PWM/DO/DI_Type037_2

Output

 

If you want to use current measuring, connect the other end of the load to the feedback pin.

 

 

It is recommended to use the function blocks in DigitalOutputDiagnostics library to protect and diagnose outputs when used as digital outputs. For more information, refer to Epec Programming and Libraries Manual.

 

 

Input

 

 

Electrical characteristics

Symbol

Parameter

Conditions

Min

Max

Units

RO

Output Resistance

Output On

 

0,2

Ω

IO

Output Current

Output On

0

3

A

Io-lim

Internal current limitation

Output On (Note 1, 2)

typ. 12

A

fPWM

PWM Frequency

 

10

3000

Hz

DutyPWM

Duty Cycle

(Note 3)

0

100,0

%

ResPWM

PWM Resolution

 

 

 0,1

%

Digital status input

RI

Input Resistance

Output Off; Referenced to Uin

typ. 12

VI-level

Input voltage level

Output Off; Unconnected pin

Uin

V

VIH

Input High Voltage

Output Off

(Note 7)

4,1

Uin

V

VIL

Input Low Voltage

Output Off

-0,5

3,3

V

fI

Input frequency

(digital input)

50% duty cycle

(Note 3, 4)

 

 1/ 2tC

Hz

tI

Digital Status Input

Pulse Width

(Note 4, 5)

> tC

ms

CI

Input pin capacitance

 

typ. 1

nF

Note 1: Current limit for short circuit protection to protect cabling and to limit internal power dissipation.

Note 2: When the limit is exceeded, the output voltage circuit starts to limit the current by switching the output voltage. The switching does not effect the application software

Note 3:  The duty cycle is defined as the percentage of digital ‘high’ to digital ‘low’ signals present during a PWM period.

Note 4:  tC denotes the software cycle time.

Note 5: The pulse width must be greater that the software cycle time. For example with 50/50 pulse ratio, the pulse frequency is 1 / (2*pulse width)

Note 6: Violating this rating may lead to system not recognizing all input state transitions.

Note 7: Exceeding the max value might cause permanent damage.

Functional block diagram