Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY
The function block reads and adjusts the given parameter value and writes it to control unit.
The function block can be used with the parameter CSV file (see also Parameters_ReadCSV).
When the function block is called and i_Enable is set to TRUE, the parameter value is read from the control unit.
This is also done, when i_NodeID, i_Index, i_SubIndex or i_StartBit changes.
Also rising edge of the i_Update input forces reading of current value from the control unit.
When a parameter value is changed, it will be written to the control unit.
If the changed parameter value exceeds i_Min or i_Max, the value is limited to minimum or maximum value.
POU can also adjust unit’s own parameters. Own node-id is read from used CANopen device.
When i_NodeID = unit’s node-id then unit's own OD parameters are adjusted.
Setting i_Enable to FALSE disables all parameter read and write functionality.
The file location in the unit for 6505 and 6510 is /opt/Project/PlcLogic. In the units 6107, 6200, 6807 and 6112 the location is /opt/user/userapp. |
Read and write permissions for parameters according to user levels are handled by application. |
Function block does not determine if adjusted parameter is safety or non-safety parameter. For safety parameter adjustment sequence, see How to adjust safety parameters |
From library version 4.1.2.0, if start bit is defined to a parameter in CSV file, the Parameters_Edit FB handles the parameter as BOOL. The OD data is however, is as defined in CSV file (i.e. BYTE, WORD or DWORD).
|
Input variable name |
Data type |
Range |
Description |
i_Enable |
BOOL |
|
Parameter read/write is disabled if enable is set to FALSE |
i_pDevice |
POINTER TO EPEC_CANopen.Device |
≠ 0 |
Used CANopen device (e.g. ADR(G_CANopen_CAN1.Device)) |
i_pValue |
POINTER TO CAA.PVOID |
≠ 0 |
Pointer to parameter value |
i_NodeID |
BYTE |
1..127 |
Node ID of the control unit |
i_Index |
WORD |
CiA 301 |
SDO object |
i_SubIndex |
BYTE |
|
SDO object sub index |
i_StartBit |
BYTE |
|
Bit number |
i_DataType |
CSVType |
|
Parameter data type enumeration |
i_Min |
DINT |
Depends on data type |
Minimum limit for parameter value |
i_Max |
DINT |
Depends on data type |
Maximum limit for parameter value |
i_Update |
BOOL |
|
Rising edge of i_Update forces reading of current value |
i_Timeout |
TIME |
Time out for the SDO request-response pair. Transfer is aborted if the response is not received during the time out time. |
|
i_pValueReal |
POINTER TO CAA.PVOID |
(≠ 0 if REAL datatype) |
Pointer to parameter value of REAL datatype. |
i_MinReal |
REAL |
Minimum limit for parameter value of REAL datatype. |
|
i_MaxReal |
REAL |
|
Maximum limit for parameter value of REAL datatype. |
Output variable name |
Data type |
Range |
Description |
o_ParameterValue |
DINT |
|
Actual parameter value at target unit. Last SDO read or written value. |
o_State |
Parameters_EditState |
see enumeration |
Current state |
o_Error |
Parameters_EditError |
see enumeration
|
Error code |
o_AbortCode |
DWORD |
Abort code |
|
o_RealTypeParameter |
BOOL |
|
TRUE = Parameter type is REAL. |
Following example adjusts parameter value for selected parameter index.
Selected parameter is determined in application / GUI.
Code template definitions: |
|
/// CAN device Device: EPEC_CANopen.Device; |
Code template definitions: |
|
///Number of parameters in network G_NUMBER_OF_PARAMETERS_NETWORK1: INT := 91;
|
Code template definitions: |
|
///Parameter CSV configuration parameters G_NETWORK1_Parameters_CSVData: ARRAY[1..G_NUMBER_OF_PARAMETERS_NETWORK1] OF EPEC_PAR.CSVData;
|
Definitions: |
|
// Struct contains own variables for integer and real parameters. There is no need for struct if only integer //parameters are used.
TYPE ParameterValues : STRUCT ParameterValueDint: DINT; ParameterValueReal: REAL; END_STRUCT END_TYPE |
Definitions: |
|
// Array where current values are stored for UI G_ParameterValues: ARRAY[1..G_NUMBER_OF_PARAMETERS_NETWORK1] OF ParameterValues;
// DINT array can be used if only integer parameters are used // G_ParameterValues: ARRAY[1..G_NUMBER_OF_PARAMETERS_NETWORK1] OF DINT; |
Definitions: |
|
parameterEdit: EPEC_PAR.Parameters_Edit; parameterCsvData: EPEC_PAR.CSVData; pParameterValue: POINTER TO DINT; pParameterValueReal: POINTER TO REAL; |
Init: |
|
pParameterValue := ADR(G_ParameterValues[10].ParameterValueDint); // Current integer parameter value pParameterValueReal := ADR(G_ParameterValues[10].ParameterValueReal); //Current real parameter value parameterCsvData := G_NETWORK1_Parameters_CSVData[10]; // Selected parameter csv row |
Following code example assumes that parameter csv has been read using Parameters_ReadCSV
Parameter value adjustment is activated when current parameter value is changed.
Code: |
|
parameterEdit( i_Enable := TRUE, i_pDevice := ADR(G_CANopen_CAN1.Device), // From code template i_pValue := pParameterValue, i_NodeID := parameterCsvData.Node, i_Index := parameterCsvData.Index, i_SubIndex := parameterCsvData.SubIndex, i_StartBit := parameterCsvData.StartBit, i_DataType := parameterCsvData.ParameterType, i_Min := parameterCsvData.LowLimit, i_Max := parameterCsvData.HighLimit, i_Update := TRUE, i_Timeout := T#1S, i_pValueReal := pParameterValueReal, i_MinReal := parameterCsvData.LowLimitReal, i_MaxReal := parameterCsvData.HighLimitReal
);
IF parameterEdit.o_Error <> EPEC_PAR.Parameters_EditError.NoError THEN ; // Application specific error handling ELSIF parameterEdit.o_State = EPEC_PAR.Parameters_EditState.Idle THEN ; // Parameter adjustment not active END_IF |
Source file topic100519.htm