Supported platforms: CODESYS 3.5, CODESYS 3.5 SAFETY, CODESYS 3.5 SP19 SAFETY

 

CalculateSRDOSignature (FUN)

Description

This function calculates safety configuration signature of one SRDO from given input parameters.

 

This function is intended to be used in device that configures safety unit. E.g. a display unit.

 

SRDO signature is calculated by MultiTool Creator when configuring the unit with it.

 

Unlike all other CRCs, safety configuration signature is specified to be calculated little-endian.

 

This function is endianness-aware.

Separate big-endian format conversions shall NOT be used.

 

Signature calculation is described in CANopen safety standard EN50325-5.

 

Operation

The function calculates CRC sequentially over SRDO communication and mapping parameters. As mentioned in safety parameter checksum calculation, each member of SRDO communication parameter STRUCT, and each mapping parameter has to be calculated individually. At start the i_Seed input parameter value for used Calculate16bitCRC is 0. Each following seed value is the result of preceding checksum calculation. All checksum calculations use i_Polynomial parameter value 1021h.

 

Order

Index

Sub-index

Name

Size

1

1301h SRDO Communication parameter

1

Information direction

1 byte

2

2

Safeguard Cycle Time / Refresh Time

2 bytes

3

3

SR Validation Time

1 byte

4

5

COB-ID 1

4 bytes

5

6

COB-ID 2

4 bytes

6

1381h SRDO mapping parameter

0

Number of SRDO mapping parameters

1 byte

7

1

Sub-index number

1 byte

8

1

SRDO 1 plain variable 1 mapping

4 bytes

9

2

Sub-index number

1 byte

10

2

SRDO 1 inverted variable 1 mapping

4 bytes

…

…

…

…

259

127

Sub-index number

1 byte

260

127

SRDO 1 plain variable 64 mapping

4 bytes

261

128

Sub-index number

1 byte

262

128

SRDO 1 inverted variable 64 mapping

4 bytes

 

Inputs

Input variable name

Data type

Unit

Range

Description

i_InfoDirection

BYTE

-

0 - 2

0 = not valid

1 = SRDO producer

2 = SRDO consumer

i_SCTime

UINT

ms

-

Safety Cycle Time / Refresh Time of SRDO

i_SRVTime

USINT

ms

-

Safety-Related Validation Time of SRDO

i_COBID1

DWORD

-

101h - 17Fh, odd values only

Plain SRDO message COB-ID

i_COBID2

DWORD

-

102h – 180h, even values only

Inverted SRDO message COB-ID

i_Mappings

USINT

-

> 0

Number of variable mappings of one SRDO message

i_pMapping

POINTER TO BYTE

-

≠ 0

Pointer to variable mapping table of one SRDO message

 

Outputs

Output variable name

Data type

Range

Description

o_OutputValid

BOOL

TRUE/FALSE

Calculated value is valid.

o_ParameterError

BOOL

TRUE/FALSE

Error in input parameters.

 

Return value

Data type

Description

WORD

Calculated SRDO signature.

 

Error diagnostic

Conditions

Return value

o_OutputValid

o_ParameterError

i_pMapping = 0 OR

i_Mappings = 0 OR

i_COBID1 out of range OR

i_COBID2 out of range

0

FALSE

TRUE

Parameters ok

Calculated result

TRUE

FALSE

 

Example code

Definitions at global variable list G_CAN1_TSRDO:

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

/// Plain SRDO variables

tdw1 AT %MD0: DWORD := DWORD#16#0;

tdw2 AT %MD1: DWORD := DWORD#16#0;

 

/// Inverted SRDO variables

tdw1_i AT %MD2: DWORD := DWORD#16#0;

tdw2_i AT %MD3: DWORD := DWORD#16#0;

 

/// Plain SRDO variable timestamps

tdw1_TIME: UDINT := UDINT#0;

tdw2_TIME: UDINT := UDINT#0;

 

/// Inverted SRDO variable timestamps

tdw1_i_TIME: UDINT := UDINT#0;

tdw2_i_TIME: UDINT := UDINT#0;

 

 

 

Definitions at global variable list G_CANopen_CAN1:

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

/// SRDO

SRDO: EPEC_CANopen.SRDOData; (* Protocol data *)

SRDOS: ARRAY[1..2] OF EPEC_CANopen.CANopenSRDO; (* SRDO instances *)

SRDO_Handler: EPEC_CANopen.CANopenSRDOHandler; (* Protocol handler *)

SRDO_Error: EPEC_CANopen.Errors := EPEC_CANopen.Errors.NotInitialized;

SRDO_Triggers: ARRAY[1..2] OF BOOL;

SRDO_Signatures: ARRAY[1..2] OF WORD;

SRDO_EventCodes: ARRAY[1..2] OF EPEC_DITF.EventCode;

 

 

Definitions at global variable list G_CANopen_CAN1_Mappings:

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

/// SRDO variable mappings

SRDO1Mappings: ARRAY [1..G_CANOPEN_NUMBER_OF_LAST_SRDO_MAP*2] OF DWORD := [

    DWORD#16#5FD60120, (* G_CAN1_TSRDO.tdw1 *)

