Supported platforms: CODESYS 3.5
This FB handles single current controlled proportional valve in products that do not have built-in controller.
The FB includes end attenuation, ramp and control curve progression.
A startup error is diagnosed if control is requested on the rising edge of i_Enable.
The output control signal is set to zero if i_Enable is FALSE, parameter error is diagnosed or startup error is diagnosed.
All internal FB initializations are done on the rising edge of i_Enable.
All errors are reset on the rising edge of i_Enable.
|
The FB uses internally SafeProportionalValveControl librarys FBs: S_EndAttenuation S_LinearRamp S_CurrentRequest S_AdaptiveController |
|
Following parameters are taken into use at the rising edge of i_Enable: - i_MaximumCurrent - i_MinimumCurrent - i_CoilResistance - i_OverCurrentLimit - i_WireBrokenLimit - i_CorrectionParameter - i_ImpulseUpParameter - i_PI_P - i_PI_I - i_AttenuationLimit - i_AscendRampTime - i_DescendRampTime - i_DiagnosticDelay + Any initialized event code. |
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
FALSE/TRUE |
Enables controlling of the PWM outputs |
i_Control |
INT |
0..10000 |
Control signal from e.g. joystick. |
i_MeasuredCurrent |
UDINT |
0..i_OverCurrentLimit |
Measured current (mA). |
i_SupplyVoltage |
DINT |
- |
Measured supply voltage (mV). |
i_AttenuationOn |
BOOL |
FALSE/TRUE |
End attenuation sensor activity status. |
i_MaximumCurrent |
UINT |
0..5000 |
Maximum current of valve (mA) |
i_MinimumCurrent |
UINT |
0..5000 |
Minimum current of valve (mA) |
i_CoilResistance |
UDINT |
> 0 |
Coil resistance (mΩ). |
i_OverCurrentLimit |
UINT |
> S_i_Wire BrokenLimit and <= 5000 |
Over current error limit (mA). |
i_WireBrokenLimit |
UINT |
0..5000 |
Wire broken error limit (mA). |
i_CorrectionParameter |
UINT |
- |
Correction factor parameter. 1000 is a neutral value. |
i_ImpulseUpParameter |
UINT |
- |
Impulse up factor parameter. Bigger value means higher impulse. 0 = use default impulse (1000). Impulse can be disabled with AdvancedInit method. |
i_PI_P |
UDINT |
>0* |
PI controller p-value |
i_PI_I |
UDINT |
>0* |
PI controller i-value with two decimals, 1 = 0,01. |
i_AttenuationLimit |
UINT |
0..100% |
End attenuation limit. Percentage from maximum control value 10000. |
i_AscendRampTime |
UINT |
- |
Time (ms) of o_PWMRatio signal to change from center to positive max (0->10000). |
i_DescendRampTime |
UINT |
- |
Time (ms) of o_PWMRatio signal to change from positive max to center (10000->0). |
i_DiagnosticDelay |
UINT |
- |
Diagnostic delay (ms) for overcurrent/wire broken errors. |
*Normally, value >0. PI-controller can be disabled by setting i_PI_P=0 and i_PI_I=0. This is required when finding the optimal i_CorrectionParameter value. See: S_AdaptiveController (FB), section Adjusting correction parameters.
Output variable name |
Data type |
Range |
Description |
o_PWMRatio |
DWORD |
HW specific |
Output value to PWM pin. Maximum value EPEC_HW.Constants.G_PWM_OUT_MAX_VALUE |
o_InputHigh |
BOOL |
FALSE/TRUE |
i_Control too high. |
o_InputLow |
BOOL |
FALSE/TRUE |
i_Control too low. |
o_StartupError |
BOOL |
FALSE/TRUE |
Control request on already when i_Enable rises. |
o_OverCurrentError |
BOOL |
FALSE/TRUE |
Overcurrent error is detected. |
o_WireBrokenError |
BOOL |
FALSE/TRUE |
Wire broken error is detected. |
o_PI_I_TermError |
BOOL |
FALSE/TRUE |
PI-controller I-term has reached it's limits. |
o_ParameterError |
BOOL |
FALSE/TRUE |
Incorrect parameter value in any of the monitored parameters. |
This optional method set controlling parameters for controller.
