Supported platforms: CODESYS 2.3

 

PVC_AdaptiveController (FB)

Description

This function block controls current controlled proportional valves. PVC_AdaptiveController is a more versatile alternative for standard PI-controller PVC_PI_Controller (which is used by PVC_CurrentValvePairController and PVC_SingleCurrentValveController). PVC_AdaptiveController gives more possibilities to adjust the behavior of output PWM ratio which in turn effects the electric current in valve coil. The usage of adaptive controller is recommended especially when a quick response for current request is required.

 

PVC_CurrentValvePair or PVC_SingleCurrentValve can be used together with PVC_AdaptiveController to get ramp or end attenuation functionalities.

See the code example below.

 

See the following chapters for more information about function block's normal operation and adjusting controller parameters.

 

OperationOperation

PVC_AdaptiveController is in normal operation mode if:

• The control is enabled, i.e. i_Enable is TRUE AND

• The input parameters are valid and the inputs are inside in allowed limits AND

• Overcurrent or wire broken situation is not detected AND

 

In normal operation the function block adjusts the output o_PWMRatio so that the measured current i_CurrentMeasured achieves the requested current i_CurrentRequest. The measured current should achieve the request current as fast as possible.

 

The output PWM ratio is calculated from equation 1 (Ohm’s law)

 

 

, where RBasis is the base value for resistance

 

, where

CorrectionFactorArr[index] is the correction factor from array defined in application,

index = i_CurrentRequest / i_ParStep, and

CORRECTION_SCALING = 1000

 

, RPI is the PI-controller

 

, where

CurrentError = OldCurrentRequest-i_MeasuredCurrent, and

Integrator = PI-controller integrator term

 

, RImp is the startup impulse

 

Positive direction:

Negative direction:

, where

TargetCurrentChange = i_CurrentRequest-OldCurrentRequest,

ImpulseFactor[Index] = Impulse up/down factor from array defined in application,

CurrentErrorPosImp = i_CurrentRequest-i_CurrentMeasured and

CurrentErrorNegImp = i_CurrentMeasured-i_CurrentRequest

 

, Feedforward term RFF

 

 

, where fffactor= 0.018

 

 

The following figure shows the current request, measured current and PWM ratio as a function of time.

 

 

 

 

 

Startup impulseStartup impulse

The function block includes a startup impulse feature for faster achievement of the target current. The startup impulse has two different modes: automatic and manual mode. Depending on the selected mode, PWM output is momentarily bigger until either the given time is exceeded (manual mode) or the measured current rises enough (automatic mode). The used mode is defined by an input i_AutomaticStartImpulse.

 

Manual mode:

In manual mode the input parameter i_StartImpulseTime defines the startup pulse length.

 

Automatic mode:

In automatic mode the startup pulse is stopped when the measured current is increased enough.

 

 

 

 

PI controller activationPI controller activation

The PI controller is activated when current error is small (≤ i_ParStep/2) or if the target current is not reached quick enough.

 

The input parameter i_CurrentChangeSpeed [mA/ms] defines how quick the measured current should change. For example,

 

The PI controller is deactivated when a new start-up pulse is started.

 

 

 

Operation in fault situationsOperation in fault situations

The output o_PWMRatio is set to 0 and corresponding error bit is set on:

i_CurrentRequest > 5000 OR

i_SupplyVoltMeasured ≤ 0 OR

• Output wire broken or overcurrent situation detected OR

• The input parameters are invalid OR

 

The output wire broken situation is detected when current request is active (i_WireBrokenLimiti_CurrentRequest) and the measured current is below i_WireBrokenLimit over diagnostic delay time i_DiagnosticDelay.  

The overcurrent situation is detected when the measured current is above i_OverCurrentLimit during diagnostic delay time i_DiagnosticDelay.

 

The output o_PWMRatio is set to 0 immediately if:

i_Enable is FALSE

 

The error bits are not reset before the rising edge of i_Enable input.

 

 

 

Adjusting controller parametersAdjusting controller parameters

How to adjust controller parameters

For accurate parameter adjusting it is recommended to utilize some CAN bus diagnostic tool, which gives the possibility to monitor graphically CAN signals. The monitored signals are

 

These signals should be transmitted to CAN bus as short transmission period as possible (for example, 10 ms) to get a good understanding how the different parameters affect to o_PWMRatio and i_CurrentMeasured.

 

The examples in following sections assumes that

 

 

 

 

Adjusting P and I termsAdjusting P and I terms

Rough instructions for adjusting PI controller's P and I terms:

    1. Set i_PI_I = 1

    2. Increase i_PI_P value (and test with different current requests) until current starts to oscillate. After that decrease i_PI_P value a few digits

    3. Increase i_PI_I value (and test with different current requests) until current starts to oscillate. After that decrease i_PI_I value a few digits    

 

Adjusting correction parametersAdjusting correction parameters

The correction parameters i_pCorrectionParameters are used to calculate the basis value to o_PWMRatio. The idea is that with correction parameters the o_PWMRatio value is set immediately close to the "correct" value and the PI controller is only used to fix the minor residual current error.

