Supported platforms: CODESYS 2.3, CODESYS 3.5, CODESYS 3.5 SAFETY
Epec units have a software called Default application. The default application provides certain CANopen indexes for Epec devices that can be used to configure the control unit. The provided indexes may differ depending on the hardware product (see the table below).
|
202x, 203x and E/S series units do not have default application, but firmware responses to indexes listed in the table. |
|
6000/X series and 2040 do not have a default application. |
Index |
Sub-index |
Type |
Description |
Additional information |
3000s |
4602 |
5050 CODESYS 2.3 |
5050 CODESYS 3.5 |
E Series |
S Series |
202x, 203x |
1000h |
|
U32 |
Device type |
Describes the type of device and its functionality. |
x |
x |
x |
x |
x |
x |
x |
1008h |
|
STRING |
Manufacturer Device Name |
Control unit name, e.g. SC52 |
|
|
in runtime |
|
x |
x |
|
1009h |
|
STRING |
Manufacturer Hardware Version |
|
|
|
|
|
|
|
|
100Ah |
|
STRING |
Manufacturer Software Version |
|
x |
x |
x |
x |
x |
x |
x |
1010h |
|
ARRAY |
Store parameters |
|
x |
x |
x |
x |
x |
x |
x |
|
0h |
U8 |
Number of entries |
|
x |
x |
x |
x |
x |
x |
x |
|
1h |
U32 |
Save all parameters |
Store parameters to non-volatile memory. Write = 65766173h, where (s = 73h, a = 61h, v = 76h, e = 65h) |
x |
x |
x |
x |
x |
x |
x |
1011h |
|
ARRAY |
Restore Parameters |
|
x |
x |
x |
x |
x |
x |
x |
|
0h |
U8 |
Number of entries |
|
x |
x |
x |
x |
x |
x |
x |
|
1h |
U32 |
Restore all default parameters |
Restore default parameter values. Write = 64616F6Ch, where (l = 6Ch, o = 6Fh, a = 61h, d = 64h) |
x |
x |
x |
x |
x |
x |
x |
1017h |
|
U16 |
Heartbeat producer time |
[ms] |
|
|
x |
x |
|
|
|
1018h |
|
RECORD |
Identity Object |
Identifies the control unit |
x |
x |
x |
x |
x |
x |
x |
|
0h |
U8 |
Number of entries |
|
x |
x |
x |
x |
x |
x |
x |
|
1h |
U32 |
Vendor-ID |
Identifies the manufacturer of a device |
x |
x |
x |
x |
x |
x |
x |
|
2h |
U32 |
Product Code |
Product code, for example - 7E8 = 2024 - E16 = 3606 - 22D4 = 8916 |
x |
x |
x |
x |
x |
x |
x |
|
3h |
U32 |
Revision Number |
|
x |
x |
x |
x |
x |
x |
x |
|
4h |
U32 |
Serial Number |
|
x |
x |
x |
x |
x |
x |
x |
2003h |
|
ARRAY |
Communication parameters for 202x and 203x units |
2020, 2023, 2024, 2038, 2040 |
|
|
|
|
|
|
x |
|
0x0h |
U8 |
Number of entries |
|
|
|
|
|
|
|
x |
|
0x1h |
U32 |
Node-ID for CAN1 |
|
|
|
|
|
|
|
x |
|
0x4h |
U32 |
Bit rate for CAN1 |
Bit rate in kbit/s |
|
|
|
|
|
|
x |
|
0xDh |
U32 |
Node-ID for CAN2 |
|
|
|
|
|
|
|
x |
|
0xEh |
U32 |
Bit rate for CAN2 |
Bit rate in kbit/s |
|
|
|
|
|
|
x |
2030h |
1h |
U32 |
Supported CODESYS platform |
Supported CODESYS version in format AABBCCFFh for example 03050000h --> CODESYS 3.5.0.0 |
|
|
|
x |
x |
x |
|
2031h |
|
ARRAY |
Password |
|
|
|
|
|
x |
x |
|
|
1h |
STRING |
Software download and parameter handling password enter |
|
|
|
|
|
x |
x |
|
|
2h |
STRING |
Software download and parameter handling password change |
|
|
|
|
|
x |
x |
|
|
3h |
STRING |
Software download and parameter handling password reset |
|
|
|
|
|
x |
x |
|
2032h |
1h |
U8 |
Software download and parameter handling status (2031h) |
|
|
|
|
|
x |
x |
|
2036h |
0h |
DOMAIN / RO |
Version information |
Data structure which describes version information for unit. Data is offered as one binary data. Byte aligment is always in platform native format.