    DWORD#16#5FD50120, (* G_CAN1_TSRDO.tdw1_i *)

    DWORD#16#5FD60220, (* G_CAN1_TSRDO.tdw2 *)

    DWORD#16#5FD50220, (* G_CAN1_TSRDO.tdw2_i *)

    12(DWORD#16#0)];   (* 16 - 4 = 12 *)

 

 

SRDO protocol initialization at non-safe Init_CANopen_CAN1 (PRG):

 

 

(*NOTE! This object is created by Epec MultiTool Creator*)

 

(*Define SRDO protocol*)

G_CANopen_CAN1.Protocols[6].Protocol:=EPEC_CANopen.ProtocolType.SRDO;

G_CANopen_CAN1.Protocols[6].pData:=ADR(G_CANopen_CAN1.SRDO);

G_CANopen_CAN1.Protocols[6].itfProtocol:=G_CANopen_CAN1.SRDO_Handler;

G_CANopen_CAN1.Protocols[6].pError:=ADR(G_CANopen_CAN1.SRDO_Error);

G_CANopen_CAN1.ProtocolAdded[6] := CANopenDeviceAddProtocol( (* Add to protocol stack *)

    i_pDevice:=ADR(G_CANopen_CAN1.Device),

    i_pProtocol:=ADR(G_CANopen_CAN1.Protocols[6])

);

IF G_CANopen_CAN1.ProtocolAdded[6] THEN

    G_CANopen_CAN1.SRDO_Handler.Init(

        i_pDevice := ADR(G_CANopen_CAN1.Device)

    );

ELSE

    G_CANopen_CAN1.SRDO_Error := EPEC_CANopen.Errors.ProtocolDataMissing;

END_IF

 

SRDO initialization at non-safe Init_CANopen_CAN1 (PRG):

 

(* Init SRDOs *)

G_CANopen_CAN1.SRDOS[1].i_pTimings[1]:= ADR(G_CAN1_TSRDO.tdw1_TIME); (*tdw1 *)

G_CANopen_CAN1.SRDOS[1].i_pTimings[2]:= ADR(G_CAN1_TSRDO.tdw1_i_TIME); (*tdw1_i *)

G_CANopen_CAN1.SRDOS[1].i_pTimings[3]:= ADR(G_CAN1_TSRDO.tdw2_TIME); (*tdw2 *)

G_CANopen_CAN1.SRDOS[1].i_pTimings[4]:= ADR(G_CAN1_TSRDO.tdw2_i_TIME); (*tdw2_i *)

G_CANopen_CAN1.SRDOS[1].Init(

    i_pDevice := ADR(G_CANopen_CAN1.Device),

    i_SRDONumber := 1,

    i_SRDOType := EPEC_CANopen.SRDOType.TransmitSRDO,

    i_SCTime := UINT#25, (* TSRDO Refresh Time (ms) *)

    i_SRVTime := USINT#0, (* Validation time (rx) (ms) *)

    i_COB_ID1 := DWORD#16#101, (* Plain message COB-ID *)

    i_COB_ID2 := DWORD#16#102, (* Inverted message COB-ID *)

    i_Mapping := G_CANopen_CAN1_Mappings.SRDO1Mappings, (* Plain + Inverted data mappings *)

    i_Mappings := 4, (* Plain + Inverted data mappings *)

    o_Error => G_CANopen_CAN1.SRDO_Error

);

 

 

Definitions:

 

srdoerror: BOOL;

srdovalid: BOOL;

 

SignatureValid: BOOL := FALSE;

SignatureError: BOOL := FALSE;

 

 

 

Code:

 

SignatureValid := TRUE;

 

FOR i := UINT#1 TO SIZEOF(G_CANopen_CAN1.SRDOS)/SIZEOF(G_CANopen_CAN1.SRDOS[1]) DO

 

    G_CANopen_CAN1.SRDO_Signatures[i] := EPEC_SDV.CalculateSRDOSignature (

        i_InfoDirection := G_CANopen_CAN1.SRDOS[i].i_SRDOType,

        i_SCTime := G_CANopen_CAN1.SRDOS[i].i_SCTime,

        i_SRVTime := G_CANopen_CAN1.SRDOS[i].i_SRVTime,

        i_COBID1 := G_CANopen_CAN1.SRDOS[i].i_COB_ID1,

        i_COBID2 := G_CANopen_CAN1.SRDOS[i].i_COB_ID2,

        i_Mappings := G_CANopen_CAN1.SRDOS[i].i_Mappings,

        i_pMappingParameter := ADR(G_CANopen_CAN1.SRDOS[i].i_Mapping),

        o_ParameterError => srdoerror,

        o_OutputValid => srdovalid

    );

 

    SignatureValid := SignatureValid AND srdovalid;

    SignatureError := SignatureError OR srdoerror;

 

END_FOR

 

 

See also

 

 

 

 

 

Source file topic100388.htm

Last updated 26-Aug-2026