PVC_CurrentValvePairController (FB)

Description

PVC_CurrentValvePairController function block controls a current controlled proportional pair in products that do not have a controller built in at firmware, such as Epec 3000 series.

 

The function block calls PVC_CurrentValvePair FB and converts its output to a PWM request with PVC_CurrentController.

ADC_To_mAOrV is used to convert feedback signal to mA value for the current controller.

 

PVC_ValveDiagnostic FB is called for diagnosing short circuit and broken circuit errors. In case of a short circuit or a broken circuit error, PWM outputs are disabled until i_Control is set to zero (this function can, however, be disabled with a parameter).

 

With i_CommonCurrentMeasure input the user can define whether there are separate current measure signals for both PWM outputs or not.

 

With i_EnableCounterControl input the user can enable the counter control feature, but only if both valves have their own current measurements  (i_CommonCurrentMeasure is FALSE). The counter control feature allows both valves to be controlled simultaneously. This makes it possible to counter control.

 

If i_Enable is inactive or in case of a parameter error or AI voltage error, the PWM request and valve supply outputs are set to zero.

Limitations

Use only with hardware that does not have a built-in current controller, i.e. PWM value is written to output.

 

i_Control must be 0 on the rising edge of i_Enable status. Otherwise control is not enabled.

 

When the linear ramp type is selected, the ramp speed changes when the current parameters are changed.

 

By leaving P- and I-parameters empty (0), default values are calculated from coil resistance. See function PVC_Initialize_P_and_I.

 

Inputs

CODESYS 2.3CODESYS 2.3

Input variable name

Data type

Range

Description

i_Enable

BOOL

FALSE/TRUE

Enables controlling of the current request outputs.

i_Control

INT

-32767..32767

Control signal from e.g. joystick

i_PosDirFeedbackCurrent

UINT

Hardware specific

ADC current value from FB input or high side current measure.

i_NegDirFeedbackCurrent

UINT

Hardware specific

ADC current value from FB input or high side current measure.

i_FBType

BYTE

0.. G_ADScaleArrMax

Type of current feedback inputs

i_CommonCurrentMeasure

BOOL

FALSE/TRUE

Defines if there is separate current measuring for both pwm outputs or not. When true, i_PosDirFeedbackCurrent input is used as common measure for both directions.

i_PosDirMaxCurrent

UINT

1..2500 mA

Maximum current for valve that is controlled with positive control signal

i_PosDirMinCurrent

UINT

1..2500 mA

Minimum current for valve that is controlled with positive control signal

i_NegDirMinCurrent

UINT

1..2500 mA

Minimum current for valve that is controlled with negative control signal

i_NegDirMaxCurrent

UINT

1..2500 mA

Maximum current for valve that is controlled with negative control signal.

i_RampType

BYTE

0..G_RampTypeMax

Defines which one of the available ramp functions is used.

i_PosDirAscendRamp

UINT

Depends on selected ramp type

Ascending speed for valve that is controlled with positive control signal, range and unit depends on selected ramp type.

i_PosDirDescendRamp

UINT

Depends on selected ramp type

Descending speed for valve that is controlled with positive control signal, range and unit depends on selected ramp type.

i_NegDirAscendRamp

UINT

Depends on selected ramp type

Ascending speed for valve that is controlled with negative control signal, range and unit depends on selected ramp type.

i_NegDirDescendRamp

UINT

Depends on selected ramp type

Descending speed for valve that is controlled with negative control signal, range and unit depends on selected ramp type.

i_PosDirAttenuationOn

BOOL

FALSE/TRUE

If input is true, controlling of positive direction valve is limited to given percentage of max control.

i_NegDirAttenuationOn

BOOL

FALSE/TRUE

If input is true, controlling of negative direction valve is limited to given percentage of max control.

i_PosDirAttenuationAmount

BYTE

0..100%

Amount of attenuation for positive direction valve.

i_NegDirAttenuationAmount

BYTE

0..100%

Amount of attenuation for negative direction valve.

i_EnableCounterControl

BOOL

FALSE/TRUE

Both valves can be controlled at the same time.

i_SupplyVoltage

UINT

Hardware specific

Measured supply voltage with two decimals, 2400 = 24,00V

i_Fast

BOOL

FALSE/TRUE

Use fast PI curve pre-scaled parameters by default. Pre-scaled P and I are used if both given i_P_Gain and i_I_Gain is zero.

i_P_Gain

UINT

0..65535

Proportional gain of PI controller, 1000 = 1

i_I_Gain

UINT

0..65535

Integration gain of PI controller, 1000 = 1

i_CoilResistance

UINT

3..200 Ohm

Coil nominal resistance value in Ohms.

i_CircuitErrorDelay

UINT

0..65535 ms

Delay before error outputs are activated in ms.

i_CircuitErrorDisablesOutput

BOOL

FALSE/TRUE

Defines if PWM output is disabled in short circuit or broken circuit error situations

 

 

CODESYS 3.5CODESYS 3.5

Input variable name

Data type

Range

Description

i_Enable

BOOL

FALSE/TRUE

Enables controlling of the current request outputs.

i_Control

INT

-32767..32767

Control signal from e.g. joystick

i_PosDirFeedbackCurrent

UINT

Hardware specific

ADC current value from FB input or high side current measure.

i_NegDirFeedbackCurrent

UINT

Hardware specific

ADC current value from FB input or high side current measure.

i_FBType

ADData

G_AIType struct

Type of current feedback inputs.

i_PWMType

ADData

G_AIType struct

Type of PWM output.

