

VAR_INPUT

    i_Enable:  BOOL := TRUE;

    i_AI_XM1_3:DWORD;                // Input AD value

END_VAR

VAR_OUTPUT

    S_o_AI_XM1_3: SAFEDINT;                         // Non-validated voltage value (mV)

    o_XM1_3_Status_ToVoltage: EPEC_SC.Status;       // Conversion status

    o_XM1_3_EventCode: EPEC_DITF.EventCode;         // Event code of the input

 

END_VAR

VAR

    S_1_03_ToVoltage: EPEC_SC.S_ADCToVoltageOrCurrent;

    init_ok: BOOL := FALSE;

END_VAR

 

 

 

Initialization:

 

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

o_XM1_3_EventCode.DeviceID := DeviceIDs.VoltageInput;                         

o_XM1_3_EventCode.ChannelID := ChannelIDs.Ch1;   

o_XM1_3_EventCode.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC; // No function has detected an error

o_XM1_3_EventCode.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;   // No error occurred by default

 

init_ok := S_1_03_ToVoltage.Init(

    S_i_OutputMaximum := EPEC_HW.VALUE_AT_AD_MAXIMUM.U_TYPE096_5V, // 5V input

    S_i_OutputHighLimit := EPEC_HW.Constants.G_AI_5V_HIGH_VOLTAGE, // High limit of voltage value

    S_i_OutputLowLimit := EPEC_HW.Constants.G_AI_LOW_VOLTAGE,      // Low limit of voltage value

    S_i_Cat2MonitoringCh:= FALSE,                                  // Input is not a CAT2 monitoring channel

    S_i_DiagnosticDelay := EPEC_HW.Constants.G_VOLTAGE_INPUT_DIAGNOSTIC_DELAY, // Delay for error diagnostic

    i_pEventCode := ADR(o_EC_XM1_3)                                // Event code pointer for FB

);

 

 

Code:

 

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

S_1_03_ToVoltage(

        i_Enable := i_Enable,

        i_ADCValue := i_AI_XM1_3,

        o_Status => o_XM1_3_Status_ToVoltage,

        S_o_Output => S_o_AI_XM1_3

);

 

 

See also