Temperature and Voltage Monitoring

This unit’s internal temperature and incoming operating voltage can be read from the PLCopen addresses with the numerical values and resolutions shown in the following table.

 

 

Type

PLCopen address

Precision

Resolution bits

Full reading

Internal Diagnostics

AI(TPCB)

%IW18

±3,5 %

10

 

AI(UR2V5)*

%IW17

±3,5 %

10

5 V

External Diagnostics

AI(Uin)

%IW19

±3,5 %

10

46 V

AI(+5 V REF)

%IW16

±3,5 %

10

5 V

* Internal precision voltage measurement can be used for internal voltage level monitoring.

 

 

Temperature

This control unit has one temperature sensor for monitoring PCB area temperature.

The temperature information is useful for self diagnostic purposes and safety features.

 

Symbol

Parameter

Conditions

Min

Max

Units

TPCB

Nominal PCB Temperature measuring range

 

-40

125

°C

TPCB-err

Temperature Measurement Error

-40 .. +100 °C

 

+/- 6

% (FS)

-55 .. +125 °C

 

+/- 9

% (FS)