Supported platforms: CODESYS 2.3, CODESYS 3.5, CODESYS 3.5 SAFETY

 

Going Online and Downloading Application

CODESYS 2.3

Using Ethernet

1. Find out the IP address of the unit1. Find out the IP address of the unit

To log in to a control unit, the IP address is needed. By default, the IP address is set as follows

    • 5050 : 192.168.0.2

    • 2040 : 192.168.0.2

 

The IP address of

    • Epec 2040 can be checked from the ApplicationLoader. For more information, refer to ApplicationLoader manual.

    • 5050 units can be checked with CANmoon:

      • open CANmoon

      • click Scan icon

 

 

      • double-click the found node from CAN bus section to see the IP address (in this example, 192.168.0.2)

 

 

2. Ethernet settings for PC2. Ethernet settings for PC

 

Screen captures in this chapter are taken using USB-Ethernet adapter. Same settings can usually be done for laptop's physical Ethernet.

 

 

2.1 Go to Network and Sharing Center and select Change adapter settings.

 

 

2.2 Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

 

 

2.3 Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

2.4 Select Internet Protocol Version 4 (TCP/IPv4) and Properties.

 

Define a static IP address for the adapter (Use the following IP address). The first three bytes (192.168.0.xxx) should be the same with Epec unit.

 

 

3. Define the communication parameters to CODESYS 3. Define the communication parameters to CODESYS

Define the communication parameters to CODESYS 2.3 (Online > Communication parameters).

 

Setting 5050 unit communication parameters

 

Double-clicking the Value column opens it to editing state. Write the unit IP address to the Address row.

Motorola byteorder is set to Yes for 5050 unit.

Using CAN

1. Find out the node-ID of the unit1. Find out the node-ID of the unit

To log in to a control unit, CODESYS node-ID is needed. The unit may have several node-IDs, but specifically the CODESYS node-ID of the unit is needed. By default, the CODESYS node-ID is set as follows

    • 202x/203x units: 127

    • 3xxx/4xxx series units : 126

    • 5050: 127

 

To check the CODESYS node-ID of the unit

    • open CANmoon

    • select Scan

 

 

    • select the found node from CAN bus section to see the CODESYS node-ID (in this example 126)

 

2. Define the communication parameters to CODESYS2. Define the communication parameters to CODESYS

Define the communication parameters in CODESYS (Online > Communication parameters).

 

Setting 3/4xxx unit communication parameters

 

Setting 5050 unit communication parameters

 

Double-clicking the Value column opens it to editing state. Write the unit CODESYS node-ID to the NodeID row and set the CAN bus baudrate to the correct one (default in all Epec units is 250).

 

Motorola byteorder selection depends on the unit type:

    • 202x/203x No

    • 3/4xxx No

    • 5050 Yes

 

The CAN card driver name depends on the CAN adapter that you use. For the supported adapters, the driver name is as follows:

CAN card

CAN card driver

Vector

vectorcan_ch1 (*)

Kvaser

kvasercan

Peak

peakcan

IXXAT

ixxatvci

Systec

usbcan

* If using a Vector adapter with several channels, the driver name may also be vectorcan_ch2, vectorcan_ch3 or vectorcan_ch4

 

CODESYS 3.5

Using Ethernet

1. Find out the IP address of the unit1. Find out the IP address of the unit

To log in to a control unit, the IP address is needed. By default, the IP address for Epec units is 192.168.0.2

 

The default IP address of the 6500 unit is 192.168.0.2. If the IP address is not known, reinstall CODESYS runtime to reset the IP address to the default value.

  1.  

The IP address of

    • Epec display products can be checked from the ApplicationLoader (if available).

    • Epec products with a PLCopen application can be checked with CANmoon:

      • open CANmoon

      • Click Scan icon

 

 

      • double-click the found node from CAN bus section to see the IP address (in this example, 192.168.0.2)

 

 

2. Ethernet settings for PC2. Ethernet settings for PC

 

Screen captures in this chapter are taken using USB-Ethernet adapter. Same settings can usually be done for laptop's physical Ethernet.

