Create CODESYS project

 

 

To create a CODESYS project:

  1. Right-click the unit and select Create CODESYS project or click on the ribbon

  2. MultiTool opens the CODESYS template project, imports the configurations to it and saves the project with a control unit name. Note that CODESYS tries to open the previously saved project and for this reason may show error dialogs. Error dialogs need to be acknowledged before importing can be done.

  3. Add Main POU to the project in CODESYS.

  4. Build and login.

 

For more information on creating a CODESYS project, refer to topics Quick Start Guide and Updating MultiTool Configurations to CODESYS Project.

 

 

Read-only files, such as libraries from version control, are not overwritten in System Export.

 

 

Vanhat kappaleet:

Code Template Structure

MultiTool Creator automatically creates a code template for CODESYS project when Create CODESYS Project is selected. The code template contains all variable definitions and initialization needed for programming the device.

This topic briefly introduces the code template parts:

 

PLC_PRG

The PLC_PRG is the main POU of a CODESYS project. MultiTool Creator automatically generates PLC_PRG for the CODESYS project and it will always be overwritten when changes done in MultiTool Creator are imported to the CODESYS project. For this reason, the user application code should never be added to PLC_PRG.

 

For the user application code, create a new POU called Main. This will be the entry point of the user application. The code template automatically calls the Main program in the PLC_PRG's action Application. It is not overwritten by MultiTool Creator. If the Main POU is missing from the application, the CODESYS build command gives an error. The code template in CODESYS 3.5 projects includes a Main POU that is made with ST language. To make the Main POU with another programming language, delete the Main POU and make a new one.

 

The CODESYS 3.5 Device tree in the following image includes all project objects on the same view:

 

 

CODESYS 2.3 code template is divided to the POUs, Data types and Resources tabs.

 

 

 

The PLC_PRG is divided into four actions: Init, Epec_In, Application and Epec_Out.

 

The Init action is run on each program cycle until all initializations are done. The initialization phase is divided into several steps to minimize the needed time of each program cycle. After the initialization phase, Epec_In, Application and Epec_Out actions are run on each program cycle.

 

 

PLC_PRGs action

Sub-action

Description

Init

Init_Entry

Reads system parameters

Contains call of the user POU

Init_Flash

Initializes non volatile memory

Init_IO

I/O initialization functions

Init_Bus

Initializes CANVXD library instance for each CAN

Init_Protocols_CANx (*)

CAN protocol initializations for each CAN bus, including CANopen and SAE J1939

Init_Events

Initializations for Events

Init_Exit

Initializes the identity object (1018h)

Epec_In

IO_Filter

Filters I/O pin raw values

Diag

CAN bus diagnostics

HWD_Diagnostic instance call

G_SystemOk  variable handling

LED handling

Bus

Updates CAN buffers

Other

Reserved for future use

Application

Only contains call for the user application Main

Epec_Out

Other

All functions that are needed to run at the end of the program cycle, such as

- analogue input protection

- parameter saving

- resetting the control device if needed (NMT reset)

IOHandleOutputs(**)

Copies data from variables which are used in application for the IO to variables defined in description file. This copying sets actual IO to wanted state.

 

* CAN bus consecutive numbering, typically 1=CAN1, 2=CAN2 etc.

** only in CODESYS 3.5 version

 

(Implicit) Globals

MultiTool Creator generates global variable and function block instance definitions to (Implicit) Globals lists. These variables and instances can be used, for example, for diagnosing CAN bus and hardware. Code template calls these function blocks automatically. Code template global definitions can be found from

  1. the Resources tab in CODESYS 2.3 or

  2. the Device tree in CODESYS 3.5 (CodeTemplate > Globals)

 

Variable definitions are divided into several global lists, defined in the table below.

 

Global variable list

Description

Code_Template_constants(**)

Constant definitions

Code_Template_Globals

All variable definitions and function block instances needed in code template, such as init phase booleans

- CANopen instance and array definitions

Variables that might be needed in application, such as G_SystemOk boolean, HWD_Measurements instance and limit definitions.

ERRORS

Error variables

EVENTS

Event source addresses and data initialization.

IO

I/O pin variables that are needed when developing an application

IO_RAW

Non scaled raw values of I/O pins.

