Configuring I/O

The input and output behavior configurations are done on the I/O tab. On the left side, the I/O pins are listed according to the Connector and Pin. When a pin is selected, the possible configurations are shown on the right.

 

 

The pin mode can be selected either directly on the I/O pin list's Modes column or from the configurations on the right. The Modes list show the possible modes for the pin and the selection works as a toggle button.

The pin Variable Name can be given either directly on the I/O pin list's Variable Name column or from the configurations on the right.

The Comment for the pin will be shown in CODESYS as a comment text on the global variable list IO.

 

To export I/O into a PDF or Excel file, press SHIFT + ALT + S.

 

For more information about the pins' electrical characteristics, refer to the device's technical manual.

 

 

 

Connector 1000 shows configurations that are common for several pins.

 

 

For example, Pull-up and Range can be configured for the following pins, shown in the pictures below.  

 

 

 

The following table describes the possible I/O pin configurations:

 

Property

Description

Pull-up

Pull-up enable selection for the pin (Disabled/To +10V)

Debounce delay

Defines the time how often the digital input status can change (TRUE/FALSE).

See also the figures below this table.

Debounce filtering

Defines the debounce filtering type of digital input.

Debounce fast (Filters_DebounceDI_Fast FB): DI status do not change more frequently than given debounce delay.

Debounce (Filters_DebounceDI FB): DI status do not change before DI value has been stable for a  debounce delay time.

See also the figures below this table.

Threshold

When the voltage level exceeds the threshold limit, the digital input state is set to true.

See also the figures below this table.

Hysteresis

Allowed hysteresis of threshold in percent. The digital input state is false, when the voltage falls below the limit calculated by subtracting hysteresis from the threshold.

See also the figures below this table.

AI to DI conversion method

Select the threshold definition: fixed threshold in runtime or adjustable threshold and hysteresis

Overcurrent

Overcurrent limit for pins that have current measurement feature. When the current measurement value is over the defined time (200ms) greater than the parameter value, the global boolean variable (PWFM_OVERCURRENT_...) is set on and the output or the channel is set to 0. The channel is disabled until the output is set off.

Default frequency

Frequency selection for the used channel in Hz.

AI mode

Signal area selection mA/V

Filter samples

The amount of samples that is used to calculate AI mean value

Filter method

Selects the filtering method (runtime / PLCopen library)

Coil resistance

The resistance of the used load

Correction gain

Correction gain is used to fix the difference between approximated ratio and actual ratio which must be used to achieve defined current demand.

Diagnostic delay

Defines the delay for overcurrent

Edge select

The selection determines whether both or one edge is counted

Channel pair (B)

The pin that is configured for channel two

Reset channel (R)

The pin that is configured to reset the pulse input count

Frequency ratio

Frequency ratio selection

Range configuration

Used voltage range

Minimum voltage

Diagnostic minimum voltage of the analog input pin. If the voltage goes under the minimum limit, the measurement is set to 0.

Maximum voltage

Diagnostic maximum voltage for the analog input pin. If the measured voltage exceeds this maximum limit, the error bit is activated and the measurement value is set to 0.

 

NOTE: If the maximum voltage value is set too high, the limit may never be exceeded and no error will be generated.

Minimum current

Diagnostic minimum current of the analog input pin. If the current goes under the minimum limit, the measurement is set to 0.

Maximum current

Diagnostic maximum current for the analog input pin. If the measured current exceeds this maximum limit, the error bit is activated and the measurement value is set to 0.

 

NOTE: If the maximum current value is set too high, the limit may never be exceeded and no error will be generated.

Safety related

When selected, the pin is regarded as a safety related pin in the project. This is also indicated by a yellow background in the list of I/O pins.

 

 

The following figure describes how threshold and hysteresis affect the signal state:

 

 

The following figure describes the debounce delay of debounce fast filtering type:

 

 

The following figure describes the debounce delay of debounce filtering type:

 

 

Epec Oy reserves all rights for improvements without prior notice.

 

Source file topic200007.htm

Last updated 26-Aug-2026