Supported platforms: CODESYS 2.3, CODESYS 3.5, CODESYS 3.5 SP19 SAFETY
|
Name of the Member |
Data Type |
Range |
Description |
|
CANVXD_CobId |
DWORD |
|
COBID which is used to define callback in CANVXD |
|
PGN_Number |
WORD |
0..65535 |
Parameter group number |
|
Priority |
BYTE |
0..7 |
Priority of the PGN |
|
SourceAddress |
BYTE |
0..255 |
Source address of the PGN |
|
DataPage |
BYTE |
0..3 |
2 datapage bits: DP & EDP. Value 0=none, 1=DP, 2=EDP, 3=Both |
|
Destination |
BYTE |
0..255 |
Destination address of the PGN |
|
CycleTime |
WORD |
5..65535 |
PGN send interval or expected PGN receive interval |
|
DataLength |
DWORD |
1..117 440 505 |
Number of bytes in this PGN |
|
PGNDataLength |
DWORD |
1..117 440 505 |
Space (number of bytes) reserved for PGN data. This value is initialized once in the beginning and not changed after that. Destination specific transport protocol uses this value to check if it can receive whole message packet or not. |
|
NumberOfSPNs |
WORD |
1..65535 |
Number of SPNs in this PGN |
|
pSPNs |
POINTER TO J1939_SPN |
|
Pointer to the beginning of the list of SPNs in this PGN |
|
NewData |
BOOL |
TRUE / FALSE |
New data received (=TRUE), active one program cycle |
|
SendTrigger |
BOOL |
TRUE / FALSE |
Trigger to send PGN immediately |
|
SendTriggerOld |
BOOL |
TRUE / FALSE |
Previous value of SendTrigger to detect rising edge |
|
SendTriggerImmediately |
BOOL |
TRUE/FALSE |
Trigger to send PGN immediately. Flag is reseted in same cycle when it is set TRUE. Note! Set this flag to TRUE only once when PGN is wanted to send. |
|
TimeStamp |
DWORD |
0..4294967295 |
Time stamp when this message was last sent or received |
|
OldTimeStamp |
DWORD |
0..4294967295 |
Reference time stamp |
|
Status |
INT |
-32768..32767 |
Error if negative, see J1939_PGNStatus |
|
DataValid |
BOOL |
TRUE / FALSE |
Data validity flag, if FALSE, data is old (not received in CycleTime) |
|
AddTransmitListTime |
DWORD |
0..4294967295 |
Used with long data transmission (BAM). Time when PGN status changed to "wait for transmission". |
|
UseChecksum |
BOOL |
TRUE/FALSE |
If set to TRUE, a checksum is added to byte 8 of the message |
|
UseMessageCounter |
BOOL |
TRUE/FALSE |
If set to TRUE, a message counter is added to byte 8 of the message. |
|
FillBitTrue |
BOOL |
TRUE/FALSE |
If set to TRUE, unused bits are filled with 1 otherwise with 0 |
|
MessageCounter |
BYTE |
0-7, 15 |
Message counter value, rolls from 7 to 0, 15 means not available |
|
TransferErrors |
J1939_TransferErrors |
J1939_TransferErrors |
Possible transfer errors for multipacket sending |
|
TransferSendBytes |
DWORD |
|
Send bytes for multipacket transfer |
|
TransferIntervalForMessages |
DWORD |
Time |
G_J1939_CYCLE_TIME_FOR_DT_MSG |
|
TransferTimeout |
DWORD |
Time |
Timeout for transport protocol and extended transport protocol |
|
pRawData |
DWORD |
Pointer |
Direct pointer to send data, used when extended transport protocol is used. Null pointer is considered as error for extended transport protocol. Extended transport protocol is used when size of the sent data > G_J1939_MAX_SIZE_OF_LONG_TRANSFER |
|
CheckSpnSize |