Not needed in normal use, since the code template filters and scales the values before writing them to I/O variables.

IO_CONFIG

I/O pin configurations, such as

- input pull up configurations

- pulse input range selections

- input mode selections (mA/V)

- output mode selections

IO_INTERNAL

Internal I/O

- Scaled and filtered voltage and temperature measurements

- Reference output enable variables

- Overcurrent error statuses for AI pins

J1939 (optional)

J1939 library instance

Global variable definitions

- J1939_CANx(*) variable for each CAN bus that uses J1939

- Variable type is a structure defined in the application

ODx_VAR (*)

OD variables whose variable type is RAM, retain or retain persistent.

ODx_PAR (*)

OD variables whose variable type is Parameter

ODx_CANI (*)

Variables of received PDOs (RPDO)

ODx_CANO (*)

Variables of transmitted PDOs (TPDO)

SYSTEM

Project information, such as device type, serial number, firmware version, 5050 FW error log.

HMI

HMI related variables, such as 2040 soft button states

slave Configurations (folder)

This folder includes a global variable list for each slave device

 

* OD's consecutive numbering, typically 1=CAN1, 2=CAN2 etc.

** only in CODESYS 3.5 version

 

 

Data (Unit) Types

MultiTool Creator creates structures and/or enumerations for

 

In CODESYS 2.3, structures and enumerations can be found from the Data types tab.

 

 

In CODESYS 3.5, Data unit types (DUT) can be found from the Device tree. Enumerations are placed into the Enums and structures into the Structs folder.

 

 

 

 

Variable Prefixes

MultiTool Creator generates global variable lists to CODESYS project. These variable lists include variables for I/O pins, CAN communication and hardware measurement data.

The variable names include prefixes to provide more information about variable type or for what purpose it is used.

 

Global Variable List

Prefix

Description

Code_Template_Globals

G_

Global variables that the code template uses

Code_Template_Constants (**)

G_

Global constant definitions

CANx_EVENTS

E_

Application specific events

ERRORS (**)

ERR_FLAG_IO_AI_OVER_CURRENT_

Error flag that is set to TRUE in case of over current for AI pin in mA mode.

IO

AI_

AI input's filtered A/D converter (ADC) value

AIPU_

AI input's pull-up voltage's filtered ADC value

DI_

Debounce filtered DI value

DO_

DO output state

DOS_

DO output status (DI) information

PWM_RATIO_

PWM pulse ratio

FB_

Low side current measurement's filtered ADC value

PWFM_CM_

PWFM output's high side current measurement value

PWFM_CR_

Current request to firmware's current controller

PWFM_STEPREQ_

Step motor's step count request

PWFM_STEPLEFT_

Remaining steps for step motor's

PWFM_STEPRESET_

Step motor's step count request reset, stops the pulse generation

PWFM_OVERCURRENT_

PWFM output's overcurrent alarm

PWFM_FORCECCRATIO_

Current controller's forced pulse ratio, bypasses the current controller and uses value in variable PWFM_RATIO_

PWFM_UPDCCPAR_

Recalculates current controller parameters

PWFM_OPENCIRCUIT_

Current controller's broken/open circuit alarm

PWFM_RATIO_

PWFM output's pulse ratio

PWFM_FREQ_

PWFM output's frequency

AI_ERRORS

AI converter's errors bit mask

FI_

Pulse input frequency (channel A if 2 channels)

PI_

Pulse input's counter value (channel A if 2 channels)

PW_

Pulse input's pulse width

OVP_RESET_

Control flag for overvoltage protection reset

OVP_STATE_

Status flag for overvoltage protection

FET_ST_

Status of the FET.