 

The following example graph shows how to adjust the correction factor value to correspond to current request 400 mA.

 

 

 

In many applications it is enough adjust just the correction parameter which corresponds the minimum current and copy that value to all indexes in correction parameter array.

 

 

 

 

Adjusting current change speedAdjusting current change speed

The input i_CurrentChangeSpeed is used to define the time delay before PI controller is activated. i_CurrentChangeSpeed affects always when the change of i_CurrentRequest is  more than i_ParStep between 2 consecutive PVC_AdaptiveController function block instance calls. Typically this situation occurs only in the beginning of movement when current request changes from 0 mA to minimum current.

 

The following graph shows how to adjust the current change speed. The current request i_CurrentRequest changes from 0 mA to 400 mA. i_CurrentChangeSpeed value 20 mA /ms is too big so PI controller is activated too quickly.

 

 
 
 

Adjusting impulse up parametersAdjusting impulse up parameters

The input i_pImpulseUpParameters is used to define the startup impulse to o_PWMRatio which will cause that current increases more quickly. i_pImpulseUpParameters affects always when the change of i_CurrentRequest is  more than i_ParStep between 2 consecutive PVC_AdaptiveController FB instance calls. Typically this situation occurs only in the beginning of movement when current request changes from 0 mA to minimum current. Note that i_UseImpulse needs to be true that startup impulse is used.  

 

The following graph shows how to adjust impulse up parameters. i_CurrentRequest changes from 0 mA to 400 mA.

 

 

 

 

 

In many applications it is enough adjust just the impulse up parameter which corresponds the minimum current and the rest of indexes in impulse up parameter array can be ignored.

 

 

 

 

 

Adjusting impulse down parametersAdjusting impulse down parameters

The input i_pImpulseDownParameters is used to define the downward impulse to o_PWMRatio which will cause that current decreases more quickly. i_pImpulseDownParameters affects always when the change (decrease) of i_CurrentRequest is  more than i_ParStep between 2 consecutive PVC_AdaptiveController FB instance calls. In many typical applications this do not occur ever so impulse down parameters can be ignored. Note that i_UseImpulse needs to be true that downward impulse is used.

 

The following graph shows how to adjust impulse down parameters. i_CurrentRequest changes from 700 mA to 500 mA.

 

 

 

In many applications the values in impulse down parameter array can be ignored. However, the impulse down array needs always  to be defined and given to the PVC_AdaptiveController as a input.

 

 

 

 

 

 

 

A parameter error is diagnosed if:

  • i_pCorrectionParameters = 0 OR

  • i_pImpulseUpParameters = 0 OR

  • i_pImpulseDownParameters = 0 OR

  • i_CoilResistance <= 0 OR

  • i_OverCurrentLimit out of range OR

  • i_WireBrokenLimit out of range OR

  • i_OverCurrentLimit <= S_i_WireBrokenLimit

 

Limitations

Parameter automatic learning (i_LearnOn) is not supported.

 

Inputs

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation.

i_CurrentRequest

UINT

mA

0 - 5000

Requested current value.

i_CurrentMeasured

DWORD

mA

0 - i_OverCurrentLimit

Measured current value.

i_SupplyVoltMeasured

UINT

Hardware specific

> 0

Measured supply voltage with two decimals, 2400=24,00V

i_CoilResistance

UDINT

 > 0

Coil resistance.

i_OverCurrentLimit

UINT

mA

> i_Wire BrokenLimit and <= 5000

Over current error limit.

i_WireBrokenLimit

UINT

mA

0-5000

Wire broken error limit. 

i_DiagnosticDelay

UINT

ms

-

Diagnostic delay for overcurrent/wire broken errors.

i_pCorrectionParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains correction factor parameters.

i_pImpulseUpParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains impulse up parameters.

i_pImpulseDownParameters

POINTER TO UINT

-

≠ 0

Pointer to array which contains impulse down parameters.

i_ParameterCount

UINT

-

-

Correction parameters array length. Impulse up and down arrays should be same size.

i_ParStep

UINT

mA

-

Difference between adjacent points in correction factor array (and also impulse arrays).

i_CurrentChangeSpeed

UINT

mA/ms

-

Current change speed.

i_UseImpulse

BOOL

-

-

Startup impulse in use.

i_PI_P

UDINT

-

-

PI controller P-value. 

i_PI_I

UDINT

-

-

PI controller I-value with two decimals, 1=0,01

i_LearnOn

BOOL

-

-

Learning is active. Note! NOT SUPPORTED

i_StartImpulseTime

UINT

ms

-

How long start impulse is active. Parameter affects only if i_AutomaticStartImpulse is FALSE and i_UseImpulse is TRUE.

i_AutomaticStartImpulse

BOOL

-

-

 

TRUE: startup pulse length is automatically defined.

