Supported platforms: CODESYS 3.5 SAFETY
This function manipulates the state of a power switch.
The function provides the second control route for deactivating outputs in case of control unit internal failure.
All outputs are energized via power switches and the switch must be activated (closed) before outputs are controlled. |
The switch can only be activated if - control unit internal diagnostic has not noticed any internal errors, - all IO's are configured and the IO-driver is in RUN state, and - switch has not been deactivated. |
The switch can be activated only one time from application. If application deactivates the switch, it will remain deactivated until the next power-on reset and the error code (33528) is added to the firmware error log.
Note, the error code is not supported in firmware version 1.0.0.34 |
Outputs are de-energized when the switch state is changed to deactivated (open). |
Input variable name |
Data type |
Range |
Description |
i_powerSwitchNbr |
BYTE |
0..2 |
Power switch number: 0 = All, 1 = One, 2 = Two. |
i_state |
BYTE |
0..1 |
Switch control state: 0 = deactivated (open), 1 = activated (closed). |
Data type |
Description |
SYSTEM_ERROR_CODES |
Retuned error code. See details in Data Types page. |
Error code |
Description |
FW_ERR_SYSTEM_DIAGNOSTIC_NOT_OK |
Control unit internal diagnostic has noticed an error. |
FW_ERR_SYSTEM_IO_DRV_NOT_RUN_STATE |
I/O initialization has not been done. |
FW_ERR_SYSTEM_INVALID_SWITCH_NBR |
Given power switch number is out of range. |
FW_ERR_SYSTEM_INVALID_STATE |
Given state is out of range. |
-
-