Supported platforms: CODESYS 3.5
This FB calibrates linear resistance sensor value i_InputValue (mV) to SI unit (°C, bar, km/h, kg, etc…).
To operate correctly it is required that sensor operates linearly.
Calibrated output value and alarm/warning limits are the same unit than input variables i_OutputMin and i_OutputMax.
Enabled alarm/warning limits are sanity checked: i_HighAlarmLimit > i_HighWarningLimit > i_LowWarningLimit > i_LowAlarmLimit. Deviation cause parameter error.
The output values o_CalibratedValue and o_Resistance are set to zero if i_Enable is FALSE, or parameter error is diagnosed.
All internal FB initializations are done on the rising edge of i_Enable.
All errors are reset on the rising edge of i_Enable.
|
|
This FB can only be used with a linear resistance sensor connected to a voltage input. |
|
|
The FB uses internally - S_VoltageToResistance FB from SafeConversion library. - S_ValueDiagnostic FB from SafeDataValidation library. |
|
|
Following parameters are taken into use at the rising edge of i_Enable: - i_ResistanceHigh - i_ResistanceLow - i_OutputMin - i_OutputMax - i_InternalPullUpResistance - i_InternalPullDownResistance - i_HighAlarmLimit - i_HighWarningLimit - i_LowWarningLimit - i_LowAlarmLimit - i_EnableHighAlarm - i_EnableHighWarning - i_EnableLowWarning - i_EnableLowAlarm - i_DiagnosticDelay + Any initialized event code. |
|
Input variable name |
Data type |
Range |
Description |
|
i_Enable |
BOOL |
FALSE/TRUE |
Enable operation. |
|
i_InputVoltage |
DINT |
- |
Measured voltage (mV) of sensor. |
|
i_ReferenceVoltage |
DINT |
- |
Measured supply voltage (mV) of sensor. |
|
i_ResistanceHigh |
DINT |
- |
Maximum resistance value of the sensor (Ohm). |
|
i_ResistanceLow |
DINT |
- |
Minimum resistance value of the sensor (Ohm). |
|
i_OutputMin |
DINT |
- |
Minimum SI-unit value of the sensor, corresponds to i_ResistanceLow. |
|
i_OutputMax |
DINT |
- |
Maximum SI-unit value of the sensor, corresponds to i_ResistanceHigh. |
|
i_InternalPullUpResistance |
EPEC_HW. PULL_UP_RESISTANCE |
ENUM |
Internal pull-up resistance of AI input (Ohm). |
|
i_InternalPullDownResistance |
EPEC_HW. PULL_DOWN_RESISTANCE |
ENUM |
Internal pull-down resistance of AI input (Ohm). |
|
i_HighAlarmLimit |
DINT |
- |
High alarm limit for calibrated value. |
|
i_HighWarningLimit |
DINT |
- |
High warning limit for calibrated value. |
|
i_LowWarningLimit |
DINT |
- |
Low warning limit for calibrated value. |
|
i_LowAlarmLimit |
DINT |
- |
Low alarm limit for calibrated value. |
|
i_EnableHighAlarm |
BOOL |
FALSE/TRUE |
High value alarm in use. |
|
i_EnableHighWarning |
BOOL |
FALSE/TRUE |
High value warning in use. |
|
i_EnableLowWarning |
BOOL |
FALSE/TRUE |
Low value warning in use. |
|
i_EnableLowAlarm |
BOOL |
FALSE/TRUE |
Low value alarm in use. |
|
i_DiagnosticDelay |
UINT |
- |
Diagnostic delay for alarms and warnings (ms). |
|
Output variable name |
Data type |
Range |
Description |
|
o_CalibratedValue |
DINT |
- |
Calibrated SI-unit value. |
|
o_Resistance |
DINT |
- |
Calculated resistance of the sensor. |
|
o_HighAlarm |
BOOL |
FALSE/TRUE |
Calibrated value high alarm status. |
|
o_HighWarning |
BOOL |
FALSE/TRUE |
Calibrated value high warning status. |
|
o_LowWarning |
BOOL |
FALSE/TRUE |
Calibrated value low warning status. |
|
o_LowAlarm |
BOOL |
FALSE/TRUE |
Calibrated value low alarm status. |
|
o_ParameterError |
BOOL |
FALSE/TRUE |
Error in input parameters. |
This optional method sets pointer for event code.
|
Input variable name |
Data type |
Description |
|
i_Enable |
BOOL |
Enable operation. |
|
i_pEventCode |
POINTER TO EPEC_DITF.EventCode |
Pointer to signal event code value provided by the application. |
|
|
Pull-up to 5 V is selected in MultiTool Creator's AI configuration when using resistance sensors.
|
|
|
Example implementation is made with EC44 unit which has pull-up measurement available. For products which does not have AI pull-up measurement (e.g. SL84), use hardcoded 5000 mV value for voltage to resistance conversion's S_i_RefVoltage.
// SL84 does not have pull-up measurements, assume 5V pullup S_TEMP_PULLUP_VOLTAGE: SAFEDINT := DINT#5000; |
-