Data structure is depicted in product specific Int libraries. For example, SC52: Libraries > S Series Specific Libraries > SafeSC52int > Data Types |
|
|
|
|
x |
x |
|
2037h |
0h |
DOMAIN / RO |
Production data |
Data structure which describes production data for unit. Data is offered as one binary data. Byte aligment is always in platform native format.
Data structure is depicted in product specific Int libraries. For example, SC52: Libraries > S Series Specific Libraries > SafeSC52int > Data Types |
|
|
|
|
x |
x |
|
2072h |
1h |
Binary |
Firmware status |
||||||||
2130h |
|
ARRAY |
Application version information |
|
x |
x |
x |
x |
|
|
|
|
1h |
STRING |
Application version |
Application software version |
x |
x |
x |
x |
|
|
|
2140h |
|
ARRAY |
MAC Address |
MAC address of the control unit |
|
|
x |
x |
|
|
|
|
0h |
U8 |
Number of entries |
|
|
|
x |
x |
|
|
|
|
1h |
U8 |
MAC address byte 1 |
|
|
|
x |
x |
|
|
|
|
2h |
U8 |
MAC address byte 2 |
|
|
|
x |
x |
|
|
|
|
3h |
U8 |
MAC address byte 3 |
|
|
|
x |
x |
|
|
|
|
4h |
U8 |
MAC address byte 4 |
|
|
|
x |
x |
|
|
|
|
5h |
U8 |
MAC address byte 5 |
|
|
|
x |
x |
|
|
|
|
6h |
U8 |
MAC address byte 6 |
|
|
|
x |
x |
|
|
|
2141h |
|
ARRAY |
Ethernet Configuration |
The new configurations are taken to use after the control unit is rebooted. |
|
|
x |
x |
|
|
|
|
0h |
U8 |
Number of entries |
|
|
|
x |
x |
|
|
|
|
1h |
U8 |
Ethernet enabled/disabled |
|
|
|
x |
x |
|
|
|
|
2h |
U8 |
DHCP on/off |
To disable/enable the DHCP, write 0/1 to index 2141h sub-index 1h. Disabling DHCP requires that the IP address, net mask and gateway are manually defined. To save the new settings, write save command to index 1010h. |
|
|
x |
x |
|
|
|
|
12h |
U8 |
Netstatus |
Valid values |
|
|
x |
x |
|
|
|
|
13h |
U8 |
IP address highest byte |
When DHCP is ON - write access is prohibited. - reading this index updates the IP address and net mask |
|
|
x |
x |
|
|
|
|
14h |
U8 |
IP address 3rd byte |
When DHCP is ON, write access is prohibited. |
|
|
x |
x |
|
|
|
|
15h |
U8 |
IP address 2nd byte |
When DHCP is ON, write access is prohibited. |
|
|
x |
x |
|
|
|
|
16h |
U8 |
IP address lowest byte |
When DHCP is ON, write access is prohibited. |
|
|
x |
x |
|
|
|
|
17h |
U8 |
Gateway highest byte |
|
|
|
x |
x |
|
|
|
|
18h |
U8 |
Gateway 3rd byte |
|
|
|
x |
x |
|
|
|
|
19h |
U8 |
Gateway 2nd byte |
|
|
|
x |
x |
|
|
|
|
1Ah |
U8 |
Gateway lowest byte |
|
|
|
x |
x |
|
|
|
|
1Bh |
U8 |
Netmask highest byte |
|
|
|
x |
x |
|
|
|
|
1Ch |
U8 |
Netmask 3rd byte |
|
|
|
x |
x |
|
|
|
|
1Dh |
U8 |
Netmask 2nd byte |
|
|
|
x |
x |
|
|
|
|
1Eh |
U8 |
Netmask first byte |
|
|
|
x |
x |
|
|
|
