Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY, CODESYS 3.5 SP19 SAFETY

 

S_AdaptiveController (FB)

Description

This function block controls current controlled proportional valves. In normal operation mode the function block adjusts the PWM ratio output so that the measured current achieves the requested current as fast as possible. The function block can be initialized with two methods: Init and InitAdvanced. The function block also includes a startup impulse feature for faster achievement of the target current.

 

See the following chapters for more information about initializing the function block, normal operation and adjusting controller parameters.

 

Initialization methodsInitialization methods

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

S_AdaptiveController contains also optional AdvancedInit method which contains additional parameters. These parameters can be used to optimize the controller in more detail. The default parameter values are used if method is not called. The default parameter values are selected so that the controller works in normal use case (tested with Parker, Schienle valves).

 

A parameter error is diagnosed if:

  • Init method is not called before the main FB call OR

  • i_pEventCode = 0 OR

  • i_pCorrectionParameters = 0 OR

  • i_pImpulseUpParameters = 0 OR

  • i_pImpulseDownParameters = 0 OR

  • S_i_CoilResistance <= 0 OR

  • S_i_OverCurrentLimit out of range OR

  • S_i_WireBrokenLimit out of range OR

  • S_i_OverCurrentLimit <= S_i_WireBrokenLimit

 

 

Init method parameters

Parameter

Type

Unit

Range

Description

S_i_CoilResistance

SAFEUDINT

 > 0

Coil resistance.

S_i_OverCurrentLimit

SAFEUINT

mA

> S_i_Wire BrokenLimit and <= 5000

Over current error limit.

S_i_WireBrokenLimit

SAFEUINT

mA

0-5000

Wire broken error limit. 

S_i_DiagnosticDelay

SAFEUINT

ms

-

Diagnostic delay for overcurrent/wire broken errors.

i_pCorrectionParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains correction factor parameters.

i_pImpulseUpParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains impulse up parameters.

i_pImpulseDownParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains impulse down parameters.

S_i_ParameterCount

SAFEUINT

-

-

Correction parameters array length. Impulse up and down arrays should be same size.

S_i_ParStep

SAFEUINT

mA

-

Difference between adjacent points in correction factor array (and also impulse arrays).

i_pEventCode

POINTER TO EventCode

-

≠ 0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

AdvancedInit method parameters

Parameter

Type

Unit

Default value

Description

S_i_CurrentChangeSpeed

SAFEUINT

mA/ms

1

Current change speed.

S_i_UseImpulse

SAFEBOOL

-

TRUE

Startup impulse in use.

S_i_PI_P

SAFEUDINT

-

30

PI controller P-value. 

S_i_PI_I

SAFEUDINT

-

200

PI controller I-value with two decimals, 1=0,01

S_i_LearnOn

SAFEBOOL

-

FALSE

Learning is active.

S_i_StartImpulseTime

SAFEUINT

ms

20

How long start impulse is active. Parameter affects only if S_i_AutomaticStartImpulse is FALSE.

S_i_AutomaticStartImpulse

SAFEBOOL

-

TRUE

TRUE: startup pulse length is automatically defined.

FALSE: Parameter S_i_StartImpulseTime defines startup pulse length.

 

AdvancedInit method return value

Return value is always TRUE.

 

 

 

 

OperationOperation

S_AdaptiveController is in normal operation mode if:

• The control is enabled, i.e. i_Enable is TRUE AND

• The input parameters are valid and the inputs are inside in allowed limits AND

• Overcurrent or wire broken situation is not detected

 

In normal operation the function block adjusts the output o_PWMRatio so that the measured current i_CurrentMeasured achieves the requested current S_i_CurrentRequest. The measured current should achieve the request current as fast as possible.