BOOL |
TRUE/FALSE |
If set TRUE J1939 checks SPN size. |
|
CallBackPOUForPgn |
WORD |
|
Callback POU which is called when PGN is received |
|
CallBackDataPointer |
DWORD |
Pointer |
Callback data pointer |
|
UseFastPacketProtocol |
BOOL |
TRUE/FALSE |
If set to TRUE, NMEA 2000 Fast Packet protocol is used for this PGN. |
|
FastPacketSequenceNumber |
BYTE |
|
Fast packet sequence number. |
|
Name of the Member |
Data Type |
Range |
Description |
|
CANVXD_CobId |
DWORD |
|
COBID which is used to define callback in CANVXD. |
|
PGN_Number |
WORD |
0..65535 |
Parameter group number. |
|
Priority |
BYTE |
0..7 |
Priority of the PGN. |
|
SourceAddress |
BYTE |
0..255 |
Source address of the PGN. |
|
DataPage |
BYTE |
0..3 |
Data page. |
|
Destination |
BYTE |
0..255 |
Destination address of the PGN. |
|
CycleTime |
WORD |
0..65535 |
PGN send interval or expected PGN receive interval. |
|
DataLength |
DWORD |
0…117 440 505 |
Number of bytes in this PGN. |
|
PGNDataLength |
DWORD |
0…117 440 505 |
Space (number of bytes) reserved for PGN data. This value is initialized once in the beginning and not changed after that. Destination specific transport protocol uses this value to check if it can receive whole message packet or not. |
|
NumberOfSPNs |
WORD |
|
Number of SPNs in this PGN. |
|
pSPNs |
POINTER TO J1939_SPN |
|
Pointer to the beginning of the list of SPNs in this PGN. |
|
NewData |
BOOL |
TRUE / FALSE |
New data received (=TRUE), active one program cycle. |
|
SendTrigger |
BOOL |
TRUE / FALSE |
Trigger to send PGN immediately. |
|
SendTriggerOld |
BOOL |
TRUE / FALSE |
Previous value of SendTrigger to detect rising edge. |
|
SendTriggerImmediately |
BOOL |
TRUE / FALSE |
Trigger to send PGN immediately. The flag is reset automatically after sending. |
|
TimeStamp |
DWORD |
|
Time stamp when this message was last sent or received. |
|
OldTimeStamp |
DWORD |
|
Reference time stamp. |
|
Status |
INT |
|
Error if negative, see J1939_PGNStatus. |
|
DataValid |
BOOL |
TRUE / FALSE |
Data validity flag, if FALSE, data is old (not received in CycleTime). |
|
AddTransmitListTime |
DWORD |
|
Used with long data transmission (BAM). Time when PGN status changed to "wait for transmission". |
|
UseChecksum |
BOOL |
TRUE / FALSE |
If set to TRUE, a checksum is added to byte 8 of the message. |
|
UseMessageCounter |
BOOL |
TRUE / FALSE |
If set to TRUE, a counter is added to byte 8 of the message. The counter is incremented each time the message is sent. Note! Counter and Checksum can be used simultaneously, both using 4 bits of the byte. |
|
FillBitTrue |
BOOL |
TRUE / FALSE |
If TRUE, unused bits are filled with 1 otherwise with 0. |
|
MessageCounter |
BYTE |
|
Message counter. See 'UseMessageCounter'. |
|
TransferErrors |
J1939_TransferErrors |
|
Possible transfer errors for multipacket sending. |
|
TransferSendBytes |
DWORD |
|
Send bytes for multipacket transfer. |
|
TransferIntervalForMessages |
DWORD |
|
DT message inhibit time. |
|
TransferTimeout |
DWORD |
|
Timeout for transport protocol and extended transport protocol. |
|
pRawData |
DWORD |
|
