DO/DI

Possible pin modes:

 

DO (digital output) mode

 

It is recommended to use the function blocks in DigitalOutputDiagnostics library to protect and diagnose outputs when used as digital outputs. For more information, refer to Epec Programming and Libraries Manual.

DI (digital input) mode

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

VLevel

Output voltage

Output Off, Pull-up selected, Unconnected pin,

Uin = 24 V

VLevel =  Uin/1,3

typ. 18,5

V

Io

Nominal Output Current

Output On
(Note 3, 4)

0

1

A

Io-lim

Internal current limitation

Output On (Note 2, 6)

typ. 12

A

Digital status input

RI

Input Resistance

Output Off, Pull-up resistor not selected, VI< Uin (referenced to GND)

typ. 44

Output Off, Pull-up resistor selected, (referenced to Uin /1,3)

typ. 8,1

VIH

High Voltage level

Output Off (Note 3, 8)

4,2

Uin

V

VIL

Low Voltage level

Output Off (Note 8)

 

3,2

V

VI-range

Input voltage range

(Note 7)

-0,5

Uin 

V

tI

Digital Status Input
Pulse Width

(Note 1, 5)

 

> tC

ms

CI

Input pin capacitance

 

typ. 1

nF

Note 1:  tC denotes software cycle time.

Note 2: Current limit for short circuit protection to protect cabling and to limit internal power dissipation.

Note 3: Exceeding the max value might cause damage to input.

Note 4: The maximum output current depends on the load and temperature.

Note 5: Pulse width must be greater that the software cycle time. For example with 50/50 pulse ratio, the pulse frequency is 1 / (2*pulse width)

Note 6: When the limit is exceeded, the output voltage circuit starts to limit the current by switching the output voltage. The switching does not affect the application software.

Note 7: Overload conditions

Note 8: Includes hysteresis. The input state is maintained until the second voltage limit is exceeded.


Functional block diagram