AI/DI_Type116

 

 

Pins 1.14, 1,15, 1.25,1.26 have optimized PT1000 sensor support. When using with PT1000, select range 0-2,5 V for the pin (with Epec MultiTool).

 

 

When configured to current mode, analog inputs can be protected against overvoltage by using 3000AnalogInputProtection programming library. For more information, refer to Epec Programming and Libraries Manual.

 

 

DI

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

VI

Input Voltage measuring range

 

0

5

V

RI

Input Resistance

Pull-up voltage mode (referenced to +5 V)

typ. 2,2

Pull-down voltage mode (referenced to GND)

typ. 84,2

Current mode

typ. 220

Ω

II

Input Current measuring range

 

0

22,7

mA

IE

Input Error

Voltage mode

 

0,18

V

Current mode

 

0,8

mA

BW

Input Low Pass Filter Bandwidth

-3 dB cut-off frequency

typ.41

Hz

CI

Input pin capacitance

 

typ. 47

nF

VI-range

Input voltage range

Voltage mode

(Note 1)

-0,5

33

V

Current mode

(Note 1)

-0,5

15

V

Note 1:  Exceeding the max value might cause damage to input.

 

 

Functional block diagram