Direct pointer to send data, used when extended transport protocol is used. Null pointer is considered as error for extended transport protocol. Extended transport protocol is used when size of the sent data > 1785 bytes. |
|
CheckSpnSize |
BOOL |
TRUE / FALSE |
If set TRUE J1939 checks SPN size. |
|
itfCallback |
|
Interface to callback POU. |
|
|
pCallbackData |
DWORD |
|
Callback data pointer. |
|
UseFastPacketProtocol |
BOOL |
TRUE / FALSE |
If set to TRUE, NMEA 2000 Fast Packet protocol is used for this PGN. |
|
FastPacketSequenceNumber |
BYTE |
Fast packet sequence number. |
|
| SafetyRelevant | BOOL | TRUE / FALSE | The PGN is safety relevant. The non-safe library does not trigger sending or reset NewData status. |
| SafetyTrigger | BOOL | TRUE / FALSE | Send trigger for safety relevant PGNs. Triggering is handled by the safety library POU. |
| MsgBuffer | POINTER TO MSGBuffer | Safety relevant CAN message buffer. |
|
Name of the Member |
Description |
Value |
|
J1939_PGN_SPNUninitialized |
SPN data pointer and size are null. (PGN Extract incomplete.) |
-7 |
|
J1939_PGN_pSPNDataNULL |
SPN data pointer in the SPN is NULL |
-6 |
|
J1939_PGN_pSPNNULL |
SPN pointer in the PGN is NULL |
-5 |
|
J1939_PGN_MultiPacketBufSize |
Multi packet buffer size too small |
-4 |
|
J1949_PGN_BAM_Failure |
Broadcast announcement message arrived, before previous was completed. |
-3 |
|
J1939_PGN_WrongSeqNbr |
Wrong sequence number |
-2 |
|
J1939_PGN_Timeout |
PGN timed out. |
-1 |
|
J1939_PGN_Idle |
Idle, status after start. |
0 |
|
J1939_PGN_Receiving |
Receiving multi packet message. |
1 |
|
J1939_PGN_DataReady |
Data received and extracted. |
2 |
|
J1939_PGN_WaitTransmission |
Waiting transmission. Used with long transfer |
3 |
|
J1939_PGN_Transmitting |
Transmitting multi packet message |
4 |
|
J1939_PGN_Transmitting_ETP |
Transmitting extended transport protocol message |
5 |
|
Name of the Member |
Data Type |
Default value |
Description |
|
pPGN |
POINTER TO J1939_PGN |
- |
Pointer to PGN |
|
Name of the Member |
Description |
Value |
|
J1939_ERR_None |
Status OK |
0000 h |
|
J1939_ERR_pRxPGNNULL |
i_pRxPGNs pointer null, when number of Rx PGNs > 0 |
8000 h |
|
J1939_ERR_pTxPGNNULL |
i_pTxPGNs pointer null, when number of Tx PGNs > 0 |
8001 h |
|
J1939_ERR_pPGNListNULL |
i_pPGNList pointer null, when long transfer is needed ( PGN DataLength > 8) |
8002 h |
|
J1939_ERR_RxRegInit |
CobID registering failure. |
8003 h |
|
J1939_ERR_TxSendFail |
Sending of Tx PGN failed. |
8004 h |
|
J1939_ERR_pSPNNULL |
SPN pointer not initialized. |
8005 h |
|
J1939_ERR_MultipacketInit |
Multi packet pointer null. |
8006 h |
|
J1939_ERR_PGNDataLength |
PGN DataLength is over G_J1939_MAX_SIZE_OF_LONG_TRANSFER or size reserved for PGN is smaller than received data size |
8007 h |
|
J1939_ERR_pRxPGNNULL |
pRxPGN pointer null in pointer array |
8008 h |
|
J1939_ERR_pTxPGNNULL |
pTxPGN pointer null in pointer array |
8009 h |
|
J1939_ERR_pSPNDataNULL |
SPN data pointer null. |
800A h |
|
J1939_ERR_SPNUninitialized |
SPN is uninitialized. (size and data pointer are null) |
800B h |
|
J1939_ERR_InvalidCANbusNbr |
CAN bus number out of range. |
