Supported platforms: CODESYS 3.5 SAFETY, CODESYS 3.5 SP19 SAFETY

 

NVMem (PRG)

Description

This program reads and writes OD parameters and user values from/to non-volatile memory and application variables.

All parameters and user values are read once from NV-memory during initialization.

 

SSeriesHardware version 1.0.0.5SSeriesHardware version 1.0.0.5

Following table defines the NV-memory layout when using default library parameters.

 

Usage

Start address

Size

OD parameters

At the start of unit nv-memory

Total NVMem size – user value size * 2

User values

NVMem size – 512 bytes

256 bytes (*)

User values backup

NVMem size – 256 bytes

256 bytes (*)

* Note that usable user values size is reduced by parameter handler header size.

 

SSeriesHardware version 1.1.3.0SSeriesHardware version 1.1.3.0

Following tables define the NV-memory layout used by the library. Parameter area sizes can be adjusted with library parameters.

 

If total area size is less than actual NVRAM size, then the NVRAM area after library areas is left unused.

Application can use the unused area with NVRAMCOPY (FB) (EXT).

 

Library includes optional OD parameter backup area.

Application can take OD backup in use with library parameter G_PARAM_BACKUP_IN_USE which is used by code template.

 

Following areas are used if OD parameter backup is not in use:

 

G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

* Note that usable user values size is reduced by parameter handler header size.

Following areas are used if OD parameter backup is in use:

 

2x G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

OD parameters backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE +

G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

* Note that usable user values size is reduced by parameter handler header size.

 

SSeriesHardware version 1.1.4.0SSeriesHardware version 1.1.4.0

DM2 log is read/write from/to non-volatile memory if valid DM2 parameters given in NVMem.Init method.

 

The following tables define the NV-memory layout used by the library. Parameter area sizes can be adjusted from MultiTool Creator.

 

If the total area size is less than the actual NVRAM size, then the NVRAM area after library areas is left unused.

Application can use the unused area with NVRAMCOPY (FB) (EXT).

 

Library includes optional OD parameter backup area.

 

The following areas are used if OD parameter backup is not in use:

 

G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE+ G_DM2_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

DM2 log

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + 2*G_USER_VALUE_AREA_MAX_SIZE

G_DM2_AREA_MAX_SIZE (bytes)

* Note that usable user values size is reduced by parameter handler header size.

The following areas are used if OD parameter backup is in use:

 

2x G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE+ G_DM2_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

OD parameters backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE +

G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

DM2 log

Start of nv-memory + 2*G_PARAM_AREA_MAX_SIZE +
2*G_USER_VALUE_AREA_MAX_SIZE

G_DM2_AREA_MAX_SIZE (bytes)

* Note that usable user values size is reduced by parameter handler header size.

 

SSeriesHardware version 1.1.5.0SSeriesHardware version 1.1.5.0

Machine type area and DM2 log are read/write from/to non-volatile memory if valid input parameters given in NVMem.Init method.

 

The following tables define the NV-memory layout used by the library. Parameter area sizes can be adjusted from MultiTool Creator.

 

If the total area size is less than the actual NVRAM size, then the NVRAM area after library areas is left unused.

Application can use the unused area with NVRAMCOPY (FB) (EXT).

 

Library includes optional OD parameter backup area.

 

The following areas are used if OD parameter backup is not in use:

 

G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE+ G_DM2_AREA_MAX_SIZE + G_MACHINE_TYPE_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

DM2 log

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + 2*G_USER_VALUE_AREA_MAX_SIZE

G_DM2_AREA_MAX_SIZE (bytes)

Machine type area

Start of nv-memory + G_PARAM_AREA_MAX_SIZE + 2*G_USER_VALUE_AREA_MAX_SIZE+

G_DM2_AREA_MAX_SIZE (bytes)

G_MACHINE_TYPE_AREA_MAX_SIZE 

(bytes)

* Note that usable user values size is reduced by parameter handler header size.

The following areas are used if OD parameter backup is in use:

 

2x G_PARAM_AREA_MAX_SIZE + 2x G_USER_VALUE_AREA_MAX_SIZE+ G_DM2_AREA_MAX_SIZE + G_MACHINE_TYPE_AREA_MAX_SIZE shall not exceed control unit’s actual NVRAM size reported by firmware. Init error is given if required size is too large.

