Epec 3606 control units are certified according to EMC tests that are described in this section.
The following tables provide a summary of performed EMC tests:
Emission tests according to the test specification EN 61000-6-3
|
Emission test |
Test method |
|
Radiated disturbance |
CISPR 16-2-3 |
|
Conducted disturbance at mains ports |
CISPR 16-2-1 |
Immunity tests according to the test specification EN 61000-6-2
|
Immunity test |
Test method |
|
Electrostatic discharge (ESD) |
EN 61000-4-2 |
|
Radiated radio-frequency electromagnetic field |
EN 61000-4-3 |
|
Electrical fast transients (EFT/B) |
EN 61000-4-4 |
|
Surges |
EN 61000-4-5 |
|
Conducted radio-frequency common mode |
EN 61000-4-6 |
Emission tests according to the E/ECE Regulation No. 10, Revision 4 (2012)
|
Emission test |
Test method |
Conclusion |
|
Measurement of radiated interference field strength in the frequency range 30 – 1000 MHz |
E/ECE Reg. No. 10, Annexes 7 and 8 |
Pass 1) |
|
Measurement of conducted disturbances |
E/ECE Reg. No. 10, Annex 10 |
Pass 2) |
1) Limit values according to the E/ECE Regulation No. 10, Sections 6.5.2 and 6.6.2.
2) Limit values according to the E/ECE Regulation No. 10, section 6.9.1.
Immunity tests according to the E/ECE Regulation No. 10, Revision 4 (2012)
|
Immunity test |
Test method |
Conclusion |
|
Radiated radio-frequency electromagnetic field |
E/ECE Reg. No. 10, Annex 9 |
Pass 1) |
|
Immunity to transient disturbances conducted along supply lines |
E/ECE Reg. No. 10, Annex 10 |
Pass 2)
|
1) The requirements defined in the E/ECE Regulation No. 10, section 6.10
2) The requirements defined in the E/ECE Regulation No. 10, section 6.8.1.
The following tables provide more detailed descriptions about the performed EMC tests:
|
Emission tests according to the E/ECE Regulation No. 10, Revision 4 (2012) |
|||||||||||||||||||||||||||||||||||||||||||||||||
|
Radiated disturbance emission test |
|
||||||||||||||||||||||||||||||||||||||||||||||||
|
Conducted disturbances emission test |
|
||||||||||||||||||||||||||||||||||||||||||||||||
|
Immunity tests according to the E/ECE Regulation No. 10, Revision 4 (2012) |
|||||||||||||||||||||||||||||||||||||||||||||||||
|
Immunity to transient disturbances conducted along supply lines test
|
|
||||||||||||||||||||||||||||||||||||||||||||||||
|
Immunity of ESAs to electromagnetic radiation
|
|
||||||||||||||||||||||||||||||||||||||||||||||||
|
Classification of functional status Class A: All functions of a device/system perform as designed during and after exposure to disturbance.
Class B: All functions of a device/system perform as designed during and after exposure to disturbance. However, one or more of them can go beyond specified tolerance. All functions return automatically to within normal limits after exposure is removed. Memory functions shall remain class A.
Class C: One or more functions of a device/system do not perform as designed during exposure but return automatically to normal operation after exposure is removed.
Class D: One or more functions of a device/system do not perform as designed during exposure and do not return to normal operation until exposure is removed and a device/system is reset by simple “operator/use” action.
Class E: One or more functions of a device/system do not perform as designed during exposure and cannot be returned to operation without repairing the device/system.
|
|||||||||||||||||||||||||||||||||||||||||||||||||
|
EN 61000-6-3 (2007) part6-3: residential, commercial and light industry |
|||||||||
|
Radiated disturbance emission test
|
|
||||||||
|
Conducted disturbance at main ports emission test |
|
||||||||
|
EN 61000-6-2 (2005) |
|||||||||
|
Conducted radio-frequency common mode immunity test |
|
||||||||
|
Radiated radio-frequency electromagnetic field immunity test |
|
||||||||
|
Electrical fast transient (EFT/B) immunity test |
|
||||||||
|
Electrostatic discharge (ESD) immunity test |
|
||||||||
|
Performance criteria for immunity tests
Performance criterion A: The EUT shall continue to operate as intended during and after the test. No degradation of performance is allowed.
Performance criterion B: The EUT shall continue to operate as intended after the test. However, moderate degradation of performance is allowed. No change of actual operating state or loss of memory functions is allowed.
|
|||||||||