Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY, CODESYS 3.5 SP19 SAFETY
This function block validates calibrated joystick control signal by direction switch statuses (negative direction, positive direction and middle position).
|
|
This function block validates only one axis of joystick. |
Init method is used to initialize the necessary static calculation parameters for the function block instance.
The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.
The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.
|
|
A parameter error is diagnosed if: • Init method is not called before the main FB call OR • i_pEventCode = 0 OR • S_i_MidPosDirSwitchesUse = TRUE AND middle position switch channel event code pointer = 0 OR • S_i_DirSwitchesInUse = TRUE AND either of direction switch channel event code pointer = 0
|
|
|
The safe output of the function block is 0, so no input parameter for safe value is specified. |
|
Parameter |
Data type |
Unit |
Range |
Description |
|
S_i_DiagnosticDelay |
SAFEUINT |
ms |
- |
Delay time for diagnostics. |
|
S_i_DirSwitchesInUse |
SAFEBOOL |
- |
- |
Direction switches are in use. |
|
S_i_MidPosSwitchInUse |
SAFEBOOL |
- |
- |
Middle position switch is in use. |
|
i_pEventCode |
POINTER TO EventCode |
- |
≠0 |
Pointer to application variable which is type EventCode. Used with POUs that use joystick control signal data. |
|
i_pEventCodePDS |
POINTER TO EventCode |
- |
≠0 |
Pointer to application variable which is type EventCode. Used with POUs that handle positive direction switch data. |
|
i_pEventCodeMPS |
POINTER TO EventCode |
- |
≠0 |
Pointer to application variable which is type EventCode. Used with POUs that handle middle position switch data. |
|
i_pEventCodeNDS |
POINTER TO EventCode |
- |
≠0 |
Pointer to application variable which is type EventCode. Used with POUs that handle negative direction switch data. |
|
TRUE: All initialization parameters ok. |
|
FALSE: Error in initialization parameter(s). |
The function block writes S_i_Control value to S_o_Control and sets o_Status.OutputValid state TRUE if
The control is enabled, i.e. i_Enable is TRUE AND
When S_i_Control < 0,
Negative direction switch status is expected to be TRUE AND
Middle position switch status is expected to be FALSE AND
Positive direction switch status is expected to be FALSE.
When S_i_Control = 0,
Negative direction switch status is expected to be FALSE AND
Middle position switch status is expected to be TRUE AND
Positive direction switch status is expected to be FALSE.
When S_i_Control > 0,
Negative direction switch status is expected to be FALSE AND
Middle position switch status is expected to be FALSE AND
Positive direction switch status is expected to be TRUE.
If control value mismatch switch statuses continuously over S_i_DiagnosticDelay time, then
S_o_Control is set to 0,
Status o_Status.OutputValid is set FALSE,
The corresponding Error bit in o_Status variable is set TRUE, and
The corresponding EventID is set to i_pEventCode
All function block statuses, including errors are reset on rising edge of i_Enable.
|
Input variable name |
Data type |
Range |
Description |
|
i_Enable |
BOOL |
- |
Enable POU operation |
|
S_i_Control |
SAFEINT |
- |
Input control value |
|
S_i_PosDirSwitch |
SAFEBOOL |
- |
Positive direction switch status |
|
S_i_MidPosSwitch |
SAFEBOOL |
- |
Middle position switch status |
|
S_i_NegDirSwitch |
SAFEBOOL |
- |
Negative direction switch status |
|
Output variable name |
Data type |
Range |
Description |
|
S_o_Control |
SAFEINT |
- |
Validated control value |
|
o_Status |
Status |
- |
Status of output value. See Status structure. |
See Diagnostic Interface library description of error status and event code functionality.
|
Conditions |
S_o_Control |
o_Status. OutputValid |
o_Status error status |
Event code FunctionID |
Event code EventID |
|
i_Enable TRUE AND init parameter error AND i_pEventCode valid |
0 |
FALSE |
ParameterError |
VALIDATE_DIRSW _JOYSTICK |
PARAMETER _ERROR |
|
i_Enable TRUE AND init parameter error AND |
0 |
FALSE |
ParameterError |
- |
- |
|
i_Enable = TRUE & init parameters Ok & S_i_Control = 0 & S_i_PosDirSwitch = FALSE & S_i_NegDirSwitch = FALSE & S_i_MidPosSwitch = TRUE & S_i_MidPosSwitchInUse = TRUE |
S_i_Control |
TRUE |
- |
NO_FUNC |
NO_ERROR |
|
i_Enable = TRUE & init parameters Ok & S_i_Control = 0 & S_i_PosDirSwitch = FALSE & S_i_NegDirSwitch = FALSE & S_i_MidPosSwitch = FALSE & S_i_MidPosSwitchInUse = FALSE |
S_i_Control |
TRUE |
- |
NO_FUNC |
NO_ERROR |
|