 

PWM Ratio Calculation SP10PWM Ratio Calculation SP10

The output PWM ratio o_PWMRatio is calculated from equation 1 (Ohm’s law)

 

 

 

,where RBasis is the base value for resistance

 

, where

CorrectionFactorArr[index] is the correction factor from array defined in application,

index = S_i_CurrentRequest / S_i_ParStep, and

CORRECTION_SCALING = 1000

 

, RPI is the PI-controller

 

, where

CurrentError = OldCurrentRequest-i_MeasuredCurrent, and

Integrator = PI-controller integrator term

 

, RImp is the startup impulse

 

Positive direction

 

Negative direction

 

, where

TargetCurrentChange = S_i_CurrentRequest-OldCurrentRequest,

ImpulseFactor[Index] = Impulse up/down factor from array defined in application,

CurrentErrorPosImp = S_i_CurrentRequest-i_CurrentMeasured and

CurrentErrorNegImp = i_CurrentMeasured-S_i_CurrentRequest

 

, Feedforward term RFF

 

, where fffactor= 0.018

 

 

PWM Ratio Calculation SP19PWM Ratio Calculation SP19

The output PWM ratio o_PWMRatio is calculated from equation 1 (Ohm’s law)




,where RBasis is the base value for resistance


, where

CorrectionFactorArr[index] is the correction factor from array defined in application,

index = S_i_CurrentRequest / S_i_ParStep, and

CORRECTION_SCALING = 1000


, RPI is the PI-controller


, where

CurrentError = OldCurrentRequest-i_MeasuredCurrent, and

Integrator = PI-controller integrator term


, RImp is the startup impulse


Positive direction


Negative direction


, where

TargetCurrentChange = S_i_CurrentRequest-OldCurrentRequest,

ImpulseFactor[Index] = Impulse up/down factor from array defined in application,

CurrentErrorPosImp = S_i_CurrentRequest-i_CurrentMeasured and

CurrentErrorNegImp = i_CurrentMeasured-S_i_CurrentRequest


 

The following figure includes the current request, measured current and PWM ratio as a function of time.

 

 

 

 

 

 

Startup impulseStartup impulse

The function block includes a startup impulse feature for faster achievement of the target current. The startup impulse has two different modes: automatic and manual mode. Depending on the selected mode, PWM output is momentarily bigger until either the given time is exceeded (manual mode) or the measured current rises enough (automatic mode). The used mode is defined by an input S_i_AutomaticStartImpulse.

 

Manual mode:

In manual mode the input parameter S_i_StartImpulseTime defines the startup pulse length.

 

Automatic mode:

In automatic mode the startup pulse is stopped when the measured current is increased enough.

 

 

 

 

PI controller activationPI controller activation

The PI controller is activated when current error is small (≤ S_i_ParStep/2) or if the target current is not reached fast enough.

 

The input parameter S_i_CurrentChangeSpeed [mA/ms] defines how quick the measured current should change.

For example,

 

The PI controller is deactivated when a new start-up pulse is started.

 

 

 

Operation in fault situationsOperation in fault situations

The output o_PWMRatio is set to 0 and o_Status.OutputValid are set false, corresponding error bit is set in o_Status and corresponding EventID value is set to EventCode if:

 

The output wire broken situation is detected when current request is active (S_i_WireBrokenLimitS_i_CurrentRequest) and the measured current is below S_i_WireBrokenLimit over diagnostic delay time S_i_DiagnosticDelay.  

The overcurrent situation is detected when the measured current is above S_i_OverCurrentLimit during diagnostic delay time S_i_DiagnosticDelay.

 

The output o_PWMRatio is set to 0, o_Status.OutputValid is set to false immediately if:

 

If the PI-controller integrator term error is detected the output o_Status.PI_I_TermError is set true but otherwise control is continued normally. In this case EventCode is not activated.

 

The o_Status error bits and EventCode error are not reset before the rising edge of i_Enable input.

 

 

 

Adjusting controller parametersAdjusting controller parameters

For accurate parameter adjusting it is recommended to utilize some CAN bus diagnostic tool, which gives the possibility to graphically monitor CAN signals. The monitored signals are

 

These signals should be transmitted to CAN bus as short transmission period as possible (for example,10 ms) to get a good understanding how the different parameters affect to o_PWMRatio and i_CurrentMeasured.

