+5V REF (Type041)

The +5V reference supply has two diagnostics checks:

Both can be used to indicate overload and overvoltage situations. The diagnostics are independent from each other.

 

For fastest and most reliable error detection, it is recommended to use both output voltage monitoring and fault-flag diagnostics to detect errors.

 

 

 

OVERLOAD

The diagnostics can detect overcurrent situation. The fault-signal is activated when excessive current is taken from the output. The output current is regulated when internal current limit is reached. The regulation current is always smaller than the limit. Current regulation causes the output voltage to drop with increasing load. This can be detected, using the output voltage monitoring feature, by setting a minimum (low) value limit for the output voltage.

 

With large enough loads, the output is switched temporarily off to protect the output from overheating. This is indicated by the fault-signal.

The fault-signal is deactivated, when the error source is removed by decreasing the load or when the output is turned off.

 

Overheat protection of the +5V REF can cause spurious errors in other analog measurements. Thus it is recommended to turn off the output when fault-signal becomes active.

 

 

 

OVERVOLTAGE

Overvoltage event caused by an external source can be detected by using a combination of the diagnostic features. The fault-signal is activated when pin voltage goes above the fault-signal overvoltage threshold level. If the output voltage monitoring value is 5 V (or more) and the fault-signal is active, it can be determined that an external voltage source is connected to the output pin.

 

The output pins are protected against external voltages, but it is not recommended to connect external voltage sources to these pins.

 

In case of a limit violation the output should be disabled as soon as possible. The control unit can handle short term errors, but long term (e.g. several hours) exposures should be avoided with application/system design. Long term exposure to overvoltage or overload can cause permanent damage to the unit.

 

 

 

Symbol

Parameter

Conditions

Min

Max

Units

 

Nominal voltage monitoring range

 

0

5

V

 

Fault-signal overvoltage threshold

Overvoltage

Typ. 5,2

V

 

Internal Current Limitation

Output On

Typ. 370

mA

 

Fault-signal activation time

Overvoltage / Overload

 

10

ms

Diagnostics

Low

High

Units

 

Recommended voltage monitoring warning level

Output On

4,6

-

V

For additional electrical characteristics refer to section +5V REF_Type041_4.