 

Usage

Start address

Size

OD parameters

At the start address of unit’s nv-memory

G_PARAM_AREA_MAX_SIZE (bytes)

OD parameters backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE

G_PARAM_AREA_MAX_SIZE (bytes)

User values

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

User values backup

Start of nv-memory + G_PARAM_AREA_MAX_SIZE +

G_PARAM_AREA_MAX_SIZE +

G_USER_VALUE_AREA_MAX_SIZE

G_USER_VALUE_AREA_MAX_SIZE (bytes)  (*)

DM2 log

Start of nv-memory + 2*G_PARAM_AREA_MAX_SIZE +
2*G_USER_VALUE_AREA_MAX_SIZE

G_DM2_AREA_MAX_SIZE (bytes)

Machine type area

Start of nv-memory + 2*G_PARAM_AREA_MAX_SIZE +
2*G_USER_VALUE_AREA_MAX_SIZE + G_DM2_AREA_MAX_SIZE

G_MACHINE_TYPE_AREA_MAX_SIZE (bytes)

* Note that usable user values size is reduced by parameter handler header size.

Limitations

This program is automatically added to code template when using MultiTool Creator.

 

Error during nv-memory read will set init to ready but it will activate init error and disable parameter writing during normal operation.

 

Safety parameters can be saved only once and then reboot is required.

When safety parameter authentication status is TRUE, then OD parameter image is disabled after parameter save is executed.

 

All memory areas use Parameter Handler library for handling the images between RAM and NVRAM. Parameter handler also checks the image integrity.

 

User values data is reset to application default values if both NVRAM memory areas become corrupted.

Default values are also used when NVRAM is empty (new unit).

 

 

Init (METHOD) SseriesHardware version 1.1.3.0 and olderInit (METHOD) SseriesHardware version 1.1.3.0 and older

Init method is used to initialize the necessary parameters for program.

 

OD parameter area and user value area in RAM are given to PRG as initialization parameters.

If an area is not given, the corresponding functionality is disabled. This is not considered as an error.

User value area and struct sizes are checked that max size is not exceeded.

This method sets the parameters to PRG for operation.

 

Init method is not considered ready until OD parameter and user values are read from non-volatile memory.

Error during nv-memory read will set init to ready but it will activate init error and disable parameter writing during normal operation.

 

Input variable name

Data type

Description

i_NVMemoryIndex

UDINT

Index number of used non-volatile memory.

i_pParameters

POINTER TO BYTE

Pointer to OD parameters image

i_ParameterAreaSize

UDINT

OD parameter image size.

i_pParameterHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to OD parameter handler FB.

i_pUserValuesArea

POINTER TO BYTE

Pointer to user value image.

i_UserValueAreaSize

UDINT

User value image size.

i_pUserValueHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to user values handler FB.

i_pUserValues

POINTER TO BYTE

Pointer to user parameter struct

i_UserValuesSize

UDINT

User value struct size

i_ParHandlerKeyword

UDINT

Keyword for both handlers.

 

Output variable name

Data type

Description

o_InitReady

BOOL

Init has been executed

 

 

Init (METHOD) SseriesHardware version 1.1.4.0 and newerInit (METHOD) SseriesHardware version 1.1.4.0 and newer

Init method is used to initialize the necessary parameters for program.

 

OD parameter area, user value area and DM2 in RAM are given to PRG as initialization parameters. If an area is not given, the corresponding functionality is disabled. This is not considered as an error. User value area and struct sizes are checked that max size is not exceeded. This method sets the parameters to PRG for operation.

Init method is not considered ready until OD parameter, user values and DM2 log (if exists) are read from non-volatile memory. Error during nv-memory read will set init to ready but it will activate init error and disable parameter writing during normal operation.
 
 

Input variable name

Data type

Description

i_NVMemoryIndex

UDINT

Index number of used non-volatile memory.

i_pParameters

POINTER TO BYTE

Pointer to OD parameters image

i_ParameterAreaSize

UDINT

OD parameter image size.

i_pParameterHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to OD parameter handler FB.

i_pUserValuesArea

POINTER TO BYTE

Pointer to user value image.

i_UserValueAreaSize

UDINT

User value image size.

i_pUserValueHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to user values handler FB.

i_pUserValues

POINTER TO BYTE

Pointer to user parameter struct

i_UserValuesSize

UDINT

User value struct size

i_pDM2Area

POINTER TO BYTE

Pointer to J1939 DM2 log image.

i_DM2AreaSize

UDINT

J1939 DM2 log area size.

i_pDM2Handler

POINTER TO EPEC_PH.ParameterHandler

Pointer to J1939 DM2 log area handler FB.

i_ParHandlerKeyword

UDINT

Keyword for both handlers.

