Supported platforms: CODESYS 3.5

 

VoltageValveController (FB)

Description

This FB handles Danfoss PVG32 voltage controlled proportional valve.

The FB includes end attenuation and ramp.

A startup error is diagnosed if control is requested on the rising edge of i_Enable.

The output control signal is set to zero if i_Enable is FALSE, parameter error is diagnosed or startup error is diagnosed.  

 

All internal FB initializations are done on the rising edge of i_Enable.

All errors are reset on the rising edge of i_Enable.

 

Limitations

 

The FB uses internally SafeProportionalValveControl librarys FBs:

S_EndAttenuation

S_PVGValveController

 

Following parameters are taken into use at the rising edge of i_Enable:

- i_PosDirMaxPWMLevel

- i_PosDirMinPWMLevel

- i_CenterPositionPWMLevel

- i_NegDirMinPWMLevel

- i_NegDirMaxPWMLevel

- i_PosDirAttenuationLimit

- i_NegDirAttenuationLimit

- i_PosDirAscendRampTime

- i_PosDirDescendRampTime

- i_NegDirAscendRampTime

- i_NegDirDescendRampTime

- i_PVGPullUpResistor

- i_PVGPullDownResistor

- i_PinPullUpResistor

- i_PinPullDownResistor

- i_DiagnosticDelay

+ Any initialized event code.

 

Inputs

Input variable name

Data type

Range

Description

i_Enable

BOOL

FALSE/TRUE

Enables controlling of the PWM outputs

i_Control

INT

0..10000

Control signal from e.g. joystick.

i_PVGError

BOOL

FALSE/TRUE

Error signal from PVG valve.

i_PosDirAttenuationOn

BOOL

FALSE/TRUE

Positive direction end attenuation sensor activity status.

i_NegDirAttenuationOn

BOOL

FALSE/TRUE

Negative direction end attenuation sensor activity status.

i_PosDirMaxPWMLevel

UINT

0..1000‰

Output voltage(PWM) level corresponding the value *i_Control* = 10000. Permil from unit's supply voltage.

i_PosDirMinPWMLevel

UINT

0..1000‰

Output voltage(PWM) level corresponding the value *i_Control* = 1. Permil from unit's supply voltage.

i_CenterPositionPWMLevel

UINT

0..1000‰

Output voltage(PWM) level corresponding the value *i_Control* = 0. Permil from unit's supply voltage.

i_NegDirMinPWMLevel

UINT

0..1000‰

Output voltage(PWM) level corresponding the value *i_Control* = -1. Permil from unit's supply voltage.

i_NegDirMaxPWMLevel

UINT

0..1000‰

Output voltage(PWM) level corresponding the value *i_Control* = -10000. Permil from unit's supply voltage.

i_PosDirAttenuationLimit

UINT

0..100%

Positive direction attenuation limit.

Percentage from maximum control value 10000.

i_NegDirAttenuationLimit

UINT

0..100%

Negative direction attenuation limit.

Percentage from maximum control value

-10000.

i_PosDirAscendRampTime

UINT

-

Time (ms) of o_PosDirPWMRatio signal to change from center to positive max

(0->10000).

i_PosDirDescendRampTime

UINT

-

Time (ms) of o_PosDirPWMRatio signal to change from positive max to center

(10000->0).

i_NegDirAscendRampTime

UINT

-

Time (ms) of o_NegDirPWMRatio signal to change from center to negative min

(0->-10000).

i_NegDirDescendRampTime

UINT

-

Time (ms) of o_NegDirPWMRatio signal to change from negative min to center

(-10000->0).

i_PVGPullUpResistor

UDINT

-

PVG valve pull up resistor (Ohm).

i_PVGPullDownResistor

UDINT

-

PVG valve pull down resistor (Ohm).

i_PinPullUpResistor

UDINT

-

Control unit PWM pin pull up resistor (Ohm).

i_PinPullDownResistor

UDINT

-

Control unit PWM pin pull down resistor (Ohm).

i_DiagnosticDelay

UINT

-

Diagnostic delay (ms) for PVG valve error signal.

Outputs

Output variable name

Data type

Range

Description

o_ValveSupply

BOOL

FALSE/TRUE

Control PVG valve supply.

o_PWMRatio

DWORD

HW specific

Output value to PWM pin.

o_InputHigh

BOOL

FALSE/TRUE

i_Control too high.

o_InputLow

BOOL

FALSE/TRUE

i_Control too low.

o_StartupError

BOOL

FALSE/TRUE

Control request on already when i_Enable rises.

o_PVGError

BOOL

FALSE/TRUE

Valve error output status.

o_ParameterError

BOOL

FALSE/TRUE

Incorrect parameter value in any of the monitored parameters.

 

 

EventCodeInit (Public Method)

This optional method sets pointers for event codes.

 

Inputs

Input variable name

Data type

Description

i_Enable

BOOL

Enable operation.

i_pEventCode

POINTER TO EPEC_DITF.EventCode

Pointer to signal event code value provided by the application.

i_pEventCodePosDir

POINTER TO EPEC_DITF.EventCode

Pointer to signal event code value provided by the application.

i_pEventCodeNegDir

POINTER TO EPEC_DITF.EventCode

Pointer to signal event code value provided by the application.

 

 

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

FunctionID and EventID are only set if EventCode is used.

 

A parameter error is diagnosed if:

  • i_PosDirAttenuationLimit out of range OR

  • i_NegDirAttenuationLimit out of range OR

  • S_i_PosDirMaxPWMLevel out of range OR

  • S_i_PosDirMinPWMLevel out of range OR

  • S_i_CenterPositionPWMLevel out of range OR

  • S_i_NegDirMinPWMLevel out of range OR

  • S_i_NegDirMaxPWMLevel out of range OR

  • i_OverCurrentLimit out of range OR

  • i_WireBrokenLimit >= i_OverCurrentLimit OR

 

 

Conditions

o_PWMRatio

Output error set TRUE

Event code FunctionID

Event code EventID

i_Enable TRUE AND

parameter error AND

 i_pEventCode valid

0

o_ParameterError

depends on the parameter

PARAMETER_ERROR

i_Enable TRUE AND

parameter error AND
i_pEventCode NULL

0

o_ParameterError

-

-

i_Enable rises AND

parameters ok AND

i_Control <> 0

0

o_StartupError

PVG_CONTROLLER

STARTUP_ERROR

i_Enable TRUE AND

 init parameters ok AND

i_Control within range

PWM ratio

-

NO_FUNC

NO_ERROR

i_Enable TRUE AND

 init parameters ok AND

i_Control > 10000  

0

o_InputHigh

END_ATTENUATION

INPUT_TOO_HIGH

i_Enable TRUE AND

 parameters ok AND

i_Control <  -10000  

0

o_InputLow

END_ATTENUATION

 INPUT_TOO_LOW

i_Enable TRUE AND

 init parameters ok AND

i_Control within range AND

i_PVGError TRUE

0

o_PVGError

PVG_CONTROLLER

PVG_VALVE_ERROR

 

Example code

 

 

 

 

See also

 

 

 

 