AI/DI/PI_type096

 

Possible pin modes:

 

Select the mode using MultiTool Creator. MultiTool Creator generates the needed code using functions from SafeSSeriesIODriverExt library. For more information refer to Epec Programming and Libraries Manual and MultiTool Creator Manual.

AI (analog input) mode

 

 

DI (digital input) mode

 

 

PI (pulse input) mode

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

VI

Input Voltage measuring range

 

0

6

V

RI

Input Resistance

Input high: Referenced to GND (Note 5)

 

86

RPD

Pull-down Resistance

DI mode

10,3

10,5

RPU

Pull-up Resistance

PU mode

2,18

2,22

VIevel

Voltage level

Unconnected pin,

no pull-up selected

typ. 0

V

Unconnected pin,

pull-up selected

typ. 4,6

IE

Input Error

Voltage mode

 

+/- 2

%

BW

Input Low Pass Filter Bandwidth

(-3 dB cut-off frequency)

Voltage mode

1600

Hz

VIH

Input High Voltage

PI mode

3,6

34

V

VIL

Input Low Voltage

PI mode

-0,5

1,4

V

fI

Input Frequency (frequency measurement and pulse counting)

(Note 4)

 

20

kHz

fI

Input Frequency
(digital inputs)

(Note 2, 3)

 

1/ 2tC

kHz

tI

Input Pulse Width

 

0,1

500

ms

CI

Input Capacitance

 

typ. 1

nF

VI-range

 

Input voltage range

 

(Note 1)

-0,5

34

V

 

Cable length

 

 

30

m

 

 

 

Note 1:  Exceeding the max value might cause damage to input.

Note 2:  tC denotes the software cycle time in milliseconds.

Note 3: The pulse width must be greater than the software cycle time. For example, with 50/50 pulse ratio, the pulse frequency is 1 / (2*pulse width)

Note 4: The maximum value can be reached with 50 % duty cycle

Note 5: The input resistance is typically 86 , while input voltage is < 5,6 V. When input voltage increases over 5,6 V, the input resistance decreases in a non-linear function.

 

Functional block diagram

 

 

 

 

 