This function block monitors voltages of CAN1, CAN2 and RS485.
All the voltages have high and low limits, which are both signaled with a boolean output.
Each measurement limit has it's own input parameter.
The low and high limit parameters for supply voltage must be set within the specified voltage range of the control unit. |
This function block is for 2021 unit. |
Input variable name |
Data type |
Range |
Description |
i_RS485HVoltage |
UINT |
|
RS485 H voltage measured value. |
i_RS485LVoltage |
UINT |
|
RS485 L voltage measured value. |
i_CAN1HVoltage |
UINT |
|
CAN 1 H voltage measured value. |
i_CAN1LVoltage |
UINT |
|
CAN 1 L voltage measured value. |
i_CAN2HVoltage |
UINT |
|
CAN 2 H voltage measured value. |
i_CAN2LVoltage |
UINT |
|
CAN 2 L voltage measured value. |
i_RS485HVoltageHighLimit |
UINT |
|
High limit of RS485 High voltage. 100 = 1.00 volts. |
i_RS485HVoltageLowLimit |
UINT |
|
Low limit of RS485 High voltage. 100 = 1.00 volts. |
i_RS485LVoltageHighLimit |
UINT |
|
High limit of RS485 Low voltage. 100 = 1.00 volts. |
i_RS485LVoltageLowLimit |
UINT |
|
Low limit of RS485 Low voltage. 100 = 1.00 volts. |
i_CAN1HVoltageHighLimit |
UINT |
|
High limit of CAN 1 High voltage. 100 = 1.00 volts. |
i_CAN1HVoltageLowLimit |
UINT |
|
Low limit of CAN 1 High voltage. 100 = 1.00 volts. |
i_CAN1LVoltageHighLimit |
UINT |
|
High limit of CAN 1 Low voltage. 100 = 1.00 volts. |
i_CAN1LVoltageLowLimit |
UINT |
|
Low limit of CAN 1 Low voltage. 100 = 1.00 volts. |
i_CAN2HVoltageHighLimit |
UINT |
|
High limit of CAN 2 High voltage. 100 = 1.00 volts. |
i_CAN2HVoltageLowLimit |
UINT |
|
Low limit of CAN 2 High voltage. 100 = 1.00 volts. |
i_CAN2LVoltageHighLimit |
UINT |
|
High limit of CAN 2 Low voltage. 100 = 1.00 volts. |
i_CAN2LVoltageLowLimit |
UINT |
|
Low limit of CAN 2 Low voltage. 100 = 1.00 volts. |
Output variable name |
Data type |
Range |
Description |
o_RS485HVoltage |
UINT |
|
Scaled value of module RS485 High voltage. 100 = 1.00 volts. |
o_RS485LVoltage |
UINT |
|
Scaled value of module RS485 Low voltage. 100 = 1.00 volts. |
o_CAN1HVoltage |
UINT |
|
Scaled value of module CAN 1 High voltage. 100 = 1.00 volts. |
o_CAN1LVoltage |
UINT |
|
Scaled value of module CAN 1 Low voltage. 100 = 1.00 volts. |
o_CAN2HVoltage |
UINT |
|
Scaled value of module CAN 2 High voltage. 100 = 1.00 volts. |
o_CAN2LVoltage |
UINT |
|
Scaled value of module CAN 2 Low voltage. 100 = 1.00 volts. |
o_RS485HVoltageHigh |
BOOL |
|
TRUE if RS485 H voltage is higher than limit. |
o_RS485HVoltageLow |
BOOL |
|
TRUE if RS485 H voltage is lower than limit. |
o_RS485LVoltageHigh |
BOOL |
|
TRUE if RS485 L voltage is higher than limit. |
o_RS485LVoltageLow |
BOOL |
|
TRUE if RS485 L voltage is lower than limit. |
o_CAN1HVoltageHigh |
BOOL |
|
TRUE if CAN 1 H voltage is higher than limit. |
o_CAN1HVoltageLow |
BOOL |
|
TRUE if CAN 1 H voltage is lower than limit. |
o_CAN1LVoltageHigh |
BOOL |
|
TRUE if CAN 1 L voltage is higher than limit. |
o_CAN1LVoltageLow |
BOOL |
|
TRUE if CAN 1 L voltage is lower than limit. |
o_CAN2HVoltageHigh |
BOOL |
|
TRUE if CAN 2 H voltage is higher than limit. |
o_CAN2HVoltageLow |
BOOL |
|
TRUE if CAN 2 H voltage is lower than limit. |
o_CAN2LVoltageHigh |
BOOL |
|
TRUE if CAN 2 L voltage is higher than limit. |
o_CAN2LVoltageLow |
BOOL |
|
TRUE if CAN 2 L voltage is lower than limit. |