LED Indicator

 

 

The LED indicator light is situated on the top side of the 3606 according to the following figure:

 

 

Some of the states must be implemented by using EXT programming library. For more information about EXT programming library, refer to Epec programming and libraries manual.

 

The LED has green and red indicators and they indicate different operating conditions according to the following table:

 

 

LED State

Green LED

Red LED

Implemented in device firmware

Implement by using EXT programming library

Explanation

Off

-

-

X

 

No supply voltage or an application stop state after a watchdog reset.

Default Application or No User Application

Blinks 5 times/second

-

X

 

Firmware is running, no PLCopen application or application download in progress

ApplicationOk

Blinks 2 times/ second

-

X

 

Application is running and the system is OK

Application Stopped or initializing

LED is constantly on

-

X

X

Stopped / Starting / Initializing

Firmware: LED is continuously on while application is stopped.

EXT Library: LED is continuously on also during the initialization: starting from power on until the application is running and the I/O / CAN initializations are done.

FatalError

-

LED is constantly on

X

 

Control unit boot-up failed or a critical firmware error while running.

ApplicationError

-

Blinks 2 times/ second

 

X

External PLCopen library controls, for example when output controlling is disabled, so called safe state.

IOError

-

Blinks 5 times/second

 

X

External PLCopen library controls, for example when system is OK but there is short circuit in one of the outputs or other similar error is active (depends of application)

Update

Blinks alternately with red LED

Blinks alternately with green LED

X

 

After firmware update boot-up, during the installation phase, red and green LEDs are flashed alternately.

 

 

 

 