 

The examples in following sections assumes that

 

 

 

Adjusting P and I termsAdjusting P and I terms

Rough instructions for adjusting PI controller's P and I terms:

  1. Set inputs S_i_PI_I and S_i_PI_P to value 1

  2. Increase S_i_PI_P value (and test with different current requests) until current starts to oscillate. After that decrease S_i_PI_P value a few digits

  3. Increase S_i_PI_I value (and test with different current requests) until current starts to oscillate. After that decrease S_i_PI_I value a few digits    

Adjusting correction parametersAdjusting correction parameters

The correction parameters i_pCorrectionParameters are used to calculate the basis value to o_PWMRatio. The idea is that with correction parameters the o_PWMRatio value is set immediately close to the "correct" value and the PI controller is only used to fix the minor residual current error.

 

The following example graph shows how to adjust the correction factor value to correspond to the current request 400 mA.

 

 

 

In many applications it is enough adjust just the correction parameter which corresponds the minimum current and copy that value to all indexes in correction parameter array.

 

 

 

 

 

Adjusting current change speedAdjusting current change speed

The input S_i_CurrentChangeSpeed is used to define the time delay before PI controller is activated. S_i_CurrentChangeSpeed affects always when the change of S_i_CurrentRequest is more than S_i_ParStep between two consecutive S_AdaptiveController function block instance calls. Typically this situation occurs only in the beginning of movement when current request changes from 0 mA to minimum current.

 

The following graph shows how to adjust  the current change speed. The current request S_i_CurrentRequest changes from 0 mA to 400 mA.

S_i_CurrentChangeSpeed value 20 mA/ms is too big which causes that PI controller is activated too quickly.

 

 
 
 
 
Adjusting impulse up parametersAdjusting impulse up parameters

The input i_pImpulseUpParameters is used to define the startup impulse to o_PWMRatio which will cause that current increases more quickly. i_pImpulseUpParameters affects always when the change of S_i_CurrentRequest is more than S_i_ParStep between two consecutive S_AdaptiveController function block instance calls. Typically this situation occurs only in the beginning of movement when current request changes from 0 mA to minimum current. Note that S_i_UseImpulse needs to be true that startup impulse is used.  

 

The following graph shows how to adjust impulse up parameters. S_i_CurrentRequest changes from 0 mA to 400 mA.

 

 

 

 

 

In many applications it is enough adjust just the impulse up parameter which corresponds the minimum current and the rest of indexes in impulse up parameter array can be ignored.

 

 

 

 

 

Adjusting impulse down parametersAdjusting impulse down parameters

The input i_pImpulseDownParameters is used to define the downward impulse to o_PWMRatio which will cause that current decreases more quickly. i_pImpulseDownParameters affects always when the change (decrease) of i_CurrentRequest is  more than i_ParStep between 2 consecutive PVC_AdaptiveController FB instance calls. In many typical applications this do not occur ever so impulse down parameters can be ignored. Note that i_UseImpulse needs to be true that downward impulse is used.

 

The following graph shows how to adjust impulse down parameters. S_i_CurrentRequest changes from 700 mA to 500 mA.

 

 

 

In many applications the values in impulse down parameter array can be ignored. However, the impulse down array needs always  to be defined and given to the PVC_AdaptiveController as a input.

 

 

 

 

 

 

Parameter automatic learning (S_i_LearnOn) is not supported.

Inputs SP10Inputs SP10

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation.

S_i_CurrentRequest

SAFEUINT

mA

0 - 5000

Requested current value.

i_CurrentMeasured

DWORD

mA

0 - S_i_OverCurrentLimit

Measured current value.

S_i_SupplyVoltMeasured

SAFEDINT

mV

> 0

Measured supply voltage.

 

Inputs SP19Inputs SP19

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation.

S_i_CurrentRequest

SAFEUINT

mA

0 - 5000

Requested current value.

i_CurrentMeasured

DINT

mA

0 - S_i_OverCurrentLimit

Measured current value.

S_i_SupplyVoltMeasured

SAFEDINT

mV

> 0

Measured supply voltage.

 

Outputs

Output variable name

Data type

Range

Description

o_PWMRatio

DWORD

0 - G_PWM_OUT_MAX_VALUE

Control value to PWM output.

o_Status

Status

-

Status of output value. See Status structure.

