Supported platforms: CODESYS 2.3

 

Updating Firmware (3000/4000 series)

Firmware version information

3000/4000 series units answer to 100Ah request is in the following format (it is possible to parse only the needed characters for application):

 

1.xxxxx.yyyyy.zzzzz.aaaaa.bbbbb.ccccc

xxxxx = firmware version, FW.bin

yyyyy = configuration file version, Conf.bin
zzzzz = mi (production version information, read-only)
aaaaa = boot version
bbbbb = Default application -> Always NODEF

ccccc = Main application -> Always NODEF

 

Updating the firmware through CODESYS

When updating firmware, check that you have files named FW.bin and Conf.bin. Different file names are not allowed. These files can be extracted from .srp packages found in Epec's Extranet.

 

 

3724 Extended Memory (EM) variants: After firmware is updated, the application needs to be re-downloaded to Control Unit. This is due to shared flash area for FW update binary and CODESYS application binary.

1. Download firmware

2. Reboot

3. Download application

 

  1. Login to the control unit: Online > Login

  2. Reset the control unit: Online > Reset

  3. Write FW.bin file to the control unit: Online > Write file to PLC

  4. Write Conf.bin file to the control unit: Online > Write file to PLC

 

Updating the firmware through CANopen

3724 Extended Memory (EM) variants: After firmware is updated, the application needs to be re-downloaded to Control Unit. This is due to shared flash area for FW update binary and CODESYS application binary.

1. Download firmware

2. Reboot

3. Download application

 

 

The firmware can be updated through CAN by, for example, another CANopen device.

 

Recommended method is to update using CODESYS 3.5 library SWDownload, function block SWD_LoadFirmware3000 (can be used with 3000 and 4000 series control units when firmware updating is done with 6000 series display). If SWDownload library is not used, then updating needs to be done with following steps.

 

Before updating firmware, check that FW & Conf binary files are valid.

SWDownload library does this automatically.

 

 

1. Login to the control unit by writing an SDO message

2. Stop the CODESYS application by writing an SDO message

3. Download the FW binary file using SDO messages.

 

 

Start byte

Size [Bytes]

Value

Description

RTS_FILE_WRITE_START

0

1

2Fh

Start file download command

Continue

1

1

0 Last block

1 Not last block

Indicates if this is the last block

NumOfDataBytesInBlock

2

2

Size of defined block

Number of data bytes in first block

FileNameLen

 

4

2

0008h (FW.bin)

000Ah (Conf.bin)

Length of file name (bytes) + 2

FileName

6

n

"FW.bin"

"Conf.bin"

Name of the file, zero-terminated string

Reserved

6 + n

2

0000h

3S reserved

Data

6 + n + 2

NumOfDataBytesInBlock

-

Content of file, first block

 

4. If the binary file is bigger than the block size (4986 bytes), repeat this step until all data is transferred

 

 

Start byte

Size [Bytes]

Value

Description

RTS_FILE_WRITE_CONT

0

1

30h

Continue file download command

Continue

1

1

0 Last block

1 Not last block

Indicates if this is the last block

NumOfDataBytesInBlock

2

2

Size of defined block  

Number of data bytes in block

Data

4

NumOfDataBytesInBlock

-

Content of file, subsequent block

 

5.  Check the file download status using SDO message

6.  Repeat steps 3-5 for Conf binary file.

 

 

 

 