FALSE: Parameter i_StartImpulseTime defines startup pulse length.

Parameter affects only if i_UseImpulse is TRUE.

Outputs

Output variable name

Data type

Range

Description

o_PWMRatio

DWORD

0 - HW specific

Control value to PWM output.

o_ParameterError

BOOL

-

Parameter error

o_OverCurrentError

BOOL

-

Overcurrent error is detected

o_WireBrokenError

BOOL

-

Wire broken error is detected

o_PI_I_TermError

BOOL

-

PI-controller I-term has reached it's limits

 

Error diagnostic

 

Conditions

o_PWMRatio

o_Parameter Error

o_OverCurrent Error

o_WireBroken Error

o_PI_I_TermError

i_Enable = TRUE AND

 parameters ok AND

i_CurrentMeasured  within given error limits

PWM ratio

FALSE

FALSE

FALSE

FALSE

i_Enable TRUE AND

i_SupplyVoltMeasured = 0

0

TRUE

FALSE

FALSE

FALSE

i_Enable TRUE AND

i_CurrentRequest > 5000

0

TRUE

FALSE

FALSE

FALSE

i_Enable TRUE AND

parameters ok AND i_CurrentMeasured > i_OverCurrentLimit

0

(After diagnostic delay)

FALSE

TRUE

(After diagnostic delay)

FALSE

FALSE

i_Enable TRUE AND

parameters ok AND i_CurrentRequest > 0 AND

i_CurrentMeasured < i_WireBrokenLimit

0

(After diagnostic delay)

FALSE

FALSE

TRUE

(After diagnostic delay)

FALSE

i_Enable TRUE AND

parameters ok AND

PI controller internal integrator term out of limits (-50000 - 50000)

(Integrator term value is limited)

PWM ratio

FALSE

FALSE

FALSE

TRUE

(Output is set true when the POU's internal integrator term limit is reached.  The input i_DiagnosticDelay

do not have an effect on this output)

 

 

Default values for different valve types

Parker valve 22 Ω

 

(*Parker valve default values to code*)

 

(*Correction factors*)

                                         (*50  100   150  200  250  300 350  400  450  500  550  600  650  700  750  800  850  900  950  1000 mA*)

ccParams:ARRAY [1..20] OF UINT :=       [ 1359,1307,1231,1172,1137,1113,1103,1093,1088,1076,1075,1075,1075,1078,1076,1075,1034,1014,1014,1014];

 

(*Impulse up factors*)

                                         (*50  100   150  200  250 300 350   400  450 500  550 600 650 700 750  800  850  900  950  1000 mA*)

ccParamsImpUp: ARRAY [1..20] OF UINT := [ 1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,950,950,950,950,950,950,950,950,950,950];

 

*Impulse down factors*)

                                          (*50  100   150  200  250 300 350   400  450 500  550  600  650  700  750  800  850  900  950  1000 mA*)

ccParamsImpDown:ARRAY [1..20] OF UINT:= [ 1200,1200,1100,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000];

 

Hydraforce 29 Ω

 

(*Correction factors*)

                                         (*50  100   150  200  250  300 350  400  450  500  550  600  650  700  750  800   mA*)

ccParams:ARRAY [1..16] OF UINT :=       [ 1230,1230,1190,1080,1070,1010,1010,1010,1010,1010,1010,1010,1010,1010,1010,1010];

 

(*Impulse up factors*)

                                         (*50  100   150  200  250 300 350 400  450 500  550 600 650 700 750  800   mA*)

ccParamsImpUp: ARRAY [1..16] OF UINT := [ 1000,1000,1000, 950, 950,950,950,950, 950,950, 950,950,950,950,950, 950];

 

*Impulse down factors*)

                                          (*50  100   150  200  250 300 350   400  450 500  550  600  650  700  750  800   mA*)

ccParamsImpDown:ARRAY [1..16] OF UINT:= [ 1200,1200,1100,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000,1000];

 

Code example

Parameters:

VAR_GLOBAL

   PAR_BoomAdaptiveCntr:  BoomAdaptiveCntr;

   PAR_CorrectionFactors: ARRAY[1..20] OF UINT:= 1359, 1307, 1231, 1172, 1137, 1113, 1103, 1093, 1088, 1076, 3(1075), 1078, 1076, 1075, 1034, 3(1014);

   PAR_ImpulseUpFactors:  ARRAY[1..20] OF UINT:= 10(1000), 10(950);

   PAR_ImpulseDownFactors:ARRAY[1..20] OF UINT:= 20(1000);

END_VAR

 

Local variables:

VAR

   boomControlEnabled:   BOOL;

   boomValvePair:        PVC_CurrentValvePair;

   boomUpController:     PVC_AdaptiveController;

END_VAR

 

 

 

See also

 

 

Source file topic100532.htm