i_Enable = TRUE & init parameters Ok & S_i_Control > 0 & S_i_PosDirSwitch = TRUE & S_i_NegDirSwitch = FALSE & S_i_MidPosSwitch = FALSE & S_i_DirSwitchInUse = TRUE |
S_i_Control |
TRUE |
- |
NO_FUNC |
NO_ERROR |
|
i_Enable = TRUE & init parameters Ok & S_i_Control < 0 & S_i_PosDirSwitch = FALSE & S_i_NegDirSwitch = TRUE & S_i_MidPosSwitch = FALSE & S_i_DirSwitchInUse = TRUE |
S_i_Control |
TRUE |
- |
NO_FUNC |
NO_ERROR |
|
i_Enable = TRUE & init parameters Ok & S_i_Control <> 0 & S_i_PosDirSwitch = FALSE & S_i_NegDirSwitch = FALSE & S_i_MidPosSwitch = FALSE & S_i_DirSwitchInUse = FALSE |
S_i_Control |
TRUE |
- |
NO_FUNC |
NO_ERROR |
|
i_Enable = TRUE & init parameters Ok & S_i_Control = 0 & S_i_MidPosSwitch = FALSE & S_i_MidPosSwitchInUse = TRUE |
0 |
FALSE |
MidPos Switch Missing |
VALIDATE_DIRSW _JOYSTICK |
MIDPOS_SWITCH _STATUS_MISSING |
|
i_Enable = TRUE & init parameters Ok & S_i_Control <> 0 & S_i_MidPosSwitch = TRUE |
0 |
FALSE |
MidPos Switch On Fault |
VALIDATE_DIRSW _JOYSTICK |
MIDPOS_SWITCH _STATUS_ON_FAULT |
|
i_Enable = TRUE & init parameters Ok & S_i_Control > 0 & S_i_PosDirSwitch = FALSE & S_i_DirSwitchesInUse = TRUE |
0 |
FALSE |
Positive Dir Switch Missing |
VALIDATE_DIRSW _JOYSTICK |
POSDIR_SWITCH _STATUS_MISSING |
|
i_Enable = TRUE & init parameters Ok & S_i_Control <= 0 & S_i_PosDirSwitch = TRUE |
0 |
FALSE |
Positive Dir Switch On Fault |
VALIDATE_DIRSW _JOYSTICK |
POSDIR_SWITCH _STATUS_ON_FAULT |
|
i_Enable = TRUE & init parameters Ok & S_i_Control < 0 & S_i_NegDirSwitch = FALSE & S_i_ DirSwitchesInUse = TRUE |
0 |
FALSE |
Negative Dir Switch Missing |
VALIDATE_DIRSW _JOYSTICK |
NEGDIR_SWITCH _STATUS_MISSING |
|
i_Enable = TRUE & init parameters Ok & S_i_Control >= 0 & S_i_NegDirSwitch = TRUE |
0 |
FALSE |
Negative Dir Switch On Fault |
VALIDATE_DIRSW _JOYSTICK |
NEGDIR_SWITCH _STATUS_ON_FAULT |
|
Safe definitions: |
|
(* Voltage conversion FBs (generated by MT) left out of example *)
(* DI conversion FBs *) S_1_09_ToDI: EPEC_SC.S_VoltageToDI; // generated by MT S_1_10_ToDI: EPEC_SC.S_VoltageToDI; // generated by MT S_1_11_ToDI: EPEC_SC.S_VoltageToDI; // generated by MT
(* DI statuses from AI values, converted with S_VoltageToDI *) S_DI_1_09_State: SAFEBOOL := FALSE; // generated by MT S_DI_1_10_State: SAFEBOOL := FALSE; // generated by MT S_DI_1_11_State: SAFEBOOL := FALSE; // generated by MT
EC_DI1_09: EPEC_DITF.EventCode; // these event codes are generated by MT EC_DI1_10: EPEC_DITF.EventCode; // and used by conversions AND validation EC_DI1_11: EPEC_DITF.EventCode; //
// joystick and validation data is not generated by MT S_SteeringJoystick: EPEC_SJCD.S_Joystick; // joystick FB EC_SteeringJoystick: EPEC_DITF.EventCode; // event code of joystick S_JoystickControl: SAFEINT; // control signal to be validated
S_DirSwitchValidation: EPEC_SDV.S_ValidateJoystickWithDirSwitches; S_Joystick_DirSwitchDiagDelay: SAFEUINT:=UINT#100; JoystickValidationStatus: EPEC_SDV.Status; S_ValidJoystickControl: SAFEINT; // validated control signal
|
|
Init at safe PRG: |
|
EC_DI1_09.DeviceID := DeviceIDs.VoltageInput; EC_DI1_09.ChannelID := ChannelIDs.Ch2; EC_DI1_09.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC; EC_DI1_09.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;
EC_DI1_10.DeviceID := DeviceIDs.VoltageInput; EC_DI1_10.ChannelID := ChannelIDs.Ch3; EC_DI1_10.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC; EC_DI1_10.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;
EC_DI1_11.DeviceID := DeviceIDs.VoltageInput; EC_DI1_11.ChannelID := ChannelIDs.Ch4; EC_DI1_11.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC; EC_DI1_11.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;
EC_SteeringJoystick.DeviceID := DeviceIDs.SteeringJoystick; EC_SteeringJoystick.ChannelID := ChannelIDs.Ch1; EC_SteeringJoystick.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC; EC_SteeringJoystick.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;
S_DirSwitchValidation.Init( S_i_DirSwitchesInUse := TRUE, S_i_MidPosSwitchInUse := TRUE, S_i_DiagnosticDelay := Joystick_DirSwitchDiagDelay, i_pEventCode := ADR(EC_SteeringJoystick), i_pEventCodePDS := ADR(EC_DI1_09), i_pEventCodeMPS := ADR(EC_DI1_10), i_pEventCodeNDS := ADR(EC_DI1_11) );
|
|
Code at safe PRG: |
|
S_DirSwitchValidation( i_Enable := S_SteeringJoystick.o_Status.OutputValid AND S_1_09_ToDI.o_Status.OutputValid AND S_1_10_ToDI.o_Status.OutputValid AND S_1_11_ToDI.o_Status.OutputValid, S_i_Control := S_JoystickControl, S_i_PosDirSwitch := S_DI_1_09_State, S_i_MidPosSwitch := S_DI_1_10_State, S_i_NegDirSwitch := S_DI_1_11_State, S_o_Control => S_ValidJoystickControl, o_Status => JoystickValidationStatus );
|