i_CommonCurrentMeasure

BOOL

FALSE/TRUE

Defines if there is separate current measuring for both pwm outputs or not. When true, i_PosDirFeedbackCurrent input is used as common measure for both directions.

i_PosDirMaxCurrent

UINT

1..2500 mA

Maximum current for valve that is controlled with positive control signal

i_PosDirMinCurrent

UINT

1..2500 mA

Minimum current for valve that is controlled with positive control signal

i_NegDirMinCurrent

UINT

1..2500 mA

Minimum current for valve that is controlled with negative control signal

i_NegDirMaxCurrent

UINT

1..2500 mA

Maximum current for valve that is controlled with negative control signal.

i_RampType

BYTE

0..G_RampTypeMax

Defines which one of the available ramp functions is used.

i_PosDirAscendRamp

UINT

Depends on selected ramp type

Ascending speed for valve that is controlled with positive control signal, range and unit depends on selected ramp type.

i_PosDirDescendRamp

UINT

Depends on selected ramp type

Descending speed for valve that is controlled with positive control signal, range and unit depends on selected ramp type.

i_NegDirAscendRamp

UINT

Depends on selected ramp type

Ascending speed for valve that is controlled with negative control signal, range and unit depends on selected ramp type.

i_NegDirDescendRamp

UINT

Depends on selected ramp type

Descending speed for valve that is controlled with negative control signal, range and unit depends on selected ramp type.

i_PosDirAttenuationOn

BOOL

FALSE/TRUE

If input is true, controlling of positive direction valve is limited to given percentage of max control.

i_NegDirAttenuationOn

BOOL

FALSE/TRUE

If input is true, controlling of negative direction valve is limited to given percentage of max control.

i_PosDirAttenuationAmount

BYTE

0..100%

Amount of attenuation for positive direction valve.

i_NegDirAttenuationAmount

BYTE

0..100%

Amount of attenuation for negative direction valve.

i_EnableCounterControl

BOOL

FALSE/TRUE

Both valves can be controlled at the same time.

i_SupplyVoltage

UINT

Hardware specific

Measured supply voltage with two decimals, 2400 = 24,00V

i_Fast

BOOL

FALSE/TRUE

Use fast PI curve pre-scaled parameters by default. Pre-scaled P and I are used if both given i_P_Gain and i_I_Gain is zero.

i_P_Gain

UINT

0..65535

Proportional gain of PI controller, 1000 = 1

i_I_Gain

UINT

0..65535

Integration gain of PI controller, 1000 = 1

i_CoilResistance

UINT

3..200 Ohm

Coil nominal resistance value in Ohms.

i_CircuitErrorDelay

UINT

0..65535 ms

Delay before error outputs are activated in ms.

i_CircuitErrorDisablesOutput

BOOL

FALSE/TRUE

Defines if PWM output is disabled in short circuit or broken circuit error situations

 

Outputs

CODESYS 2.3CODESYS 2.3

 

Output variable name

Data type

Range

Description

o_PosDirPWMOutput

UINT

HW specific

PWM control for valve that is controlled with positive control signal.

o_PosDirValveSupply

BOOL

FALSE/TRUE

Control condition for valve supply volt output.

o_NegDirPWMOutput

UINT

HW specific

PWM control for valve that is controlled with negative control signal.

o_NegDirValveSupply

BOOL

FALSE/TRUE

Control condition for valve supply volt output.

o_ParameterError

BOOL

FALSE/TRUE

True when incorrect parameter value in any of the FB’s input.

o_PosDirShortCircuit

BOOL

FALSE/TRUE

Short circuit in positive direction valve’s circuit.

o_NegDirShortCircuit

BOOL

FALSE/TRUE

Short circuit in negative direction valve’s circuit.

o_PosDirBrokenCircuit

BOOL

FALSE/TRUE

Positive direction valve’s circuit is broken.

o_NegDirBrokenCircuit

BOOL

FALSE/TRUE

Negative direction valve’s circuit is broken.

o_PosDirCurrentWithoutControl

BOOL

FALSE/TRUE

There is measured current without control in positive direction circuit.

o_NegDirCurrentWithoutControl

BOOL

FALSE/TRUE

There is measured current without control in negative direction circuit.

 

CODESYS 3.5CODESYS 3.5

 

Output variable name

Data type

Range

Description

o_PosDirPWMOutput

UINT

HW specific

PWM control for valve that is controlled with positive control signal.

o_PosDirValveSupply

BOOL

FALSE/TRUE

Control condition for valve supply volt output.

o_NegDirPWMOutput

UINT

HW specific

PWM control for valve that is controlled with negative control signal.

o_NegDirValveSupply

BOOL

FALSE/TRUE

Control condition for valve supply volt output.

o_ParameterError

BOOL

FALSE/TRUE

True when incorrect parameter value in any of the FB’s input.

o_PosDirShortCircuit

BOOL

FALSE/TRUE

Short circuit in positive direction valve’s circuit.

o_NegDirShortCircuit

BOOL

FALSE/TRUE

Short circuit in negative direction valve’s circuit.

o_PosDirBrokenCircuit

BOOL

FALSE/TRUE

Positive direction valve’s circuit is broken.

o_NegDirBrokenCircuit

BOOL

FALSE/TRUE

Negative direction valve’s circuit is broken.

o_PosDirCurrentWithoutControl

BOOL

FALSE/TRUE

There is measured current without control in positive direction circuit.

o_NegDirCurrentWithoutControl

BOOL

FALSE/TRUE

There is measured current without control in negative direction circuit.

o_IllegalControlRequestInStartup

BOOL

FALSE/TRUE

True if unexpected control request occurs. i_Control is not 0 when i_Enable is set to true.

 

Example code

 

See also

 