Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY

 

S_AIOverCurrentProtection (FB)

Description

This function block is used for protection of a current mode input from over current.

 

Library versions up to 1.3.2.7Library versions up to 1.3.2.7

Initialization

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

A parameter error is diagnosed if:

  • Init is not called before the main FB call OR

  • i_pEventCode = 0  

 

Initialization parameters

Parameter

Data type

Unit

Range

Description

i_pEventCode

POINTER TO EventCode

-

≠0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

Operation

The block sets o_Status.OutputValid state TRUE if:

• The control is enabled, i.e. i_Enable is TRUE and

• No fault (including initialization) has been diagnosed

 

If the diagnosed AI pin is set to operate in current mode, and S_i_Current value is over G_AI_OVERCURRENT_LIMIT continuously over G_AI_OVERCURRENT_DIAG_DELAY time, then

• The diagnostic statuses o_Status.OutputValid is set FALSE, o_Status.OverCurrent error is set TRUE and the corresponding EventID is set to i_pEventCode.

 

If S_i_Current input value is under 0 when i_Enable is TRUE, then

• Immediately the diagnostic statuses o_Status.OutputValid is set FALSE, o_Status.ParameterError error is set TRUE and the corresponding EventID is set to i_pEventCode.

 

The application must set the pin to voltage mode with FW-provided function.

 

Inputs

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation

S_i_Current

SAFEDINT

uA

>=0

Measured current of input

Outputs

Output variable name

Data type

Range

Description

o_Status

Status

-

Status of output value. See Status struct.

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

i_Enable TRUE AND

i_pEventCode valid AND

  S_i_Current < 0

FALSE

ParameterError

AI_OC_PROTECTION

PARAMETER_ERROR

i_Enable TRUE AND
i_pEventCode NULL

FALSE

ParameterError

-

-

i_Enable rises AND

i_pEventCode valid AND

S_i_Current <= G_AI_OVERCURRENT_LIMIT

TRUE

-

NO_FUNC

NO_ERROR

i_Enable TRUE AND

i_pEventCode valid AND

S_i_Current > G_AI_OVERCURRENT_LIMIT

FALSE

OverCurrent

AI_OC_PROTECTION

INPUT_TOO_HIGH

 

Example code

When enabling IO configuration on-the-fly, the firmware turns the safety switch off.

 

S_AIOverCurrentProtection FB is included for current inputs in Multitool Creator code template.

 

Safety Definitions:

 

Result: EPEC_SYSTEM.SYSTEM_ERROR_CODES:= EPEC_SYSTEM.SYSTEM_ERROR_CODES.FW_ERR_OK;

 

PIN_1_03_OC: EPEC_SHWD.S_AIOverCurrentProtection;

PIN_1_03_OC_Status: EPEC_SHWD.Status;

PIN_1_03_OC_EC: EPEC_DITF.EventCode;

 

 

 

Safety Init:

 

PIN_1_03_OC_EC.DeviceID := BYTE#1;

PIN_1_03_OC_EC.ChannelID := BYTE#3;

PIN_1_03_OC_EC.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC;

PIN_1_03_OC_EC.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;

 

PIN_1_03_OC.Init(

    i_pEventCode := ADR(PIN_1_03_OC_EC)

);

 

 

Safety Code:

 

PIN_1_03_OC(

    i_Enable := TRUE,

    S_i_Current := PIN_1_03_Current,   (* Mapped to pin current feedback in io_interface *)

    o_Status => PIN_1_03_OC_Status

);

 

(* Pin overcurrent -> set to voltage mode *)

IF PIN_1_03_OC_Status.OverCurrent THEN

    Result := EPEC_IODRV.IoDrvDOSetConfig(EPEC_HW.IO_Channels.PIN_1_03_DO_TYPE_V_mA,FALSE);

END_IF

 

 

 

 

See also:

 

 

 

 

Library versions 1.4.0.0 or laterLibrary versions 1.4.0.0 or later

Initialization

Init method is used to initialize the necessary static calculation parameters for the function block instance.

