Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY, CODESYS 3.5 SP19 SAFETY
This function block controls Danfoss PVG32 voltage controlled proportional valves.
Init method is used to initialize the necessary static calculation parameters for the function block instance.
The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.
The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.
|
A parameter error is diagnosed if:
|
Parameter |
Type |
Unit |
Range |
Description |
S_i_PosDirMaxPWMLevel |
SAFEUINT |
‰ |
0 - 1000 |
Defines PWM ratio when S_i_Control = 10000 |
S_i_PosDirMinPWMLevel |
SAFEUINT |
‰ |
0 - S_i_PosDirMaxPWMLevel |
Defines PWM ratio when S_i_Control = 1 |
S_i_CenterPositionPWMLevel |
SAFEUINT |
‰ |
0 - S_i_PosDirMinPWMLevel |
Defines PWM ratio when S_i_Control = 0 |
S_i_NegDirMinPWMLevel |
SAFEUINT |
‰ |
0 - S_i_CenterPositionPWMLevel |
Defines PWM ratio when S_i_Control = -1 |
S_i_NegDirMaxPWMLevel |
SAFEUINT |
‰ |
0 - S_i_NegDirMinPWMLevel |
Defines PWM ratio when S_i_Control = -10000 |
S_i_PosDirAscendRampTime |
SAFEUINT |
ms |
- |
Defines time how long it takes from ramped signal to change from center to max (0 to 10000). |
S_i_PosDirDescendRampTime |
SAFEUINT |
ms |
- |
Defines time how long it takes from ramped signal to change from max to center (10000 to 0) |
S_i_NegDirAscendRampTime |
SAFEUINT |
ms |
- |
Defines time how long it takes from ramped signal to change from center to negative max (0 to -10000 ) |
S_i_NegDirDescendRampTime |
SAFEUINT |
ms |
- |
Defines time how long it takes from ramped signal to change from negative max to center (-10000 to 0 ) |
S_i_PVGPullUpResistor |
SAFEUDINT |
Ω |
- |
PVG valve pull up resistor |
S_i_PVGPullDownResistor |
SAFEUDINT |
Ω |
- |
PVG valve pull down resistor |
S_i_PinPullUpResistor |
SAFEUDINT |
Ω |
- |
Control unit pin pull up resistor |
S_i_PinPullDownResistor |
SAFEUDINT |
Ω |
- |
Control unit pin pull down resistor |
S_i_DiagnosticDelay |
SAFEUINT |
ms |
- |
Diagnostic delay for PVG valve error signal. |
i_pEventCode |
POINTER TO EventCode |
- |
≠ 0 |
Pointer to application variable where event code is stored. |
i_pEventCodePVGError |
POINTER TO EventCode |
- |
≠ 0 |
Pointer to application variable where event code is stored. |
TRUE: All initialization parameters ok. |
FALSE: Error in initialization parameter(s). |
POU is in normal operation mode if:
• The control is enabled, i.e. i_Enable is TRUE AND
• The input parameters are valid and the input S_i_Control is inside its allowed limits AND
• Startup error is not detected AND
• PVG valve error is not activated
In normal operation the POU first ramp the input control value based on the given acceleration and deceleration parameters and the measured application cycle time.
The ramped value is scaled to output PWM ratio by using compensated PWM level parameters.
When the ramped value is 0 then the output o_PWMRatio is set to compensated center position value.
When the ramped value > 0 then o_PWMRatio is scaled to between compensated positive direction minimum and maximum level values.
When the ramped value < 0 then o_PWMRatio is scaled to between Compensated negative direction minimum and maximum level values.
The PWM level parameters are given as per mil from PWM maximum value G_PWM_OUT_MAXVALUE.
The constant G_PWM_OUT_MAXVALUE is HW dependent and it is defined in HW specific int library.
In normal operation the output o_ValveSupply is also set TRUE.
The output o_PWMRatioControl is set to 0, o_ValveSupply and o_Status.OutputValid are set false, corresponding error bit is set in o_Status and corresponding EventID value is set to EventCode if:
• S_i_Control exceeds the allowed limits -10000- (+)10000 OR
• Input parameter i_pEventCode = 0 OR
• Input parameter i_pEventCodePVG = 0 OR
• PWM parameters exceeds the allowed limits or are not in consistent order OR
• compensated PWM level parameters exceed the allowed limits or are not in consistent order OR
• Startup error is detected i.e. S_i_Control ≠ 0 when i_Enable rises OR
• the PVG error signal is active for the diagnostic delay time
The output o_PWMRatioControl is set to 0, o_Status.OutputValid is set to false immediately if:
• i_Enable is FALSE
• A parameter error occurred.
The o_Status error bits and EventCode error are not reset before the rising edge of i_Enable input.
Input variable name |
Data type |
Unit |
Range |
Description |
i_Enable |
BOOL |
- |
- |
Enable POU operation. |
S_i_Control |
SAFEINT |
- |
-10000 - (+) 10000 |
Control value. |
S_i_PVGError |
SAFEBOOL |
- |
- |
Error signal from PVG valve |
Output variable name |
Data type |
Range |
Description |
o_ValveSupply |
BOOL |
- |
Valve supply output |
o_PWMRatio |
DWORD |
0 - G_PWM_OUT_MAX_VALUE |
Control value to PWM output. |
o_Status |
Status |
- |
Status of output value. See Status structure. |
See Diagnostic Interface library description of error status and event code functionality.
Conditions |
o_PWM Ratio |
o_Valve Supply |
o_Status. OutputValid |
o_Status error status |
Event code FunctionID |
Event code EventID |
i_Enable TRUE AND init parameter error AND |
0 |
FALSE |
FALSE |
ParameterError |
- |
- |
i_Enable TRUE & Parameter error (i_pEventCode ≠ 0) |
0 |
FALSE |
FALSE |
ParameterError |
PVG_CONTROLLER |
PARAMETER_ERROR |
i_Enable TRUE AND init parameters ok AND S_i_Control in normal area (-10000- (+)10000) |
PWM ratio |
TRUE |
TRUE |
- |
NO_FUNC |
NO_ERROR |
i_Enable TRUE AND init parameters ok AND S_i_Control > 10000 |
0 |
FALSE |
FALSE |
InputHigh |
PVG_CONTROLLER |
INPUT_TOO_HIGH |
i_Enable TRUE AND init parameters ok AND S_i_Control < -10000 |
0 |
FALSE |
FALSE |
InputLow |
PVG_CONTROLLER |
INPUT_TOO_LOW |
i_Enable TRUE AND init parameters ok AND S_i_Control in normal area (-10000- (+)10000) AND S_i_PVGError TRUE |
0 |
FALSE |
FALSE |
PVGValveError |
PVG_CONTROLLER |
PVG_VALVE_ERROR |