IO_RAW

AI_RAW_

AI input's latest unfiltered ADC value

AI_ARR_

Buffer of AI input unfiltered ADC samples

AI_ARR_INDEX_

Index of latest AI input sample in AI_ARR_ buffer

AI_ARR_TS_

Buffer/table of AI samples' timestamps

AIPU_RAW_

AI input's pull-up voltage's latest unfiltered ADC value

AIPU_ARR_

Buffer of AI input pull-up voltage's unfiltered ADC samples

DI_RAW_

DI input's unfiltered value

FB_RAW_

Latest unfiltered value for low side current measurement

IO_CONFIG

AI_SET_mA_

AI input's configuration into mA input

AI_SET_PU_

AI input's pull-up configuration

PWFM_SET_PU_

PWFM output's pull-up configuration

PWFM_ERROR_INIT_

PWFM init error (0 = no error)

PWFM_MODE_

PWFM output's active mode (read only)

PI_ERROR_

Pulse input initialization error code

PI_SET_PU_

Pulse input's pull-up configuration

PI_SET_RANGE_

Pulse input voltage range configuration

IO_INTERNAL

POWER_

Power switch control

ODx_CANI (*)

CANI_

Variable received in PDO message (from a device not included in the MultiTool project)

CANI_UnitName_

Variable received in PDO message (from a device included in the MultiTool project) UnitName depends on the device name that the message is received from

ODx_CANO (*)

CANO_

Variable transmitted in PDO message

ODx_PAR (*)

PAR_

OD variable stored in non-volatile memory, so called application parameter

ODx_VAR (*)

OD_

- parameter stored in volatile memory (RAM parameter) and  defined in OD

- retain and persistent variable defined in OD

- all the other OD variables that do not belong any of the other ODx groups mentioned above

 

x* CAN bus consecutive numbering, typically 1=CAN1, 2=CAN2 etc.

x** only in CODESYS 3.5 version

 

Fixed Variable Names

 

Some of the variables MultiTool Creator creates for the CODESYS project have fixed names. These variables provide information about hardware and are not user configurable.

The following table lists fixed reserved variable names:

 

Global variable list

Variable name

Description

ERRORS

ERR_FLAG_OUTPUT_ST_INIT

Boolean variable for diagnostics that indicates a voltage in a pin when the device is started up and the pin is defined to DO (digital output) mode

ERR_FLAG_IO_INIT

Boolean variable for indicating error(s) in I/O initialization functions when the device is started up

IO

AI_ERRORS

Error flag field of the AD conversions

IO_INTERNAL

AI_SupplyLogic

Filtered ADC value of Logic supply voltage

SUPPLY_Logic

Filtered Logic supply voltage value [10 mv]

AI_SupplyPower1

Filtered ADC value of Power1 supply voltage

SUPPLY_Power1

Filtered Power1 supply voltage value [10 mv]

AI_ Power1Pin

Power1 supply voltage (filtered unscaled value)

SUPPLY_ Power1Pin

Filtered Power1 supply voltage value [10 mv]

AI_SupplyPower2

Filtered ADC value of Power2 supply voltage

SUPPLY_Power2

Filtered Power2 supply voltage value [10 mv]

SUPPLY_Power2Pin

Filtered ADC value of Power2 operating voltage

AI_ Power2Pin

Power2 supply voltage (filtered unscaled value)

AI_Ref5V

Filtered ADC value of 5 V reference voltage output

REF_5V

Filtered 5 V reference voltage output value [10 mv]

AI_Ref10V

Filtered ADC value of 10 V reference voltage output

REF_10V

Filtered 10 V reference voltage output value [10 mv]

AI_InternADCReference

Filtered ADC value of AD converter's reference voltage

REF_InternalADC

Filtered AD converter's reference voltage value [10 mv]

AI_10VPullUpSupply

Filtered ADC value of 10 V pull-ups’ supply voltage

REF_10VPullUpSupply

Filtered 10 V pull-ups’ supply voltage value [10 mv]

AI_CoreTemperature

Filtered core temperature ADC value

TEMP_Core

Device's internal core temperature [Celsius]

AI_ PCBTemperature

Filtered ADC value of device's internal PCB temperature

TEMP_PCB

Device's internal PCB temperature [Celsius]

REF_OUT_5V_Enable

Enables the 5 V reference outputs

REF_OUT_5V_OK

Status of 5 V REF outputs. TRUE = output OK.

REF_OUT_10V_Enable

Enables the 10 V reference outputs

POWER_1_Enable

Enables the outputs that are supplied by Power1 supply voltage

POWER_2_Enable

Enables the outputs that are supplied by Power2 supply voltage

SYSTEM_FWErrorLog

Pointer to 5050 firmware error log (Read only).

