These pins are analog inputs
The pins can be configured either as a current input or as a voltage input.
There is a control signal for selecting:
Voltage mode: High impedance input for signal from 0 to 5 V
Current mode: Low impedance input for signal from 0 to 22 mA
Pins of this kind can be used as e.g. joystick connection when 82,2 kΩ GND (voltage input) is selected.
The input impedance of each pin is controlled by a bit in output memory (%Q)
|
|
When configured to current mode, analog inputs can be protected against overvoltage by using 3000AnalogInputProtection programming library. For more information, refer to Epec Programming and Libraries Manual.
|
These pins can also be used as digital inputs by using an application library.
The pin must be configured to voltage mode when using as digital input
Electrical characteristics
|
Symbol |
Parameter |
Conditions |
Min |
Max |
Units |
|
VI |
Input Voltage measuring range |
|
0 |
5 |
V |
|
RI |
Input Resistance |
Voltage mode (referenced to GND) |
typ. 82,2 |
kΩ |
|
|
Current mode |
typ. 220 |
Ω |
|||
|
II |
Input Current measuring range |
|
0 |
22,7 |
mA |
|
IE |
Input Error |
Voltage mode |
|
0,18 |
V |
|
Current mode |
|
0,8 |
mA |
||
|
BW |
Input Low Pass Filter Bandwidth |
-3 dB cut-off frequency |
typ. 100 |
Hz |
|
|
CI |
Input pin capacitance |
|
typ. 1 |
nF |
|
|
VI-range |
Input voltage range |
Voltage mode (Note 1) |
-0,5 |
33 |
V |
|
Current mode (Note 1) |
-0,5 |
15 |
V |
||
Note 1: Exceeding the max value might cause damage to input.
