AI/DI

 

This pin has a dedicated AI GND pin (X1.18) that is internally connected to the I/O ground and data ground pins.

 

 

Configure the pin to current mode before applying the current signal.

 

A switch will disconnect the measurement circuit if an overvoltage event is detected.

Overvoltage protection mode is indicated with a dedicated signal (DEV_DSC_OVP_STATE_X1_17). The protection mode is active as long as the overvoltage persists.

The protection circuit can be bypassed (the switch will reconnect the measurement circuit) momentarily with a reset signal (DEV_DSC_OVP_RESET_X1_17). The signal is edge activated and the bypass time is fixed.

 

DI

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

VI

Input Voltage measuring range

Voltage mode

0

5

V

 

Overvoltage Detection Threshold

Protection mode not active (Note 5)

typ. 7,2

V

Protection mode active (Note 5)

typ. 5,6

V

 

Scaling factor

Voltage mode (Note 4)

10/11

 

Current mode (Note 4)

10/11

 

VPU

Pull-up voltage

(Note 1)

typ. 5

V

II

Input Current measuring range

Current mode

0

22

mA

RI

Input Resistance

Voltage mode, pull-up resistor not selected (referenced to GND)

typ. 70

kΩ

Voltage mode, pull-up resistor selected (referenced to + 5 V)

typ. 2200

Ω

Current mode (referenced to GND)

typ. 220

Ω

Overvoltage protection mode,

VI > Overvoltage detection threshold

 (referenced to GND)

typ. 9,6

kΩ

BW

Input Low Pass Filter Bandwidth

Voltage mode (Note 3)

typ. 1

kHz

Current mode (Note 3)

typ. 1

kHz

IE

Input Error

Voltage mode

 

0,25

V

Current mode

 

1,1

mA

CI

Input pin capacitance

 

typ. 4,4

nF

VI-range

Input Voltage Range

Voltage mode (Note 2)

-0,5

43

V

Current mode (Note 2)

-0,5

43

V

Note 1: Temperature-dependent.

Note 2:  Exceeding the max value might cause damage to input.

Note 3: 2nd order low pass filter  

Note 4: HW multiplies the measurement by 10/11. The effect is compensated in 6107Int.library (the measurement is multiplied by 11/10), so the measurement is automatically accurate when using Epec programming libraries. For more information about conversions, refer to Epec Programming and Libraries manual.

Note 5: When protection mode is active the measurement circuit is disconnected from the input.

 

 

Functional block diagram