This function block monitors voltages, temperatures and the program cycle time of the control unit. All the voltages and temperatures have high and low limits, both signaled with a boolean output when exceeded. Each measurement limit has it's own parameter. Only the high limit of the program cycle time can be set and monitored.
  | 
		The low and high limit parameters for supply voltage must be set within the specified voltage range of the control unit. 
  | 
	
Input variable name  | 
		Data type  | 
		Range  | 
		Description  | 
	
i_SupplyVoltage  | 
		UINT  | 
		0..1023  | 
		Supply voltage measured value.  | 
	
i_Internal2_5V  | 
		UINT  | 
		0..1023  | 
		Internal 2,5V measured value.  | 
	
i_Internal3_6V  | 
		UINT  | 
		0..1023  | 
		Internal 3,6V measured value.  | 
	
i_Internal7_3V  | 
		UINT  | 
		0..1023  | 
		Internal 7,3V measured value.  | 
	
i_Ref5V  | 
		UINT  | 
		0..1023  | 
		Reference 5V measured value.  | 
	
i_Temperature  | 
		UINT  | 
		0..1023  | 
		Temperature measured value.  | 
	
i_SupplyVoltageHighLimit  | 
		UINT  | 
		
  | 
		High limit of supply voltage. 100 = 1,00 volts.  | 
	
i_SupplyVoltageLowLimit  | 
		UINT  | 
		
  | 
		Low limit of supply voltage. 100 = 1,00 volts.  | 
	
i_Internal2_5VHighLimit  | 
		UINT  | 
		
  | 
		High limit of internal 2,5V voltage. 100 = 1,00 volts.  | 
	
i_Internal2_5VLowLimit  | 
		UINT  | 
		
  | 
		Low limit of internal 2,5V voltage. 100 = 1,00 volts.  | 
	
i_Internal3_6VHighLimit  | 
		UINT  | 
		
  | 
		High limit of internal 3,6V voltage. 100 = 1,00 volts.  | 
	
i_Internal3_6VLowLimit  | 
		UINT  | 
		
  | 
		Low limit of internal 3,6V voltage. 100 = 1,00 volts.  | 
	
i_Internal7_3VHighLimit  | 
		UINT  | 
		
  | 
		High limit of internal 7,3V voltage. 100 = 1,00 volts  | 
	
i_Internal7_3VLowLimit  | 
		UINT  | 
		
  | 
		Low limit of internal 7,3V voltage. 100 = 1,00 volts.  | 
	
i_Ref5VHighLimit  | 
		UINT  | 
		
  | 
		High limit of 5V reference voltage. 100 = 1,00 volts.  | 
	
i_Ref5VLowLimit  | 
		UINT  | 
		
  | 
		Low limit of 5V reference voltage. 100 = 1,00 volts.  | 
	
i_TempHighLimit  | 
		INT  | 
		
  | 
		High limit of temperature 1. 10 = 1 °C.  | 
	
i_TempLowLimit  | 
		INT  | 
		
  | 
		Low limit of temperature 1. 10 = 1 °C.  | 
	
i_CycleTimeHighLimit  | 
		UINT  | 
		
  | 
		High limit of application cycle time in milliseconds.  | 
	
Output variable name  | 
		Data type  | 
		Range  | 
		Description  | 
	
o_SupplyVoltage  | 
		UINT  | 
		0..45,99V  | 
		Scaled value of module supply voltage. 100 = 1,00 volts..  | 
	
o_Internal2_5V  | 
		UINT  | 
		0..5,00V  | 
		Scaled value of internal 2,5V voltage. 100 = 1,00 volts.  | 
	
o_Internal3_6V  | 
		UINT  | 
		0..5,00V  | 
		Scaled value of internal 3,6V voltage. 100 = 1,00 volts.  | 
	
o_Internal7_3V  | 
		UINT  | 
		0..10,00V  | 
		Scaled value of internal 7,3V voltage. 100 = 1,00 volts.  | 
	
o_Ref5V  | 
		UINT  | 
		0..5,00V  | 
		Scaled value of 5V reference voltage. 100 = 1,00 volts.  | 
	
o_Temperature  | 
		INT  | 
		
  | 
		Calculated value of temperature 1. 10 = 1 °C  | 
	
o_CycleTime  | 
		UINT  | 
		
  | 
		Latest application cycle time in milliseconds  | 
	
o_CycleTimeAverage  | 
		UINT  | 
		
  | 
		Average application cycle time in milliseconds.  | 
	
o_SupplyVoltageHigh  | 
		BOOL  | 
		
  | 
		TRUE if supply voltage is higher than limit  | 
	
o_SupplyVoltageLow  | 
		BOOL  | 
		
  | 
		TRUE if supply voltage is lower than limit  | 
	
o_Internal2_5VHigh  | 
		BOOL  | 
		
  | 
		TRUE if internal 2,5V voltage is higher than limit  | 
	
o_Internal2_5VLow  | 
		BOOL  | 
		
  | 
		TRUE if internal 2,5V voltage is lower than limit  | 
	
o_Internal3_6VHigh  | 
		BOOL  | 
		
  | 
		TRUE if internal 3,6V voltage is higher than limit  | 
	
o_Internal3_6VLow  | 
		BOOL  | 
		
  | 
		TRUE if internal 3,6V voltage is lower than limit  | 
	
o_Internal7_3VHigh  | 
		BOOL  | 
		
  | 
		TRUE if internal 7,3V voltage is higher than limit  | 
	
o_Internal7_3VLow  | 
		BOOL  | 
		
  | 
		TRUE if internal 7,3V voltage is lower than limit  | 
	
o_Ref5VHigh  | 
		BOOL  | 
		
  | 
		TRUE if 5V reference voltage is higher than limit  | 
	
o_Ref5VLow  | 
		BOOL  | 
		
  | 
		TRUE if 5V reference voltage is lower than limit  | 
	
o_TemperatureHigh  | 
		BOOL  | 
		
  | 
		TRUE if temperature 1 is higher than limit  | 
	
o_TemperatureLow  | 
		BOOL  | 
		
  | 
		TRUE if temperature 1 is lower than limit  | 
	
o_CycleTimeHigh  | 
		BOOL  | 
		
  | 
		TRUE if application cycle time is higher than limit  | 
	

-