2150h |
|
ARRAY |
CAN1 Configuration |
|
x |
x |
x |
x |
x |
x |
|
|
0h |
U8 |
Number of entries |
|
x |
x |
x |
x |
x |
x |
|
|
1h |
U16 |
CODESYS communication enabled |
This does not have any effect since CODESYS communication is enabled always for CAN1 |
x |
x |
x |
x |
x |
x |
|
|
2h |
U16 |
CODESYS communication node-ID |
|
x |
x |
x |
x |
x |
x |
|
|
3h |
U16 |
Bit rate |
Bit rate in kbit/s |
x |
x |
x |
x |
x |
x |
|
|
4h |
U16 |
Cable detection offset for CODESYS node-ID |
|
x |
x |
x |
x |
|
|
|
|
5h |
U16 |
Cable detection offset for PLCopen node-ID |
For information about cable detection calculation, see hardware specific sections for cable detection (for example Programming 3606 > 3606 Cable Detection). |
x |
x |
x |
x |
|
|
|
|
6h |
U16 |
Mask for cable detection pins |
Mask is used to define pins which are used to configure node-ID for CODESYS and PLCopen application based on the pin state for cable detection.
|
x |
x |
x |
x |
|
|
|
|
Ah |
U16 |
PLCopen application node-ID in CAN1 |
|
x |
x |
x |
x |
x |
x |
|
2151h |
|
ARRAY |
CAN2 Configuration |
|
x* |
x |
x |
x |
|
|
|
|
0h |
U8 |
Number of entries |
|
x* |
x |
x |
x |
|
|
|
|
1h |
U16 |
CODESYS communication enabled |
This setting is valid only for CAN1 |
x* |
x |
x |
x |
|
|
|
|
2h |
U16 |
CODESYS communication node-ID |
This setting is valid only for CAN1 |
x* |
x |
x |
x |
|
|
|
|
3h |
U16 |
Bit rate |
Bit rate in kbit/s |
x* |
x |
x |
x |
|
|
|
|
4-9h |
U16 |
Reserved for future use |
|
x* |
x |
x |
x |
|
|
|
|
Ah |
U16 |
PLCopen application node-ID in CAN2 |
|
x* |
x |
x |
x |
|
|
|
2152h |
|
ARRAY |
CAN3 Configuration |
|
|
|
x |
x |
|
|
|
|
0h |
U8 |
Number of entries |
|
|
|
x |
x |
|
|
|
|
1h |
U16 |
CODESYS communication enabled |
This setting is valid only for CAN1 |
|
|
x |
x |
|
|
|
|
2h |
U16 |
CODESYS communication node-ID |
This setting is valid only for CAN1 |
|
|
x |
x |
|
|
|
|
3h |
U16 |
Bit rate |
Bit rate in kbit/s |
|
|
x |
x |
|
|
|
|
4-9h |
U16 |
Reserved for future use |
|
|
|
x |
x |
|
|
|
|
Ah |
U16 |
PLCopen application node-ID in CAN3 |
|
|
|
x |
x |
|
|
|
2153h |
|
ARRAY |
CAN4 Configuration |
|
|
|
x |
x |
|
|
|
|
0h |
U8 |
Number of entries |
|
|
|
x |
x |
|
|
|
|
1h |
U16 |
CODESYS communication enabled |
This setting is valid only for CAN1 |
|
|
x |
x |
|
|
|
|
2h |
U16 |
CODESYS communication node-ID |
This setting is valid only for CAN1 |
|
|
x |
x |
|
|
|
|
3h |
U16 |
Bit rate |
Bit rate in kbit/s |
|
|
x |
x |
|
|
|
|
4-9h |
U16 |
Reserved for future use |
|
|
|
x |
x |
|
|
|
|
Ah |
U16 |
PLCopen application node-ID in CAN4 |
|
|
|
x |
x |
|
|
|
x* depends on the hardware version
Source file topic000800.htm