 

Output variable name

Data type

Description

o_InitReady

BOOL

Init has been executed

 

 

Init (METHOD) SseriesHardware version 1.1.5.0 and newerInit (METHOD) SseriesHardware version 1.1.5.0 and newer

Init method is used to initialize the necessary parameters for program.

 

OD parameter area, user value area, DM2 area and machine type area in RAM are given to PRG as initialization parameters. If an area is not given, the corresponding functionality is disabled. This is not considered as an error. User value area and struct sizes are checked that max size is not exceeded. This method sets the parameters to PRG for operation.

Init method is not considered ready until OD parameter, user values and DM2 log (if exists) are read from non-volatile memory. Error during nv-memory read will set init to ready but it will activate init error and disable parameter writing during normal operation.
 
 

Input variable name

Data type

Description

i_NVMemoryIndex

UDINT

Index number of used non-volatile memory.

i_pParameters

POINTER TO BYTE

Pointer to OD parameters image

i_ParameterAreaSize

UDINT

OD parameter image size.

i_pParameterHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to OD parameter handler FB.

i_pUserValuesArea

POINTER TO BYTE

Pointer to user value image.

i_UserValueAreaSize

UDINT

User value image size.

i_pUserValueHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to user values handler FB.

i_pUserValues

POINTER TO BYTE

Pointer to user parameter struct

i_UserValuesSize

UDINT

User value struct size

i_pDM2Area

POINTER TO BYTE

Pointer to J1939 DM2 log image.

i_DM2AreaSize

UDINT

J1939 DM2 log area size.

i_pDM2Handler

POINTER TO EPEC_PH.ParameterHandler

Pointer to J1939 DM2 log area handler FB.

i_pMachineTypeArea

POINTER TO BYTE

Pointer to machine type area image.

i_MachineTypeAreaSize

UDINT

Machine type area size.

i_pMachineTypeHandler

POINTER TO EPEC_PH.ParameterHandler

Pointer to machine type area handler FB.

i_ParHandlerKeyword

UDINT

Keyword for both handlers.

 

Output variable name

Data type

Description

o_InitReady

BOOL

Init has been executed

 

 

SetParameterBackup (METHOD)SetParameterBackup (METHOD)

I

Requires library version 1.1.3.0 or later.

Code template executes this method automatically.

 

Method is used to enable OD parameter backup functionality.

 

If i_Enable is TRUE, the OD parameter backup is in use.

By default OD parameter backup is not in use.

 

Method shall be called before Init method.

 

Input variable name

Data type

Description

i_Enable

BOOL

TRUE = OD parameter backup in use

 

 

IsBackupLoaded (METHOD)IsBackupLoaded (METHOD)

Requires library version 1.1.3.0 or later.

Code template executes this method automatically.

 

Method is used to check if backup image has been loaded during initialization.

 

Outputs return TRUE if corresponding primary image is corrupted and valid backup image has been taken in use.

 

Output variable name

Data type

Description

o_ParameterBackupLoaded

BOOL

Valid OD parameter backup has been taken in use because primary image is corrupt. Output is FALSE if primary image is in use or both images are corrupt.

o_UserValueBackupLoaded

BOOL

Valid user value backup has been taken in use because primary image is corrupt. Output is FALSE if primary image is in use or both images are corrupt.

 

 

 

 

Operation

SseriesHardware version 1.1.3.0 and olderSseriesHardware version 1.1.3.0 and older


Writing new values to NV-memory is triggered by rising edge of input parameters i_WriteParameters and i_WriteUserValues.


Inputs

Input variable name

Data type

Description

i_WriteParameters

BOOL

Trigger OD parameters’ writing sequence.

i_WriteUserValues

BOOL

Trigger user values’ writing sequence.

i_Authentication

BOOL

Safety parameter authentication status.