AI_SupplyVolt

Filtered ADC value of device supply voltage

SUPPLY_Volt

Filtered voltage value of device supply voltage [10 mv]

SUPPLY_Cur

Supply current [mA]

AI_Ref12V

Filtered ADC value of 12 V reference voltage output

REF_12V

Filtered voltage value of 12 V reference voltage output [10 mv]

RS485_H_ST_CHN0

H-bus status of RS485 channel 0

RS485_H_AI_CHN0

H-bus AI measurement of RS485 channel 0

RS485_L_ST_CHN0

L-bus status of RS485 channel 0

RS485_L_AI_CHN0

L-bus AI measurement of RS485 channel 0

POWER_CONX_ENABLE

Boolean variable which is used to connect power to connector X.

CAN_CONX_CANX_ENABLE

Enables CAN bus X in connector X.

REF_OUT_5V_FAULT

Fault flag for 5 V reference output. TRUE means overload situation.

AUX_OUT_FAULT

Fault flag for auxiliary output

OVP_OCCURED

OVP (Overvoltage Protection) situation has occurred at least once.

OVP_STATE

Current OVP (Overvoltage Protection) state

OVP_RESET

Control flag for OVP (Overvoltage Protection)  reset

UPS_Volt

UPS voltage level [mV]

PWM_BacklightPWMValue

Backlight PWM value

SENSOR_LightSensorValue

Light sensor value

CLK_ClockSpeed

Microcontroller clock speed (MHz)

IO_RAW

AI_ARR_INDEX

Index of the latest sample in AI_ARR_ buffers of analog inputs and measurements.

AI_ARR_TS

Buffer of AI conversion samples' timestamps

AI_RAW_SupplyLogic

Latest unfiltered ADC value of Logic’s supply voltage

AI_ARR_SupplyLogic

Buffer of unfiltered ADC samples of Logic’s supply voltage

AI_RAW_SupplyPower1

Latest unfiltered ADC value of Power1 supply voltage

AI_ARR_SupplyPower1

Buffer of unfiltered ADC samples of Power1 supply voltage

AI_RAW_ Power1Pin

Latest unfiltered ADC value of Power1's operating voltage

AI_ARR_ Power1Pin

Buffer of unfiltered ADC samples of Power1 operating voltage

AI_RAW_SupplyPower2

Latest unfiltered ADC value of Power2 supply voltage

AI_ARR_SupplyPower2

Buffer of unfiltered ADC samples of Power2 supply voltage

AI_RAW_Ref5V

Latest unfiltered ADC value of 5V reference voltage output

AI_ARR_Ref5V

Buffer of unfiltered ADC samples of 5V reference voltage output

AI_RAW_Ref10V

Latest unfiltered ADC value of 10V reference voltage output

AI_ARR_Ref10V

Buffer of unfiltered ADC samples of 10V reference voltage output

AI_RAW_InternADCReference

Latest unfiltered ADC value of internal AD converter reference voltage

AI_ARR_ InternADCReference

Buffer of unfiltered ADC samples of internal AD converter reference voltage

AI_RAW_10VPullUpSupply

Latest unfiltered ADC value of internal 10 V pull-ups’ supply voltage

AI_ARR_ 10VPullUpSupply

Buffer of unfiltered ADC samples of internal 10 V pull-ups’ supply voltage

AI_RAW_CoreTemperature

Latest unfiltered ADC value of  device's internal core temperature

AI_ARR_ CoreTemperature

Buffer of unfiltered ADC samples of device's internal core temperature

AI_RAW_PCBTemperature

Latest unfiltered ADC value of device's internal PCB temperature

AI_ARR_ PCBTemperature

Buffer of unfiltered ADC samples of device's internal PCB temperature

SYSTEM

SYSTEM_NVRAM_Use_2040

NVRAM usage

SYSTEM_FW_Version

Firmware version info

SYSTEM_VendorId

Vendor ID which is read from the firmware

SYSTEM_ProjectInfo

CODESYS application project info

SYSTEM_ControlUnitType

Device's type. 32-bit number

SYSTEM_ControlUnitRevision

Device's hardware revision. 32-bit number

SYSTEM_SerialNumber

Device's serial number. 32-bit number

 

 

Epec Oy reserves all rights for improvements without prior notice.

 