Configuring Ethernet and DNS Settings

 

Units with a display:

  • Default IP address for Ethernet 1 is 192.168.0.2

  • Ethernet 2 is not configured by default

 

Units without a display:

  • Default IP address for Ethernet 1 is 192.168.0.2

  • Ethernet 2 is not configured by default

 

This section describes how to set the following settings:

 

Ethernet:

 

DNS (Domain Name System):

 

 

If the device contains a PLCopen application, the IP address can also be changed using CANmoon software (available in Epec Extranet).

 

 

 

For 6000/X series units with a displayFor 6000/X series units with a display

To configure the Ethernet settings:

  1. 6107 display unit: Boot-up the display unit and press the lower right corner of the display during boot-up until the embedded ApplicationLoader software starts.
    6112 and 6807 display unit: Boot-up the display unit and rub the lower right corner of the display during boot-up until the embedded ApplicationLoader software starts.

  2. Navigate to Communication Setup view:

  3. Select the wanted Ethernet mode:

    • Disabled

    • DHCP

    • Static IP

  4. If Static IP mode is selected, set the addresses:

    1. Tap the number field to be changed. Selected field is emphasized by a background color and a number keypad pop-up opens.

    2. Set the wanted numbers (max 3 numbers per field (0-255)) and tap

  5. To save the settings, tap Save.

 

Return to main view by tapping in the lower left corner.

 

 

 

To set the DNS addresses manually:

  1. 6107 display unit: Boot-up the display unit and press the lower right corner of the display during boot-up until the embedded ApplicationLoader software starts.
    6112 and 6807 display unit: Boot-up the display unit and rub the lower right corner of the display during boot-up until the embedded ApplicationLoader software starts.

  2. Navigate to Communication Setup view:

  3. Select DNS tab

  4. Select Manual DNS enabled

  5. To set the DNS address, tap the number field to be changed. Selected field is emphasized by a background color and a number keypad pop-up opens. Set the wanted numbers (max 3 numbers per field (0-255)) and tap

  6. To save the settings, tap Save.

 

Return to main view by tapping in the lower left corner.

 

 

 

 

For 6000/X series units without a displayFor 6000/X series units without a display

Configure the settings using a configuration file, see section Configuring Settings Using a File

 

 

 

 

 

 

 