PWM/DI/DO_Type073_1

Output (PWM/DO)

 

 

 

 

If you want to use current measuring, you need to connect the other end of the load to the feedback pin.

 

It is recommended to use the function blocks in DigitalOutputDiagnostics library to protect and diagnose outputs when used as digital outputs. For more information, refer to Epec Programming and Libraries Manual.

 

Input (DI)

 

Closed circuit loops are  mandatory when you are using DO or PWM pin as an input.

Closed circuit loop means that the current from the control unit to the sensor must return to the same control unit, see the figures in section I/O Cabling.

 

 

 

Symbol

Parameter

Conditions

Min

Max

Units

RO

Output Resistance

Output On

 

0,1

Ω

IO

Output Current

Output On

0

4

A

Io-lim

Internal current limitation

Output On (Note 2, 3)

typ. 12

A

fPWM

PWM Frequency

(Note 1)

10

3000

Hz

DutyPWM

Duty Cycle

(Note 4, 9)

0 to 100,0

%

ResPWM

PWM Resolution

(Note 1, 8)

0,1

%

Digital status input

RI

Input Resistance

Output Off; Referenced to GND

 

VIH

Input High Voltage

Output Off

(Note 7)

3,5

Uin

V

VIL

Input Low Voltage

Output Off

-0,5

1,5

V

fI

Input frequency

(digital input)

50% duty cycle

(Note 4, 5)

 

1/ 2tC

Hz

tI

Digital Status Input

Pulse Width

(Note 5, 6)

> tC

ms

CI

Input pin capacitance

 

typ. 1

nF

Note 1: PWM capable outputs are divided into groups. All outputs in the same group share the same PWM frequency (default value 10 Hz). The groups are indicated with upper case characters in the pin table's Group column in section .

Note 2: Current limit for short circuit protection to protect cabling and to limit internal power dissipation.

Note 3: When the limit is exceeded, the output voltage circuit starts to limit the current by switching the output voltage. The switching does not effect the application software

Note 4: The duty cycle is defined as the percentage of digital ‘high’ to digital ‘low’ signals present during a PWM period.

Note 5: tC denotes the software cycle time.

Note 6: The pulse width must be greater that the software cycle time. For example with 50/50 pulse ratio, the pulse frequency is 1 / (2*pulse width)

Note 7: Exceeding the max value might cause permanent damage.

Note 8: The PWM resolution is defined as a maximum number of pulses that you can pack into a PWM period.

Note 9: When the frequency increases, the actual duty cycle may be bigger than the value that has been set.

 

 

Functional block diagram