Power supply pins and limitations

Power supply pins are located in the following pins:

 

Connector pin number

Pin Name

Current / Pin

Note

X1.1

LOGIC GND

 

 

X1.24

Power Supply Logic

 

 

X2.1

Power1 GND

10 A

The maximum sum of GND pin currents should not continuously exceed 20 A.

X2.2

Power1 GND

10 A

X2.24

Power Supply1

10 A

The maximum sum of supply pin currents cannot exceed 14 A.

X2.25

Power Supply1

10 A

X3.1

Power2 GND

10 A

The maximum sum of GND pin currents should not continuously exceed  20 A.

X3.2

Power2 GND

10 A

X3.24

Power Supply2

10 A

The maximum sum of supply pin currents should not continuously exceed 14 A.

X3.25

Power Supply2

10 A

X2.5

+5 V REF

 

 

X3.20

+5 V REF

 

 

X1.8

+10 V REF

 

 

X2.4

+10 V REF

 

 

X3.13

+10 V REF

 

 

 

 

The following table describes which power gives certain pins the currency needed:

 

Connector pin number

Pin Type

Powered by

Current/
voltage

X1.12

PWM/DO/DI/CM

Power 1

2A

X1.22

PWM/DO/DI

Power 1

4A

X1.23

PWM/DO/DI/CM

Power 1

2A

X1.29

PWM/DO/DI

Power 1

2A

X1.30

PWM/DO/DI

Power 1

2A

X1.31

PWM/DO/DI

Power 1

2A

X1.32

PWM/DO/DI

Power 1

2A

X1.33

PWM/DO/DI

Power 1

4A

X1.34

PWM/DO/DI

Power 1

4A

X1.35

PWM/DO/DI

Power 1

4A

X2.13

PWM/DO/DI/CM

Power 1

2A

X2.14

PWM/DO/DI/CM

Power 1

2A

X2.26

DO_GND

Power 1

3A

X2.27

DO_GND

Power 1

3A

X2.34

DO_GND

Power 1

3A

X2.35

DO_GND

Power 1

3A

 

X2.28

PWM/DO/DI/CM

Power 2

2A

X2.29

PWM/DO/DI/CM

Power 2

2A

X2.30

PWM/DO/DI/CM

Power 2

2A

X2.31

PWM/DO/DI/CM

Power 2

2A

X2.32

PWM/DO/DI/CM

Power 2

2A

X2.33

PWM/DO/DI/CM

Power 2

2A

X3.26

PWM/DO/DI/CM

Power 2

2A

X3.27

PWM/DO/DI/CM

Power 2

2A

X3.28

PWM/DO/DI/CM

Power 2

2A

X3.29

PWM/DO/DI/CM

Power 2

2A

X3.30

PWM/DO/DI/CM

Power 2

2A

X3.31

PWM/DO/DI/CM

Power 2

2A

X3.32

PWM/DO/DI/CM

Power 2

2A

X3.33

PWM/DO/DI/CM

Power 2

2A

X3.34

PWM/DO/DI/CM

Power 2

2A

X3.35

PWM/DO/DI/CM

Power 2

2A

 

 

Connector pin number

Current / Pin

Note

X2.3

10 A

The maximum sum of GND pin currents cannot exceed 28 A.

X2.10

10 A

X2.11

10 A

X2.12

10 A

X3.3

10 A

X3.4

10 A

 

 

 

If the Logic power is >43 V, there is a risk that the control unit shuts down.

 

If Power1 or Power2 is > 43 V, the outputs in the group must be disabled.

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

VI

Nominal Input voltage

 

8,3

36

V

PLogic

Logic Power Consumption

No external loads,
Uin = 24V

typ. 2,2

W

ITOT-max

Max Total Current output

Power groups together

 

28

A

IPIN-max

Max through current per pin

Tamb ≤ 85°C

typ. 12,5

A

VI-Load-dump

Max Input transient Voltage level

(Note 1)

97,5

 

V

VI-max

Max Continuous Input Voltage level

Each power group

(Note 2)

-58

60

V

VOVP-Reg

Regulated Overvoltage threshold level

 

typ. 43

V

VOVP-oper.

Operational Overvoltage level

(Note 3,4)

 

50

V

VUVP

Undervoltage threshold level

 

typ. 7,5

V

VRVP

Reverse Voltage Protection level

No extra facilities needed (Note 5)

-58

 

V

Voltage monitoring

VI-range

Nominal Input Voltage measuring range

 

0

55

V

VI-prop

Measuring accuracy
Proportional factor

Calculated

 

+/-1

%

VI-zero

Offset Error

Calculated

 

+/-0,1

%

 

+/-55

mV

 

Note 1: Load dump protection according to ISO7636-2: 2004 pulse 5, Us=+70V

Note 2: Limited functionality when the voltage is higher than the nominal. If the voltage is less than 8,3 V, the control unit is in non-operational state.
Note 3:
This parameter is only related to the logic power input.
Note 4: This parameter is influenced by +10V REF’s load level.
Note 5: 
Nominal voltage level where reverse protection will be activated. Keep in mind the fuse parameters, such as the reaction time.


 

 

 

 