 

 

2.1 Go to Network and Sharing Center and select Change adapter settings.

 

 

2.2 Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

 

 

2.3 Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

2.4 Select Internet Protocol Version 4 (TCP/IPv4) and Properties.

 

Define a static IP address for the adapter (Use the following IP address). The first three bytes (192.168.0.xxx) should be the same with Epec unit.

 

 

3. Connect to the unit3. Connect to the unit

1. Open CODESYS 3.5 project for an Epec unit

2. Double-click Device to open Communication Settings dialog and select Scan network...

 

 

 

3. Select the unit and click OK.

 

 

4. Select Online > Login from the menu bar and the application is downloaded. Click Debug > Start (F5) to run the program.

 

For more information, see CODESYS help (section Quickstart).

 

Using CAN

1. Define settings for CODESYS Gateway1. Define settings for CODESYS Gateway

1.  Go to Start menu and select Epec > CAN gateway for C3.5 units which is a program that defines the communication parameters to CODESYS gateway.

 

        

 

2. Define the server settings for the gateway:

 

    • Set the wanted Port value

    • Bit rate = the control unit's bit rate

    • Target node-ID = control unit's CODESYS node-ID

      • CODESYS Scan finds other node-IDs too, but communication is more reliable using right node-ID

    • Gateway node-ID = set node-ID that is not used by the target or any other devices connected to the bus (range 1-127)

    • Select the used CAN adapter from the drop-down list. Only adapters connected to the PC are shown on the list.

    • Select the correct CAN adapter channel from the drop-down list.

 

 

3. The gateway for CAN is now defined. Then click Start button.

 

    

 

2. Define the communication parameters to CODESYS2. Define the communication parameters to CODESYS

6. Open CODESYS 3.5

 

7. Double-click the device to open Communication Settings tab. Select Gateway > Add new gateway:

 

 

8. Define the gateway settings. The Port must be the same as given earlier in CAN gateway for C3.5 units program (step 3).

 

   

 

9. In Communication Settings tab, select the added gateway from the drop-down menu. The gateway indicator lamp turns green to indicate a successful connection:

 

    

 

10. To ensure correct connection, click Scan network in Communication Settings tab.

Select the wanted device and check that the serial number (included to the device name) is corresponding with the control unit (found in the product label).

 

 

 

11. S Series only:  the user name and password must be given in a popup before login is possible.

The user name is User and default password is last 4 digits of the control unit serial number.

See also, Known issues.

 

 

12. S Series only: CODESYS debug mode needs to be activated before new application download is possible using CODESYS IDE.

Select SIL2 > Enter debug mode.... from the menu bar. This requires SIL2 extension to be installed (see also, Safety project prerequisites).

 

Note, this is not required when going online with an up-to-date application.

 

13. To download the application, select Online > Login from the menu bar. To run the program, click Debug > Start (F5)

 

 

 

 

 

Using USB-Ethernet adapter (6505)
 

Connect the USB end of the USB-Ethernet adapter to the USB port of the 6505 unit and then connect the ethernet cord into the ethernet port of the USB-Ethernet adapter.

Find the IP address of the unit.
 

The default IP address of the 6505 unit is 192.168.0.2. If the IP address is not known, reinstall CODESYS runtime to reset the IP address to the default value.

 

Ethernet settings for PCEthernet settings for PC

 

Screen captures in this chapter are taken using USB-Ethernet adapter. Same settings can usually be done for laptop's physical Ethernet.

 

 

Go to Network and Sharing Center and select Change adapter settings.

 

 

Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

 

 

Right-click the USB-Ethernet adapter (or physical Ethernet) and select Properties.

 

 Select Internet Protocol Version 4 (TCP/IPv4) and Properties.

 

Define a static IP address for the adapter (Use the following IP address). The first three bytes (192.168.0.xxx) should be the same with Epec unit.

 

 

 

Connect to the unitConnect to the unit

1. Open CODESYS 3.5 project for an Epec unit

2. Double-click Device to open Communication Settings dialog and select Scan network...

 

 

 

3. Select the unit and click OK.

 

 

4. Select Online > Login from the menu bar and the application is downloaded. Click Debug > Start (F5) to run the program.

 

For more information, see CODESYS help (section Quickstart).

 

 

 

 