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

o_PWMRatio

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

Description

i_Enable TRUE AND

init parameter error AND

 i_pEventCode valid

0

FALSE

ParameterError

CURRENT

CONTROLLER  

PARAMETER_ERROR

Check initialization parameters

 

i_Enable TRUE AND

init parameter error AND
i_pEventCode NULL

0

FALSE

ParameterError

-

-

Add event code

i_Enable rises AND

 init parameters ok AND

signal voltage within given limits

PWM ratio

TRUE

-

NO_FUNC

NO_ERROR

Normal operation

i_Enable TRUE AND

init parameters ok AND

S_i_CurrentRequest > 5000

0

FALSE

InputHigh

CURRENT

CONTROLLER  

INPUT_TOO_HIGH

Check current request level

 

i_Enable TRUE AND

init parameters ok AND

S_i_SupplyVoltMeasured ≤ 0

0

FALSE

InputLow

CURRENT

CONTROLLER

 INPUT_TOO_LOW

Check supply voltage level. Also check that outputs are energized when calling the function block.

i_Enable TRUE AND

init parameters ok AND

i_CurrentMeasured > S_i_OverCurrentLimit

0

FALSE

OverCurrentError

CURRENT

CONTROLLER

OVER_CURRENT

Check wires

i_Enable TRUE AND

init parameters ok AND S_i_CurrentRequest > 0 AND i_CurrentMeasured < S_i_WireBrokenLimit

0

FALSE

WireBrokenError

CURRENT

CONTROLLER

WIRE_BROKEN

Check wires

i_Enable TRUE AND

init parameters ok AND PI controller internal integrator (I) term out of limits (range                  -500000...500000)

PWM ratio

TRUE

PI_I_TermError

NO_FUNC

NO_ERROR

The requested current is never reached. Check

- requested current

- P and I terms

Typically, this error occurs if S_i_CurrentRequest is too high

 

Note that the input S_i_DiagnosticDelay does not affect this error.

 

Default values for different valve types

Parker valve 22 Ω

 

(*Parker valve default values to code*)

 

(*Correction factors*)

                                         (*50  100   150  200  250  300 350  400  450  500  550  600  650  700  750  800  850  900  950  1000 mA*)

ccParams:ARRAY [1..20] OF UINT :=       [ 1359,1307,1231,1172,1137,1113,1103,1093,1088,1076,1075,1075,1075,1078,1076,1075,1034,1014,1014,1014];

 

(*Impulse up factors*)

                                         (*50  100   150  200  250 300 350   400  450 500  550 600 650 700 750  800  850  900  950  1000 mA*)

ccParamsImpUp: ARRAY [1..20] OF UINT := [ 1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,950,950,950,950,950,950,950,950,950,950];

 

(*Impulse down factors*)

                                          (*50  100   150  200  250 300 350   400  450 500  550  600  650  700  750  800  850  900  950  1000 mA*)

ccParamsImpDown:ARRAY [1..20] OF UINT:= [ 1200,1200,1100,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000];

 

Hydraforce 29 Ω

 

(*Correction factors*)

                                         (*50  100   150  200  250  300 350  400  450  500  550  600  650  700  750  800   mA*)

ccParams:ARRAY [1..16] OF UINT :=       [ 1230,1230,1190,1080,1070,1010,1010,1010,1010,1010,1010,1010,1010,1010,1010,1010];

 

(*Impulse up factors*)

                                         (*50  100   150  200  250 300 350 400  450 500  550 600 650 700 750  800   mA*)

ccParamsImpUp: ARRAY [1..16] OF UINT := [ 1000,1000,1000, 950, 950,950,950,950, 950,950, 950,950,950,950,950, 950];

 

(*Impulse down factors*)

                                          (*50  100   150  200  250 300 350   400  450 500  550  600  650  700  750  800   mA*)

ccParamsImpDown:ARRAY [1..16] OF UINT:= [ 1200,1200,1100,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000];

 

How to use S_AdaptiveController as traditional PI-controller

It is possible to use S_AdaptiveContoller as traditional PI-controller by using the following settings:

 

  1. Call AdvancedInit method once with the following input values

  2. Set every index of Correction parameters array (Init method input i_pCorrectionParameters address to this array) to value 1. 

 

See also

 

 

 

 