The method shall be called at least once before the actual function block can be called, i.e. at the application initialization phase.

The method checks the validity of input parameters. However, none of the function block outputs are affected by the initialization.

 

A parameter error is diagnosed if:

  • Init is not called before the main FB call OR

  • i_pEventCode = 0  

 

Initialization parameters

Parameter

Data type

Unit

Range

Description

i_pEventCode

POINTER TO EventCode

-

≠0

Pointer to application variable which is type EventCode.

 

Initialization method return value

TRUE: All initialization parameters ok.

FALSE: Error in initialization parameter(s).

 

Operation

The input value i_ADCValue is always written to output o_ADCValue.

 

The block sets o_Status.OutputValid state TRUE if:

• The control is enabled, i.e. i_Enable is TRUE and

• No fault (including initialization) has been diagnosed

 

If the diagnosed AI pin is set to operate in current mode, and i_ADCValue value is at hardware specific AD_MAXIMUM continuously over G_AI_OVERCURRENT_DIAG_DELAY time, then

• The diagnostic statuses o_Status.OutputValid is set FALSE, o_Status.OverCurrent error is set TRUE and the corresponding EventID is set to i_pEventCode.

 

 

The application must set the pin to voltage mode with FW-provided function.

 

Inputs

Input variable name

Data type

Unit

Range

Description

i_Enable

BOOL

-

-

Enable POU operation.

i_ADCValue

DWORD

-

-

Raw AD converter value.

Outputs

Output variable name

Data type

Range

Description

o_ADCValue

DWORD

-

Raw AD converter value.

o_Status

Status

-

Status of output value. See Status struct.

Error diagnostic

See Diagnostic Interface library description of error status and event code functionality.

 

Conditions

o_Status. OutputValid

o_Status error status

Event code FunctionID

Event code EventID

i_Enable TRUE AND
i_pEventCode NULL

FALSE

ParameterError

-

-

i_Enable rises AND

i_pEventCode valid AND

i_ADCValue < G_ADC_MAXIMUM_VALUE

TRUE

-

NO_FUNC

NO_ERROR

i_Enable TRUE AND

i_pEventCode valid AND

i_ADCValue >= G_ADC_MAXIMUM_VALUE

FALSE

OverCurrent

AI_OC_PROTECTION

INPUT_TOO_HIGH

 

Example code

When enabling IO configuration on-the-fly, the firmware turns the safety switch off.

 

S_AIOverCurrentProtection FB is included for current inputs in Multitool Creator code template.

 

Safety Definitions:

 

Result: EPEC_SYSTEM.SYSTEM_ERROR_CODES:= EPEC_SYSTEM.SYSTEM_ERROR_CODES.FW_ERR_OK;

 

PIN_1_03_OC: EPEC_SHWD.S_AIOverCurrentProtection;

PIN_1_03_OC_Status: EPEC_SHWD.Status;

PIN_1_03_OC_EC: EPEC_DITF.EventCode;

 

 

 

Safety Init:

 

PIN_1_03_OC_EC.DeviceID := BYTE#1;

PIN_1_03_OC_EC.ChannelID := BYTE#3;

PIN_1_03_OC_EC.FunctionID := EPEC_DITF.FunctionIDs.NO_FUNC;

PIN_1_03_OC_EC.EventID := EPEC_DITF.ErrorIDs.NO_ERROR;

 

PIN_1_03_OC.Init(

    i_pEventCode := ADR(PIN_1_03_OC_EC)

);

 

 

Safety Code:

 

PIN_1_03_OC(

    i_Enable := TRUE,

    i_ADCValue := AI_RAW_MAIN_X1_03,   

    o_Status => PIN_1_03_OC_Status

);

 

(* Pin overcurrent -> set to voltage mode *)

IF PIN_1_03_OC_Status.OverCurrent THEN

    Result := EPEC_IODRV.IoDrvDOSetConfig(EPEC_HW.IO_Channels.PIN_1_03_DO_TYPE_V_mA,FALSE);

END_IF

 

 

 

 

See also:

 

 

 

 

 

 

 