Supported platforms: CODESYS 3.5 SAFETY

 

S_OutputGroupControlAndDiagnostics (FB)

Description

This function block monitors supply voltage and diagnoses safety switch faults.

The function block uses internally S_ADCToVoltageOrCurrent to convert ADC values to voltage and validate voltage limits.

Voltage tolerance is validated by library's internal implementation.

 

Initialization

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

A parameter error is diagnosed if:

  • Init is not called before the main FB call OR

  • i_pEventCode = 0 OR

  • S_i_VoltageLowLimit >= S_i_VoltageHighLimit OR

  • S_i_VoltageLowLimit < 0 OR

  • S_i_VoltageHighLimit <= 0 OR

  • S_i_VoltageHighLimit > VALUE_AT_AD_MAXIMUM.U_SUPPLY OR

  • S_i_DiagnosticDelay > 100

 

Parameter

Data type

Unit

Range

Description

S_i_VoltageHighLimit

SAFEDINT

mV

> 0

Limit for overvoltage diagnosis.

S_i_VoltageLowLimit

SAFEDINT

mV

>= 0

Limit for undervoltage diagnosis.

S_i_DiagnosticDelay

SAFEUINT

ms

0 - 100

Delay time for diagnostics.

i_pEventCode

POINTER TO EventCode

-

≠ 0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

Operation

Input i_SupplyBeforeSafetySwitch (channel 1) and i_SupplyAfterSafetySwitch (channel 2) ADC values are converted to voltage values using hardware specific enumeration VALUE_AT_AD_MAXIMUM.U_SUPPLY as voltage value at AD maximum for both channels.

 

While i_SafetySwitch is FALSE and i_Enable is TRUE, channel 1 voltage is checked to be within allowed (given) limits and channel 2 voltage is checked to be less than hardware specific constant G_OUTPUT_SUPPLY_OFF_MAX_VOLT_AFTER_OVP. Voltage value of input i_SupplyAfterSafetySwitch is assigned to S_o_Voltage output.

 

While i_SafetySwitch is TRUE and i_Enable is TRUE, the input channel 1 and 2 voltages are monitored to be within allowed (given) limits and channel tolerance is monitored.

Tolerance monitoring checks that channel 2 voltage does not drop below channel 1 voltage by percentage defined in platform specific constant G_OUTPUT_SUPPLY_TOLERANCE.

The tolerance error is diagnosed after G_OUTPUT_SUPPLY_TOLERANCE_DIAG_DELAY.

 

If parameters and voltages are ok, o_SafetySwitch output follows the request of i_SafetySwitch input.

 

In case of parameter error, or if either of the voltages fail,

• The output o_SafetySwitch is set FALSE.

• Corresponding Error bit in o_Status structure is set TRUE

• Corresponding EventID is set to i_pEventCode

 

Inputs

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation

i_SafetySwitch

BOOL

-

-

Safety switch status request

i_SupplyBeforeSafetySwitch

DWORD

-

0 - G_ADC_MAXIMUM_VALUE

Measured channel 1 AD value

i_SupplyAfterSafetySwitch

DWORD

-

0 - G_ADC_MAXIMUM_VALUE

Measured channel 2 AD value

Outputs

Output variable name

Data type

Unit

Range

Description

o_SafetySwitch

BOOL

-

-

Safety switch output control status. This output is given as input for FW-provided function that controls diagnosed power group.

S_o_Voltage

SAFEDINT

mV

-

Validated output group control voltage.

o_Status

Status

-

-

Status of output value. See Status struct.

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

S_o_Voltage

o_SafetySwitch

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

i_Enable TRUE

AND

init parameter error AND

 i_pEventCode valid

0

FALSE

FALSE

ParameterError

GROUP_CONTROL

PARAMETER_ERROR

i_Enable TRUE

AND

init parameter error AND
i_pEventCode NULL

0

FALSE

FALSE

ParameterError

-

-

i_Enable TRUE AND

init parameters ok AND

( i_SupplyBeforeSafetySwitch > G_ADC_MAXIMUM_VALUE OR i_SupplyAfterSafetySwitch > G_ADC_MAXIMUM_VALUE )

