Ethernet Cabling

In order that the electromagnetic interference (EMI) would not effect the data transfer, the installation of the cable should be done as close as possible to the body of the machine.

 

It is recommended to wire the cable under the shelter of mechanical hits if the installation environment makes it possible.

 

The cable must be installed as far away as possible from other cables with high power.

 

The maximum length of a connection is 30 meters.

 

 

 

Cable

If the installation environment requires a cable that takes heat and low temperature, the minimum demand for the cable is under 20 m with connection Outdoor UTP Cat5E 4Pairs (Water Blocking / UV Resistant).

For longer connections it is recommended to use cable Outdoor UTP Cat6 4Pairs (Water blocking / UV Resistant), similar to it or better.

 

 

Ethernet cable connection with Epec 6000 series unit:

M12 male connector (front)

M12 pin (Ethernet)

M12 pin (Ethernet 2)

RJ45 male pin

T568B  Pair

Color

(according to T568B standard)

RJ45 male connector (front)

6 (rxd1+)

1 (rxd2+)

3 (rxd+)

3

White/green

5 (txd1+)

2 (txd2+)

1 (txd+)

2

White/orange

4 (rxd1-)

7 (rxd2-)

6 (rxd-)

3

Green

8 (txd1-)

3 (txd2-)

2 (txd-)

2

Orange

 

 

 

4

1

Blue

 

 

 

5

1

White/blue

 

 

 

7

4

White/brown

 

 

 

8

4

Brown

 

 

Ethernet cabling for system developers

The following figure describes a cabling example for Ethernet communication between Epec control units and a PC.

Ordering codes for the needed hardware are included in the figure.

 

To check 6000 series unit's IP addresses, use ApplicationLoader (device software). For more information, see Epec Programming & Libraries Manual: Programming > Programming 6000 Series Units > Configuring Ethernet and DNS Settings (available from Epec's Extranet).

 

 

 

 