S_DOValveEcoControlAndDiagnostics (FB)

Description

This function block is for controlling DO valves more economic with PWM signal to reduce unnecessary current consumption and heating of valve and control unit.

 

The output diagnostic is done using:

Initialization

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

A parameter error is diagnosed if:

  • Init is not called before the main FB call OR

  • i_pEventCode = 0 OR

  • S_i_BrokenCircuitCurrentLimit >= S_i_OverCurrentLimit OR

  • S_i_BrokenCircuitCurrentLimit < 0 OR

  • S_i_DiagnosticDelay > G_DO_MAX_DIAG_DELAY OR

  • S_i_ReducedControlRatio > 1000 ‰

 

The G_DO_MAX_DIAG_DELAY constant is the hardware specific maximum value for diagnostic delay.

Initialization parameters

Parameter

Data type

Unit

Range

Description

S_i_ReducedControlDelay

SAFEUINT

ms

-

Delay time when PWM control is reduced to given ratio after rising edge of S_i_DOControl.

S_i_ReducedControlRatio

SAFEDINT

0 - 1000

Ratio that PWM control is reduced after delay.

S_i_BrokenCircuitCurrentLimit

SAFEDINT

mA

>= 0

Limit for undercurrent diagnosis.

S_i_OverCurrentLimit

SAFEDINT

mA

> 0

Limit for overcurrent diagnosis.

S_i_DiagnosticDelay

SAFEUINT

ms

0 - G_DO_MAX_ DIAG_DELAY

Delay time for diagnostics.

i_pEventCode

POINTER TO EventCode

-

≠ 0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

Operation

The output o_PWMRatio follows the input S_i_DOControl if:

 

When S_i_DOControl is FALSE, the PWM ratio is set to 0%.

On the rising edge of S_i_DOControl is FALSE, the PWM ratio is set to 100%.

When time of S_i_ReducedControlDelay has elapsed from the rising edge of S_i_DOControl, the output PWM ratio is reduced to S_i_ReducedControlRatio value.

 

From the library version 2 (SP19), the output o_PWMRatio is scaled to HW specific resolution using G_PWM_OUT_MAX_VALUE constant.

 

 

When S_i_DOControl is TRUE, the output o_PWMRatio is set to 0 after given diagnostic delay time S_i_DiagnosticDelay

 

When S_i_DOControl is FALSE and i_Enable is TRUE, the external voltage error is diagnosed after given diagnostic delay time S_i_DiagnosticDelay if i_DOStatus is TRUE.

 

The output o_PWMRatio is set to 0‰ immediately if i_Enable is FALSE, or i_OverCurrentProtectionStatus is TRUE.

 

Version 1 (SP10) specific inputs and outputsVersion 1 (SP10) specific inputs and outputs


Parameter error during normal operation is diagnosed if i_OutputCurrent is out of range.


Inputs


Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation

S_i_DOControl

SAFEBOOL

-

-

DO control request

i_OutputCurrent

DWORD

mA

0 – 2147483647

Measured current value of DO pin

i_OverCurrentProtectionStatus

BOOL

-

-

Overcurrent protection status of firmware

i_DOStatus

BOOL

-

-

Output digital status input

Outputs

Output variable name

Data type

Unit

Range

Description

o_PWMRatio

DWORD

0 - 1000

PWM ratio of DO after diagnostics

o_Status

Status

-

-

Status of output value. See Status struct.


Version 2 (SP19) specific inputs and outputsVersion 2 (SP19) specific inputs and outputs


Inputs


Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation

S_i_DOControl

SAFEBOOL

-

-

DO control request

i_OutputCurrent

DINT

mA

-

Measured current value of DO pin

i_OverCurrentProtectionStatus

BOOL

-

-

Overcurrent protection status of firmware

i_DOStatus

BOOL

-

-

Output digital status input

Outputs

Output variable name

Data type

Unit

Range

Description

o_PWMRatio

DWORD

HW specific

0 - G_PWM_OUT

_MAX_VALUE

PWM ratio of DO after diagnostics

o_Status

Status

-

-

Status of output value. See Status struct.


