DO/DI (sinking)_Type074_1

 

Closed circuit loops are  mandatory when using this pin.

Closed circuit loop means that the current from the control unit to the sensor must return to the same control unit, see the figures in section I/O Cabling.

 

Output

 

It is recommended to use the function blocks in DigitalOutputDiagnostics library to protect and diagnose outputs when used as digital outputs. For more information, refer to Epec Programming and Libraries Manual.

 

Input

 

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

RON

On-resistance

Output On

 

50

II

Nominal Input Current

Output On,

VDCLOAD < max VI-range
(Note 1)

0

4

A

Digital status input

RI

Input Resistance

Output Off

 

VIH

Digital status input
High Voltage level

Output Off (Note 2, 3)

2,3

Uin

V

VIL

Digital status input
Low Voltage level

Output Off (Note 3)

-0,5

1

V

CI

Input Capacitance

 

typ. 1

nF

Note 1: Parameter is defined by resistive load.

Note 2: Exceeding the limit values might cause damage to input.

Note 3: No hysteresis. State between voltages 1 V and 2,3 V is unknown.

 

Functional block diagram