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
FALSE/TRUE |
Enable operation. |
i_CurrentChangeSpeed |
UINT |
>0 |
Current change speed mA/ms. |
i_UseImpulse |
BOOL |
FALSE/TRUE |
Impulse is used when current request changes more than i_ParStep. |
i_LearnOn |
BOOL |
FALSE/TRUE |
Adaptive controller learning, yet to be implemented. |
i_StartImpulseTime |
UINT |
- |
How long start impulse is active. Parameter affects only if i_AutomaticStartImpulse is false |
i_AutomaticStartImpulse |
BOOL |
FALSE/TRUE |
Controller automatically set start impulse when current request is deviated from 0. |
This optional method can be used for setting an array of correction and impulse parameters for controllers.
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
FALSE/TRUE |
Enable operation. |
i_pCorrectionParameters |
POINTER TO UINT |
>0 |
Pointer to first correction factor parameter. |
i_pImpulseUpParameters |
POINTER TO UINT |
>0 |
Pointer to first impulse up factor parameter. |
i_pImpulseDownParameters |
POINTER TO UINT |
>0 |
Pointer to first impulse down factor parameter. |
i_ParameterCount |
UINT |
- |
Parameter count. |
i_ParStep |
UINT |
>0 |
Difference (mA) between consecutive correction factor parameters. |
This optional method sets pointer for event code.
Input variable name |
Data type |
Description |
i_Enable |
BOOL |
Enable operation. |
i_pEventCode |
POINTER TO EPEC_DITF.EventCode |
Pointer to signal event code value provided by the application. |
See Diagnostic Interface library description of error status and event code functionality.
|
FunctionID and EventID are only set if EventCode is used. |
|
A parameter error is diagnosed if:
|
Conditions |
o_PWMRatio |
Output error set TRUE |
Event code FunctionID |
Event code EventID |
i_Enable TRUE AND parameter error AND i_pEventCode valid |
0 |
o_ParameterError |
depends on the parameter |
PARAMETER_ERROR |
i_Enable TRUE AND parameter error AND |
0 |
o_ParameterError |
- |
- |
i_Enable rises AND parameters ok AND i_Control <> 0 |
0 |
o_StartupError |
CURRENT CONTROLLER |
STARTUP_ERROR |
i_Enable TRUE AND init parameters ok AND S_i_Control within range |
PWM ratio |
- |
NO_FUNC |
NO_ERROR |
i_Enable TRUE AND init parameters ok AND S_i_Control > 10000 |
0 |
o_InputHigh |
END_ATTENUATION |
INPUT_TOO_HIGH |
i_Enable TRUE AND parameters ok AND S_i_Control < -10000 |
0 |
o_InputLow |
END_ATTENUATION |
INPUT_TOO_LOW |
i_Enable TRUE AND parameters ok AND i_CurrentMeasured > i_OverCurrentLimit |
0 |
o_OverCurrentError |
CURRENT CONTROLLER |
OVER_CURRENT |
i_Enable TRUE AND parameters ok AND i_CurrentRequest > 0 AND i_CurrentMeasured < i_WireBrokenLimit |
0 |
o_WireBrokenError |
CURRENT CONTROLLER |
WIRE_BROKEN |
i_Enable TRUE AND parameters ok AND PI controller internal integrator (I) term out of limits |
PWM ratio |
o_PI_I_TermError |
NO_FUNC |
NO_ERROR |
It is possible to use SingleCurrentValveController as traditional PI-controller by using the following settings:
Call AdvancedInit method once with the following input values
i_Enable = TRUE
i_UseImpulse = FALSE.
i_CurrentChangeSpeed = 5000 mA/ms. This ensures that PI-controller is activated immediately.
Other inputs can be FALSE/0.
Set main block input i_CorrectionParameter to value 1. Other inputs can be application specific.