800C h |
|
J1939_ERR_InvalidControlByte |
Invalid transport protocol connection management control byte |
800D h |
|
J1939_ERR_MultipacketTimeout |
Timeout in transport protocol. |
800E h |
|
J1939_ERR_NullPointer |
Generic null pointer error. |
800F h |
|
J1939_ERR_RX_ListFull |
Can not add PGN, maximum number of rx PGNs reached. |
8010 h |
|
J1939_ERR_TX_ListFull |
Can not add PGN, maximum number of tx PGNs reached. |
8011 h |
|
J1939_ERR_RQST_ListFull |
Reserved size for request callbacks in G_J1939_MAX_NBR_OF_RQST_CALLBACKS is too low. |
8012 h |
|
Name of the Member |
Description |
Value |
|
J1939_ERR_None |
Status OK |
0000 h |
|
J1939_ERR_pRxPGNNULL |
i_pRxPGNs pointer null, when number of Rx PGNs > 0 |
8000 h |
|
J1939_ERR_pTxPGNNULL |
i_pTxPGNs pointer null, when number of Tx PGNs > 0 |
8001 h |
|
J1939_ERR_pPGNListNULL |
i_pPGNList pointer null, when long transfer is needed ( PGN DataLength > 8) |
8002 h |
|
J1939_ERR_RxRegInit |
CobID registering failure. |
8003 h |
|
J1939_ERR_TxSendFail |
Sending of Tx PGN failed. |
8004 h |
|
J1939_ERR_pSPNNULL |
SPN pointer not initialized. |
8005 h |
|
J1939_ERR_MultipacketInit |
Multi packet pointer null. |
8006 h |
|
J1939_ERR_PGNDataLength |
PGN DataLength is over G_J1939_MAX_SIZE_OF_LONG_TRANSFER or size reserved for PGN is smaller than received data size |
8007 h |
|
J1939_ERR_pRxPGNNULL |
pRxPGN pointer null in pointer array |
8008 h |
|
J1939_ERR_pTxPGNNULL |
pTxPGN pointer null in pointer array |
8009 h |
|
J1939_ERR_pSPNDataNULL |
SPN data pointer null. |
800A h |
|
J1939_ERR_SPNUninitialized |
SPN is uninitialized. (size and data pointer are null) |
800B h |
|
J1939_ERR_InvalidCANbusNbr |
CAN bus number out of range. |
800C h |
|
J1939_ERR_InvalidControlByte |
Invalid transport protocol connection management control byte |
800D h |
|
J1939_ERR_MultipacketTimeout |
Timeout in transport protocol. |
800E h |
|
J1939_ERR_NullPointer |
Generic null pointer error. |
800F h |
|
J1939_ERR_RX_ListFull |
Can not add PGN, maximum number of rx PGNs reached. |
8010 h |
|
J1939_ERR_TX_ListFull |
Can not add PGN, maximum number of tx PGNs reached. |
8011 h |
|
J1939_ERR_RQST_ListFull |
Reserved size for request callbacks in G_J1939_MAX_NBR_OF_RQST_CALLBACKS is too low. |
8012 h |
|
J1939_ERR_RQST_NotInUse |
Request PGNs not set to use before adding them. |
8013 h |
|
J1939_ERR_InvalidSPNFMIConversionMethod |
Given invalid SPN/FMI conversion method. |
8014 h |
|
J1939_ERR_DM1LogFull |
DM1 log is full. |
8015 h |
|
J1939_ERR_DM2LogFull |
DM2 log is full. |
8016 h |
|
J1939_ERR_DMLogSizeTooSmall |
DM1 log maximum size is too small. Minimum size is 2 DTCs. |
8017 h |
|
J1939_ERR_DM2LogSavingFailed |
Saving the DM2 log failed. |
8018 h |
|
J1939_ERR_DataOutOfRange |
Data out of specified range. |
8019 h |
|
Name of the Member |
Data Type |
Range |
Description |
|
pBasePGN |
POINTER TO J1939_PGN |
- |
Pointer to received PGN |
|
TotalNumberOfBytes |
BYTE |
2..255 |
Number of bytes in fast transfer. |
|
FrameNumber |
BYTE |
|
Frame number of packet. |
|
SequenceNumber |
BYTE |
|
Sequence number of packet. |
|
DataBuffer |
