Power Supply Cabling

 

The maximum continuous current per pin is 10 A.

 

The power for sensors, encoders and other equipment should be supplied from the very same unit that the equipment is connected to, to ensure the best performance of the system. No external power (or ground) connections are allowed.

 

In ISOBUS control systems the control unit must be connected to the ISOBUS wire harness' ECU_PWR and ECU_GND pins. Actuator power pins (PWR and GND) cannot be used.

 

 

 

Power supply’s wiring example:

 

 

 

Power supply's wiring:

 

 

 

 

 

 

Emergency Stop

 

In all European Community countries, the emergency stop should be implemented in accordance with standard EN ISO 13850, which complies to the EC Machinery directive 2006/42/EC. In other countries, the emergency stop should be implemented according to local standards and/or to local legislation.