In order that the electromagnetic interference (EMI) would not effect the data transfer, the installation of the cable should be done as close as possible to the body of the machine.
It is recommended to wire the cable under the shelter of mechanical hits if the installation environment makes it possible.
The cable must be installed as far away as possible from other cables with high power.
The maximum length of a connection is meters. |
This Ethernet connection is based on 10BASE-T/100BASE-T connection where two twisted pairs are used.
connector is not a standard connecting format and to get the best operation reliability the following issues should be considered in circuitry and installation; type of the used cable, connecting the cable and the installation method.
If the installation environment requires a cable that takes heat and low temperature, the minimum demand for the cable is under 20 m with connection Outdoor UTP Cat5E 4Pairs (Water Blocking / UV Resistant).
For longer connections it is recommended to use cable Outdoor UTP Cat6 4Pairs (Water blocking / UV Resistant), similar to it or better.
(SFTP = Shielded Foiled Twisted Pair)
(FTP = Foiled Twisted Pair)
(STP = Shielded Twisted Pair)
(UTP= Unshielded Twisted Pair)
Ethernet cable connection with Epec unit:
RJ45 male pin |
T568B Pair |
Color (according to T568B standard) |
RJ45 male connector (front) |
3 (rxd+) |
3 |
White/green |
![]() |
1 (txd+) |
2 |
White/orange |
|
6 (rxd-) |
3 |
Green |
|
2 (txd-) |
2 |
Orange |
|
4 |
1 |
Blue |
|
5 |
1 |
White/blue |
|
7 |
4 |
White/brown |
|
8 |
4 |
Brown |