ARRAY [0..G_J1939_MAX_SIZE_OF_FAST_TRANSFER] OF BYTE |
|
Fast-packet data buffer. |
|
DataBufferIndex |
BYTE |
0..G_J1939_MAX_SIZE_OF_FAST_TRANSFER |
Data buffer index. |
|
Name of the Member |
Data Type |
Range |
Description |
|
pBasePGN |
POINTER TO J1939_PGN |
- |
Pointer to received PGN |
|
TotalNumberOfPackets |
BYTE |
2..255 |
TP: Number of packets in multipacket transfer |
|
MaxNumberOfPackets |
BYTE |
2..255 |
TP: The message originator uses the maximum number of packets to limit the responder CTS request. Used only with destination spesific communication. |
|
SequenceNumber |
BYTE |
1..255 |
TP/ETP: Sequence number of packet |
|
AllowDataTransfer |
BOOL |
TRUE/FALSE |
Data transfer allowed. |
|
DestinationSpecific |
BOOL |
TRUE/FALSE |
Multi packet transfer is destination specific i.e. peer to peer connection |
|
DataMessageSize |
DWORD |
0…117 440 505 |
TP/ETP: Size of data message |
|
NumberOfPacketsOffset |
BYTE |
0…255 |
ETP: Number of packets to apply next data offset |
|
PacketNumForNextCTSMsg |
DWORD |
|
TP/ETP: Packet number when next CTS msg should be send or waited. Used only with destination spesific communication |
|
ExtendedTransfer |
BOOL |
TRUE/FALSE |
If true extended transfer used. Extended transfer protocol is used if data size > G_J1939_MAX_SIZE_OF_LONG_TRANSFER |
|
DataOffset |
DWORD |
|
ETP: Offset for send data |
|
DataPacketNumber |
DWORD |
|
ETP: Next packet number |
|
DataBuffer |
ARRAY [0..J1939_MAX_SIZE_OF_LONG_TRANSFER] OF BYTE |
0 |
Data buffer for receiving |
|
pDataDirect |
DWORD |
Pointer |
Pointer to data if extended transport protocol is used. In this case data is send directly without copying to temp data buffer. |
|
Name of the Member |
Data Type |
Range |
Description |
|
SPN |
DWORD |
0..524287 |
Suspect Parameter Number |
|
FMI |
BYTE |
0..31 |
Failure Mode Identifier |
|
OC |
BYTE |
0..255 |
Occurrence Count |
|
CM |
BOOL |
TRUE / FALSE |
Conversion Method |
J1939_SPN structure defines one SPN. The structure consists of a pointer to the actual variable containing the value, and the size of the value in bits.
|
Name of the Member |
Data Type |
Range |
Description |
|
Size |
DWORD |
0…4294967296 |
Size of the SPN (bits) |
|
pData |
POINTER TO BYTE |
- |
Pointer to data |
Transport protocol connection management enumeration.
Enumeration is also used for ISO 11783-3 extended transport protocol connection management.
|
Name of the Member |
Description |
Value |
|
J1939_TP_CM_RTS |
TP Request to send |
16 |
|
J1939_TP_CM_CTS |
TP Clear to send |
17 |
|
J1939_TP_CM_EOMA |
TP End of message acknowledgement |
19 |
|
J1939_ETP_CM_RTS |
ETP Request to send |
20 |
|
J1939_ETP_CM_CTS |
ETP clear to send |
21 |
|
J1939_ETP_CM_DPO |
ETP packet offset |
22 |
|
J1939_ETP_CM_EOMA |
ETP End of message acknowledgement |
23 |
|
J1939_TP_CM_BAM |
TP Broadcast Announce Message |
32 |
|
J1939_TP_CM_ConnAbort |
Connection aborted |
255 |
|
J1939_TP_DT |
TP Data transfer |
256 |
|
J1939_ETP_DT |
ETP Data transfer |
257 |
Enumeration defines possible errors in data transfer. Used as abort codes in destination specific transport protocol (see J1939-21 or ISO 11783-3:2014).