Outputs

Output variable name

Data type

Description

o_InitError

BOOL

Init not called before calling the main PRG.

o_InputError

BOOL

Size of an area given without pointer to the area or user parameter size too large

o_ParameterError

EPEC_PH.ParamHandlerStatus

Error returned by OD parameter handler.

o_UserValueError

EPEC_PH.ParamHandlerStatus

Error returned by user value parameter handler.

o_NVMemError

EPEC_SYSTEM.SYSTEM_ERROR_CODES

Error returned by low-level NV-memory function.

o_ParSaveBusy

BOOL

Saving OD parameters to NV-memory.

o_ParSaveDone

BOOL

OD parameters saved to NV-memory successfully.

o_ParSaveError

BOOL

Error occurred in saving OD parameters to NV-memory.


 

SseriesHardware version 1.1.4.0 and newerSseriesHardware version 1.1.4.0 and newer

 

Writing new values to NV-memory is triggered by rising edge of input parameters i_WriteParameters and i_WriteUserValues. Writing DM2 log to NV-memory is triggered by setting input i_WriteDM2 to TRUE.

 

Inputs

Input variable name

Data type

Description

i_WriteParameters

BOOL

Trigger OD parameters’ writing sequence.

i_WriteUserValues

BOOL

Trigger user values’ writing sequence.

i_WriteDM2

BOOL

Trigger DM2 writing sequence

i_Authentication

BOOL

Safety parameter authentication status.

Outputs

Output variable name

Data type

Description

o_InitError

BOOL

Init not called before calling the main PRG.

o_InputError

BOOL

Size of an area given without pointer to the area or user parameter size too large

o_ParameterError

EPEC_PH.ParamHandlerStatus

Error returned by OD parameter handler.

o_UserValueError

EPEC_PH.ParamHandlerStatus

Error returned by user value parameter handler.

o_DM2Error

EPEC_PH.ParamHandlerStatus

Error returned by DM2 parameter handler.

o_NVMemError

EPEC_SYSTEM.SYSTEM_ERROR_CODES

Error returned by low-level NV-memory function.

o_ParSaveBusy

BOOL

Saving OD parameters to NV-memory.

o_ParSaveDone

BOOL

OD parameters saved to NV-memory successfully.

o_ParSaveError

BOOL

Error occurred in saving OD parameters to NV-memory.

 

 

SseriesHardware version 1.1.5.0 and newerSseriesHardware version 1.1.5.0 and newer

 

Writing new values to NV-memory is triggered by rising edge of input parameters i_WriteParameters and i_WriteUserValues. Writing DM2 log or machine type area to NV-memory is triggered by setting input i_WriteDM2 or i_WriteMachineType to TRUE.

 

Inputs

Input variable name

Data type

Description

i_WriteParameters

BOOL

Trigger OD parameters’ writing sequence.

i_WriteUserValues

BOOL

Trigger user values’ writing sequence.

i_WriteDM2

BOOL

Trigger DM2 writing sequence

i_WriteMachineType

BOOL

Trigger machine type writing sequence.

i_Authentication

BOOL

Safety parameter authentication status.

Outputs

Output variable name

Data type

Description

o_InitError

BOOL

Init not called before calling the main PRG.

o_InputError

BOOL

Size of an area given without pointer to the area or user parameter size too large

o_ParameterError

EPEC_PH.ParamHandlerStatus

Error returned by OD parameter handler.

o_UserValueError

EPEC_PH.ParamHandlerStatus

Error returned by user value parameter handler.

o_DM2Error

EPEC_PH.ParamHandlerStatus

Error returned by DM2 parameter handler.

o_MachineTypeError

EPEC_PH.ParamHandlerStatus

Error returned by machine types parameter handler.

o_NVMemError

EPEC_SYSTEM.SYSTEM_ERROR_CODES

Error returned by low-level NV-memory function.

o_ParSaveBusy

BOOL

Saving OD parameters to NV-memory.

o_ParSaveDone

BOOL

OD parameters saved to NV-memory successfully.

o_ParSaveError

BOOL

Error occurred in saving OD parameters to NV-memory.

 

 

Example code

This program is automatically added to code template when using MultiTool Creator.

See also

 

 

 

 

 

Source file topic100541.htm

Last updated 26-Aug-2026