Supported platforms: CODESYS 2.3, CODESYS 3.5
PVC_SingleCurrentValveController function block controls a current controlled proportional valve in products that do not have a controller built in at firmware, such as Epec 3000 series.
The function block calls PVC_SingleCurrentValve FB and converts its output to a PWM request with PVC_CurrentController.
ADC_To_mAOrV is used to convert feedback signal to mA value for the current controller.
PVC_ValveDiagnostic FB is called for diagnosing short circuit and broken circuit errors. In case of a short circuit or a broken circuit error, PWM output is disabled until i_Control is set to zero (this function can, however, be disabled with parameter).
If i_Enable is inactive or in case of a parameter error or AI voltage error, the PWM request and valve supply outputs are set to zero.
|
Use only with hardware that does not have a built-in current controller, i.e. PWM value is written to output. |
|
i_Control must be 0 on the rising edge of i_Enable status. Otherwise control is not enabled. |
|
When the linear ramp type is selected, the ramp speed changes when the current parameters are changed. |
|
By leaving P- and I-parameters empty (0), default values are calculated from coil resistance. See function PVC_Initialize_P_and_I. |
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
FALSE/TRUE |
Enables controlling of the o_CurrentRequest output. |
i_Control |
INT |
0..32767 |
Control signal from e.g. pedal. |
i_FeedbackCurrent |
UINT |
Hardware specific |
ADC current value from FB input or high side current measure. |
i_FBType |
BYTE |
0.. G_ADScaleArrMax |
Type of current feedback input |
i_MaxCurrent |
UINT |
1..2500 mA |
Maximum current for valve. |
i_MinCurrent |
UINT |
1..2500 mA |
Minimum current for valve. |
i_RampType |
BYTE |
0..G_RampTypeMax |
Defines which one of the available ramp functions is used. |
i_AscendRamp |
UINT |
Ramp specific |
Ascending speed for valve, range and unit depends on selected ramp type. |
i_DescendRamp |
UINT |
Ramp specific
|
Descending speed for valve, range and unit depends on selected ramp type. |
i_AttenuationOn |
BOOL |
FALSE/TRUE |
If input is true, controlling is limited to given percentage of max control. |
i_AttenuationAmount |
BYTE |
0..100% |
Amount of attenuation. |
i_SupplyVoltage |
UINT |
Hardware specific |
Measured supply voltage with two decimals, 2400=24,00V |
i_Fast |
BOOL |
FALSE/TRUE |
Use fast PI curve pre-scaled parameters by default. Pre-scaled P and I are used if either of given (i_P_Gain or i_I_Gain) is zero. |
i_P_Gain |
UINT |
0..65535 |
Proportional gain of PI controller, 1000 = 1 |
i_I_Gain |
UINT |
0..65535 |
Integration gain of PI controller, 1000 = 1 |
i_CoilResistance |
UINT |
3..200 Ohm |
Coil resistance value in Ohms. |
i_CircuitErrorDelay |
UINT |
0..65535 ms |
Delay before error outputs are activated in ms. |
i_CircuitErrorDisablesOutput |
BOOL |
FALSE/TRUE |
Defines if PWM output is disabled in short circuit or broken circuit error situations. |
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
FALSE/TRUE |
Enables controlling of the o_CurrentRequest output. |
i_Control |
INT |
0..32767 |
Control signal from e.g. pedal. |
i_FeedbackCurrent |
UINT |
Hardware specific |
ADC current value from FB input or high side current measure. |
i_FBType |
ADData |
G_AIType struct |
Type of current feedback input. |
i_PWMType |
ADData |
G_AIType struct |
Type of PWM output. |
i_MaxCurrent |
UINT |
1..2500 mA |
Maximum current for valve. |
i_MinCurrent |
UINT |
1..2500 mA |
Minimum current for valve. |
i_RampType |
BYTE |
0..G_RampTypeMax |
Defines which one of the available ramp functions is used. |
i_AscendRamp |
UINT |
Ramp specific |
Ascending speed for valve, range and unit depends on selected ramp type. |
i_DescendRamp |
UINT |
Ramp specific
|
Descending speed for valve, range and unit depends on selected ramp type. |
i_AttenuationOn |
BOOL |
FALSE/TRUE |
If input is true, controlling is limited to given percentage of max control. |
i_AttenuationAmount |
BYTE |
0..100% |
Amount of attenuation. |
i_SupplyVoltage |
UINT |
Hardware specific |
Measured supply voltage with two decimals, 2400=24,00V |
i_Fast |
BOOL |
FALSE/TRUE |
Use fast PI curve pre-scaled parameters by default. Pre-scaled P and I are used if either of given (i_P_Gain or i_I_Gain) is zero. |
i_P_Gain |
UINT |
0..65535 |
Proportional gain of PI controller, 1000 = 1 |
i_I_Gain |
UINT |
0..65535 |
Integration gain of PI controller, 1000 = 1 |
i_CoilResistance |
UINT |
3..200 Ohm |
Coil resistance value in Ohms. |
i_CircuitErrorDelay |
UINT |
0..65535 ms |
Delay before error outputs are activated in ms. |
i_CircuitErrorDisablesOutput |
BOOL |
FALSE/TRUE |
Defines if PWM output is disabled in short circuit or broken circuit error situations. |
Output variable name |
Data type |
Range |
Description |
o_PWMOutput |
UINT |
Hardware specific |
PWM control for valve. |
o_ValveSupply |
BOOL |
FALSE/TRUE |
Control condition for valve supply volt output. |
o_ParameterError |
BOOL |
FALSE/TRUE |
True when incorrect parameter value in any of the FB’s input. |
o_ShortCircuit |
BOOL |
FALSE/TRUE |
Short circuit in valve’s circuit |
o_BrokenCircuit |
BOOL |
FALSE/TRUE |
Valve’s circuit is broken |
o_CurrentWithoutControl |
BOOL |
FALSE/TRUE |
There is current without control |
Output variable name |
Data type |
Range |
Description |
o_PWMOutput |
UINT |
Hardware specific |
PWM control for valve. |
o_ValveSupply |
BOOL |
FALSE/TRUE |
Control condition for valve supply volt output. |
o_ParameterError |
BOOL |
FALSE/TRUE |
True when incorrect parameter value in any of the FB’s input. |
o_ShortCircuit |
BOOL |
FALSE/TRUE |
Short circuit in valve’s circuit |
o_BrokenCircuit |
BOOL |
FALSE/TRUE |
Valve’s circuit is broken |
o_CurrentWithoutControl |
BOOL |
FALSE/TRUE |
There is current without control |
o_IllegalControlRequestInStartup |
BOOL |
FALSE/TRUE |
True if unexpected control request occurs. i_Control is not 0 when i_Enable is set to true. |

Source file Topic000469.htm