0

FALSE

FALSE

ParameterError

GROUP_CONTROL

PARAMETER_ERROR

i_Enable rises AND

 init parameters ok AND

i_SafetySwitch TRUE AND

voltages ok AND

tolerance ok

Calculated voltage of channel 2

i_SafetySwitch

TRUE

-

NO_FUNC

NO_ERROR

i_Enable rises AND

 init parameters ok AND

i_SafetySwitch FALSE AND

channel 1 voltage ok AND

channel 2 voltage < G_OUTPUT_SUPPLY_ OFF_MAX_VOLT_AFTER_OVP

Calculated voltage of channel 2

i_SafetySwitch

FALSE

-

NO_FUNC

NO_ERROR

i_Enable TRUE AND

init parameters ok AND

i_SafetySwitch TRUE AND

voltages ok AND

tolerance fault

(channel 2 < channel 1 by more than G_OUTPUT_SUPPLY _TOLERANCE)

0

FALSE

FALSE

ValueMismatch

GROUP_CONTROL

DATA_MISMATCH

i_Enable TRUE AND

init parameters ok AND

channel 1 voltage < S_i_VoltageLowLimit)

0

FALSE

FALSE

OutputLow

GROUP_CONTROL

OUTPUT_TOO_LOW

i_Enable TRUE AND

init parameters ok AND

(channel 1 or 2 voltage > S_i_VoltageHighLimit)

0

FALSE

FALSE

OutputHigh

GROUP_CONTROL

OUTPUT_TOO_HIGH

i_Enable rises AND

init parameters ok AND

i_SafetySwitch FALSE AND channel 1 voltage ok AND

channel 2 voltage >= G_OUTPUT_SUPPLY_OFF _MAX_VOLT_AFTER_OVP

0

FALSE

FALSE

ExternalVoltage

GROUP_CONTROL

EXTERNAL_VOLTAGE

i_Enable rises AND

init parameters ok AND

i_SafetySwitch TRUE AND

channel 1 voltage ok AND

channel 2 voltage < S_i_VoltageLowLimit

0

FALSE

FALSE

SafetySwitch Error

GROUP_CONTROL

VOLTAGE_SHORTCUT

 

 

Example code

Function block is included in hardware specific diagnostic program.

It is automatically generated to code template when MultiTool Creator is used.

 

Output group control and diagnostic is a safe-context POU.

 

Definitions:

 

VAR_INPUT

(* Output Group Control Inputs *)

i_Enable: BOOL := FALSE;                      // Enable operation

i_OutputGroup1Control: BOOL := FALSE;         // Application status request for output group #1

i_SupplyBeforeSafetySwitch1:DWORD := DWORD#0; // Filtered ADC value for power supply before safety switch

i_SupplyAfterSafetySwitch1: DWORD := DWORD#0; // Filtered ADC value for power supply after safety switch

END_VAR

 

VAR_OUTPUT

(* Output Group Control Outputs *)

o_OutputGroup1ControlStatus: EPEC_SHWD.Status; // FB status

o_OutputGroup1Control_EC: EPEC_DITF.EventCode; // Event code

o_OutputGroup1Control: BOOL;                   // Group control status for controlling FB function

o_OutputGroup1ControlVoltage: SAFEDINT;        // Measured output group control voltage

END_VAR

 

VAR

init_ok: BOOL;                                                    // Initialization status

outputGroupControl: EPEC_SHWD.S_OutputGroupControlAndDiagnostics; // POU instance

 

END_VAR

 

 

 

Init:

 

(* Output group control and diagnostic *)

init_ok := outputGroupControl.Init(  

S_i_VoltageHighLimit := G_IO.OUTPUTGROUP1_HIGH_VOLTAGE_LIMIT, // Limit of overvoltage (mV)

S_i_VoltageLowLimit := G_IO.OUTPUTGROUP1_LOW_VOLTAGE_LIMIT,   // Limit of undervoltage (mV)

S_i_DiagnosticDelay := G_IO.OUTPUTGROUP1_DIAGNOSTIC_DELAY,    // Delay time (ms) for error diagnostic

i_pEventCode := ADR(o_OutputGroup1Control_EC)                 // Event code pointer for FB

);

 

 

Code:

 

(* Output group control and diagnostic *)

outputGroupControl(

i_Enable := i_Enable,                                      // Enable operation

i_SafetySwitch := i_OutputGroup1Control,                   // Control request status

i_SupplyBeforeSafetySwitch := i_SupplyBeforeSafetySwitch1, // Filtered ADC value before safety switch

i_SupplyAfterSafetySwitch := i_SupplyAfterSafetySwitch1    // Filtered ADC value after safety switch

S_o_Voltage => o_OutputGroup1ControlVoltage,               // Measured output group control voltage

o_SafetySwitch => o_OutputGroup1Control,                   // Output group control status for FW function

o_Status => o_OutputGroup1ControlStatus                    // FB status

);

 

 

 

See also

 

 

 

 

Source file topic100437.htm