Supported platforms: CODESYS 3.5 SAFETY
A safety project's application has a safety task and a non-safety task. Due to lower priority, the non-safety task may be interrupted at any time by the safety task.
Interruption can occur when the non-safety task is updating the non-safe related data. To prevent data corruption:
a data interlock implementation needs to be used to ensure data integrity
non-safety data needs to be used only in non-safety related task
This section describes how a data interlock can be used between non-safety and safety related application parts. The data can consist of, for example,
CANopen PDO variables
SAE J1939
application internal variables
CANopen and SAE J1939 protocols are all executed in non-safety code.
This topic does not apply to SRDO variables. SRDO variables are already interlocked in code template. See also, How to send and receive variables over SRDO
|
The following example uses two structures:
data from non-safety related application to safety related application
data from safety related application to non-safety related application
The main idea is that the non-safety related task sets the structure Interlock boolean to TRUE when the data is used (read/written). Non-safety related task resets the Interlock boolean to FALSE when reading/writing is done. The safety related task does not use the data when the Interlock boolean is TRUE.
NewData boolean is set to TRUE in that task which updates the data. The task which uses the data resets the NewData to FALSE.
Declaration // Safety task updates data and read by non-safety task TYPE AppDataFromSafe : STRUCT Interlock: BOOL; // Set TRUE by non-safety task when data read in progress NewData:BOOL; // Set TRUE by safety task when new data is available (copying complete)
SafeInternalVar1: BYTE; // Internal variable from non-safety PRG to safety PRG TransmitData1: DWORD; // Data from safety PRG to non-safety TPDO SpeedRequest: WORD; // Variable from safety PRG to non-safety J1939 transmit PGN END_STRUCT END_TYPE
|
Declaration
// Non-safety task updates data and read by safety task TYPE AppDataToSafe : STRUCT Interlock: BOOL; // Set TRUE by non-safety task when data write in progress NewData:BOOL; // Set TRUE by non-safety task when new data is available (copying complete)
NonSafeInternalVar1: BYTE; // Internal variable from non-safety PRG to safety PRG ReceivedData1: WORD; // RPDO variable to safety PRG ActualSpeed: WORD; // Received J1939 variable to safety PRG END_STRUCT END_TYPE
|
Declarations for GVL G_AppData
{attribute 'qualified_only'} {attribute 'location' := '16#800'} // Non-safety data to allow both tasks to write in data VAR_GLOBAL DataToSafeTask: AppDataToSafe; DataFromSafeTask: AppDataFromSafe; END_VAR
|
Declarations VAR // to safety task non_safe_var1: BYTE; actual_speed: WORD;
// from safety task var1_from_safe_task: BYTE; speed_request: WORD; END_VAR
|
Update received non-safety related variables which are needed in safety related task.
The received data is updated for safety related task only when NewData is FALSE. This is needed to prevent lock being always on when the safety related task is executed.
Non-safe PRG |
IF NOT G_AppData.DataToSafeTask.NewData THEN // non-safety task indicates that data copy in progress G_AppData.DataToSafeTask.Interlock := TRUE;
// copy data G_AppData.DataToSafeTask.NonSafeInternalVar1 := non_safe_var1; G_AppData.DataToSafeTask.ReceivedData1 := G_CAN1_RPDO.ReceivedData; G_AppData.DataToSafeTask.ActualSpeed := actual_speed;
// indicate new data available G_AppData.DataToSafeTask.NewData := TRUE; // Remove data lock G_AppData.DataToSafeTask.Interlock := FALSE; END_IF |
Application code:
Non-safe PRG |
non_safe_var1 := non_safe_var1 + 1; G_J1939.CAN2.Out.Engine.TSC1_EngRqedSpeed_SpeedLimit := speed_request * 8; actual_speed := G_J1939.CAN2.In.Engine.EEC1_EngSpeed / WORD#8; |
Reading data from the safety related task and update transmit variables, for example, TPDO messages.
The data is read only if NewData is TRUE. This prevents situation where Interlock would always be true during the safety related task.
Non-safe PRG |
IF G_AppData.DataFromSafeTask.NewData THEN // non-safety task indicates that data copy in progress G_AppData.DataFromSafeTask.Interlock := TRUE;
// copy data var1_from_safe_task := G_AppData.DataFromSafeTask.SafeInternalVar1; G_CAN1_TPDO.TransmitData1 := G_AppData.DataFromSafeTask.TransmitData1; speed_request := G_AppData.DataFromSafeTask.SpeedRequest;
// non-safety task sets new data to false when data is read and removes lock G_AppData.DataFromSafeTask.NewData := FALSE; G_AppData.DataFromSafeTask.Interlock := FALSE; END_IF |
Declarations |
VAR // fron non-safety task var1_from_nonsafe_task: BYTE; received_data1: WORD; actual_speed: WORD;
// to non-safety task safetask_var1: BYTE; speed_request: WORD; transmit_data1: DWORD; END_VAR |
Read received non-safety variables which are needed in the safety related task.
The data is read only when NewData is TRUE and Interlock is FALSE.
Safe PRG: |
IF G_AppData.DataToSafeTask.NewData AND NOT G_AppData.DataToSafeTask.Interlock THEN // copy data var1_from_nonsafe_task := G_AppData.DataToSafeTask.NonSafeInternalVar1; received_data1 := G_AppData.DataToSafeTask.ReceivedData1; actual_speed := G_AppData.DataToSafeTask.ActualSpeed;
// Set new data to FALSE which allows non-safe task to update new data G_AppData.DataToSafeTask.NewData := FALSE; END_IF |
Application code:
Safe PRG: |
safetask_var1 := safetask_var1 + 1; speed_request := 1000; transmit_data1 := transmit_data1 + 1; |
Write safety related task variables for non-safety related task. The data is written only if Interlock is FALSE.
Safe PRG: |
IF NOT G_AppData.DataFromSafeTask.Interlock THEN
// copy data G_AppData.DataFromSafeTask.SafeInternalVar1 := safetask_var1; G_AppData.DataFromSafeTask.TransmitData1 := transmit_data1; G_AppData.DataFromSafeTask.SpeedRequest := speed_request;
// safety task sets new data to TRUE when data has been written G_AppData.DataFromSafeTask.NewData := TRUE; END_IF |
SC52 Safety Manual > Safety Related Application Development > Application Interface > Code Template > Tasks in Code Template. The manual is available from Epec's extranet.