|
Name of the Member |
Description |
Value |
|
J1939_TRS_ERR_SUCCESS |
Transfer success |
0 |
|
J1939_TRS_ERR_SESSION_ON |
Already in one or more connection-managed sessions AND cannot support another |
1 |
|
J1939_TRS_ERR_NO_SYS_RES |
System resources were needed for another task so this connection managed session was terminated |
2 |
|
J1939_TRS_ERR_TIMEOUT |
A timeout occurred and this is the connection abort to close the session |
3 |
|
J1939_TRS_ERR_WRONG_CTS_MSG |
CTS messages received when data transfer is in progress |
4 |
|
J1939_TRS_ERR_RETRANS_LIMIT_REACHED |
Maximum retransmit request limit reached |
5 |
|
J1939_TRS_ERR_UNEXCP_DATA_PACKET |
Unexpected data transfer packet |
6 |
|
J1939_TRS_ERR_BAD_SEG_NBR |
Bad sequence number and software is not able to recover |
7 |
|
J1939_TRS_ERR_DUP_SEQ_NBR |
Duplicate sequence number and software is not able to recover |
8 |
This is PGN request structure for received EA00 requests. Defines the requested PGN and callback POU pair.
|
Name of the Member |
Data Type |
Range |
Description |
|
PGN |
WORD |
0…65535 |
Requested PGN |
|
CallbackPOU |
WORD |
INDEXOF POU |
POU index which is called when PGN is requested |
|
pPGNData |
DWORD |
Pointer |
Callback parameter: Pointer to PGN structure |
|
pUserData |
DWORD |
Pointer |
Callback parameter: Pointer to user specific data |
Structure defines PGN request callback’s data. Callback data is set when the callback is triggered.
|
Name of the Member |
Data Type |
Range |
Description |
|
SA |
BYTE |
0…255 |
Source address of request |
|
DA |
BYTE |
0…255 |
Destination address for request |
|
pPGNData |
DWORD |
Pointer |
Callback parameter: Pointer to PGN structure |
|
pUserData |
DWORD |
Pointer |
Pointer Callback parameter: Pointer to user specific data |
Received EA00 request callback list.
|
Name of the Member |
Data Type |
Range |
Description |
|
RequestPGN |
ARRAY [1..G_J1939_MAX_NBR_OF_RQST_CALLBACKS] OF J1939_RequestedPGN |
Array |
List of defined PGN request callbacks |
|
NumberOfRequestPGN |
WORD |
0… G_J1939_MAX_NBR_OF_RQST_CALLBACKS |
Amount of currently defined callbacks. |
This structure defines J1939 safety CAN message buffer.
|
|
The buffer size minimum is 2 messages. |
|
|
The message buffer is only used with J1939-76 messages together with CODESYS 3.5 SP19 specific S_J1939 safety FB. |
|
Name of the Member |
Data Type |
Range |
Description |
| pMsg | POINTER TO EPEC_CANVXD.Msg | Pointer | Pointer to CAN message table |
| SizeOfBuffer | USINT | > 1 | Size of message table |
| ReadIndex | USINT | 0..SizeOfBuffer-1 | Next index to read from buffer |
| WriteIndex | USINT | 0..SizeOfBuffer-1 | Next index to write to buffer |
| RejectMessage | BOOL | TRUE / FALSE | Reject SDM's before first SHM |
| Received | BOOL | TRUE / FALSE | Message received |
Source file Topic000441.htm
Last updated 26-Aug-2026