Supported platforms: CODESYS 2.3, CODESYS 3.5
JCD_AutoCalib function block can be used for calibration of the joystick or pedal.
In the calibration mode, it measures the value of i_AISignal, converts it to the voltage value with the ADC_To_mAOrV function, and stores the maximum and minimum values of the measured signal (meanwhile the user moves the joystick or pedal to both end positions). Mid position value of the joystick is stored when the calibration mode is deactivated. The joystick should be centered when the calibration mode is deactivated.
o_TrigSave output is activated for one program cycle, when the calibration mode is deactivated (at falling edge). This output can be used to trigger an additional parameter saving function if necessary (for example if parameters are stored to FLASH memory).
Current calibration parameter values are given to the FB as inputs and the FB's output calibration values are assigned to those same variables. When the calibration mode is not active, input calibration values are directly assigned to output calibration values, therefore calibration values only change during calibration mode.
With G_JCType.Percentage type given to i_ParameterType, max, mid and min calibration values are percentage (1000 = 100,0%) of measured
joystick supply voltage.
The calibration type changes internally only on rising edge of i_CalibrationMode.
|
Calibration has 2 operation modes: - Voltage mode: Input parameters are given in volts and joystick supply voltage is not compensated. - Percentage mode: Input parameters are given in percentage of joystick supply voltage. Due to that, changes in joystick supply voltage are compensated. |
|
In voltage mode ( i_ParameterType = G_JCType.Voltage), both output and input calibration parameters are handled as volts (1000 = 10,00V). In percentage mode ( i_ParameterType = G_JCType.Percentage), both output and input calibration parameters are handled as proportion (1000 = 100,0%) of joystick supply voltage. |
|
Joystick and pedal must be connected to voltage input. |
|
When i_ParameterType = G_JCType.Voltage and voltage values are used for joystick calibration, there is a reference voltage monitoring feature built in to detect drop of reference voltage level. In such case, o_Control signal output is reset and can be used again after rising edge of i_Enable. This monitoring feature can however detect only sudden drop of ref voltage level. |
|
It is highly recommended to set i_ParameterType to G_JCType.Percentage and to use percentage values for joystick calibration. This ensures that unexpected dropping of reference voltage level doesn’t cause o_ControlSignal output changing and unwanted response in controlled actuator. |
Input variable name |
Data type |
Range |
Description |
i_CalibrationMode |
BOOL |
FALSE/TRUE |
AI signal is monitored and calibration is done when value is true |
i_AISignal |
UINT |
Hardware specific |
Analog input signal |
i_AIType |
BYTE |
0..G_ADScaleArrMax |
Defines the Analog input type and range |
i_AISupply |
UINT |
Hardware specific |
Joystick supply voltage measurement |
i_AISupplyType |
BYTE |
0..G_ADScaleArrMax |
Joystick supply type and range. |
i_ParameterType |
ENUM |
G_JCType.Voltage, G_JCType.Percentage |
Calibration parameter type Voltage/Percentage |
i_MaxValue |
UINT |
Hardware and calibration type specific |
Maximum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
i_MidValue |
UINT |
Hardware and calibration type specific |
Middle calibration value of joystick or minimum value of pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
i_MinValue |
UINT |
Hardware and calibration type specific |
Minimum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
Input variable name |
Data type |
Range |
Description |
i_CalibrationMode |
BOOL |
FALSE/TRUE |
AI signal is monitored and calibration is done when value is true |
i_AISignal |
UINT |
Hardware specific |
Analog input signal |
i_AIType |
ADData |
G_AIType struct
|
Defines the Analog input type and range |
i_AISupply |
UINT |
Hardware specific |
Joystick supply voltage measurement |
i_AISupplyType |
ADData |
G_AIType struct |
Joystick supply type and range. |
i_ParameterType |
ENUM |
G_JCType.Voltage, G_JCType.Percentage |
Calibration parameter type Voltage/Percentage |
i_MaxValue |
UINT |
Hardware and calibration type specific |
Maximum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
i_MidValue |
UINT |
Hardware and calibration type specific |
Middle calibration value of joystick or minimum value of pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
i_MinValue |
UINT |
Hardware and calibration type specific |
Minimum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
Output variable name |
Data type |
Range |
Description |
o_TrigSave |
BOOL |
FALSE/TRUE |
True for one cycle after calibration end, can be used trigger parameter saving |
o_MaxValue |
UINT |
Hardware and calibration type specific |
Maximum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
o_MidValue |
UINT |
Hardware and calibration type specific |
Middle calibration value of joystick or minimum value of pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |
o_MinValue |
UINT |
Hardware and calibration type specific |
Minimum calibration value of joystick or pedal. Value is given in voltage (500 = 5,00V) or percentage (1000 = 100,0%). |

![]()

NOTE! Example's StoreJoystickCalibrationToFlash is not implemented in the library.