 

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

o_PWMRatio

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

i_Enable TRUE

AND

parameter error AND

 i_pEventCode valid

0‰

FALSE

ParameterError

DO_CONTROL _ECO

PARAMETER_ERROR

i_Enable TRUE

AND

init parameter error AND
i_pEventCode NULL

0‰

FALSE

ParameterError

-

-

i_Enable rises AND

 parameters ok AND

S_i_DOControl TRUE

0‰

FALSE

StartupError

DO_CONTROL

_ECO

STARTUP_ERROR

i_Enable rises

AND

 init parameters ok AND

input valid

See operation chapter

TRUE

-

NO_FUNC

NO_ERROR

i_Enable TRUE AND

init parameters ok AND

o_PWMRatio > 0 AND

S_i_OutputCurrent < S_i_BrokenCircuitCurrentLimit

0‰

FALSE

BrokenCircuit

DO_CONTROL

_ECO

INPUT_TOO_LOW

i_Enable TRUE AND

parameters ok AND

S_i_OutputCurrent > S_i_OverCurrentLimit

0‰

FALSE

OverCurrent

DO_CONTROL

 _ECO

INPUT_TOO_HIGH

i_Enable TRUE AND

parameters ok AND

i_OverCurrentProtectionStatus TRUE

0‰

FALSE

OverCurrent

DO_CONTROL

 _ECO

INPUT_TOO_HIGH

i_Enable TRUE AND

init parameters ok AND

S_i_DOControl FALSE AND

i_DOStatus = TRUE

0‰

FALSE

External

Voltage

DO_CONTROL

 _ECO

INPUT_TOO_HIGH

 

 

Example code

Used I/O variables must be mapped to I/O-interface.

 

I/O variables and configuration are provided by MultiTool Creator code template.

See also How to control DO & DO ECO

 

IO variables:

 

 

X1_32_CurrentFeedback: DWORD; // DWORD mA   Current feedback

X1_32_PWM_Ratio: DWORD;       // DWORD 0,1% PWM ratio

X1_32_Overcurrent: BOOL;     // BOOL OC status from firmware (Status flags bit 2)

X1_32_DOS: BOOL;             // BOOL output's digital input status

 

 

Safety Definitions:

Result: EPEC_SYSTEM.SYSTEM_ERROR_CODES:= EPEC_SYSTEM.SYSTEM_ERROR_CODES.FW_ERR_OK;

 

PIN_1_32_DO_ECO: EPEC_SHWD.S_DOValveEcoControlAndDiagnostics;

PIN_1_32_DO_Status: EPEC_SHWD.Status;

PIN_1_32_DO_Control: BOOL := FALSE;

PIN_1_32_DO_EC: EPEC_DITF.EventCode;

 

Safety Init:

 

(* Set IO driver to configuration state *)

IF EPEC_SYSTEM.SYSTEM_ERROR_CODES.FW_ERR_OK = Result THEN

    Result := EPEC_IODRV.IoDrvSetState(i_State:=EPEC_IODRV.IoDrvStates.IODRV_STATE_CONFIGURATION);

END_IF

 

(* Configure pin X1-32 to PWM/DO *)

IF EPEC_SYSTEM.SYSTEM_ERROR_CODES.FW_ERR_OK = Result THEN

    Result := EPEC_IODRV.IoDrvPWMSetMode(

        EPEC_HW.IO_Channels.PIN_1_32_PWFM,

        EPEC_IODRV.IoDrvModes.IODRV_MODE_PWM_DIRECT

    );

END_IF

 

(* Set IO driver to run state *)

EPEC_IODRV.IoDrvSetState(EPEC_IODRV.IoDrvStates.IODRV_STATE_RUN);

 

(* Init control POU *)

 

PIN_1_32_DO_EC.DeviceID := BYTE#1;

PIN_1_32_DO_EC.ChannelID := BYTE#32;

PIN_1_32_DO_EC.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC;

PIN_1_32_DO_EC.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;

 

PIN_1_32_DO.Init(

    S_i_ReducedControlDelay := UINT#100, // Reduced current after 100 ms

    S_i_ReducedControlRatio := DINT#300, // Reduced current ratio 30,0%

    S_i_BrokenCircuitCurrentLimit := DINT#30, Under current 30 mA

    S_i_OverCurrentLimit := DINT#300, // Over current 300 mA

    S_i_DiagnosticDelay := EPEC_HW.Constants.G_DIGITAL_OUTPUT_DIAGNOSTIC_DELAY,

    i_pEventCode := ADR(PIN_1_32_DO_EC)

);

 

 

Safety Code:

 

PIN_1_32_DO_ECO(

    i_Enable := TRUE,

    S_i_DOControl := PIN_1_32_DO_Control,

    i_OutputCurrent := X1_32_CurrentFeedback,

    i_OverCurrentProtectionStatus := X1_32_Overcurrent,

    i_DOStatus:=X1_32_DOS,

    o_PWMRatio => X1_32_PWM_Ratio,

    o_Status => PIN_1_32_DO_Status

);

 

 

See also

 

 

 

 

Source file topic100440.htm

Last updated 21-Feb-2025