JCD_Scale (FUN)

Description

JCD_Scale function is used for scaling the analog input ADC value to the control signal within a range of  0..32767 based on calibration values and dead band value given as input.

 

The ControlSignal output is zero until the AI signal level exceeds the deadband voltage limit, which is calculated with the following algorithm:

 

Deadband voltage limit = (i_VoltageForMaxControl - i_VoltageForMinControl) * i_Deadband / 100 + i_VoltageForMinControl

 

Between the calculated deadband voltage limit and i_VoltageForMaxControl, o_ControlSignal increases linearly according to i_AISignal. o_ControlSignal is limited to 32767 if i_AISignal exceeds i_VoltageForMaxControl value.

i_VoltageForMaxControl and i_VoltageForMinControl values are converted to ADC values using the  ADC_From_mAOrV function.

 

 

Example control value curves with i_VoltageForMinControl of 2,5V. Higher i_VoltageForMaxControl gives positive slope, and vice versa gives negative.

Limitations

This function block is primarily intended for JoystickCalibrationAndDiagnostic library's internal use.

Inputs

CODESYS 2.3CODESYS 2.3

Input variable name

Data type

Range

Description

i_AISignal

UINT

hardware specific

Analog input signal

i_AIType

BYTE

0..G_ADScaleArrMax

Analog input type and range

i_CalibratedMax

UINT

hardware specific

Max calibration voltage value, value given in voltage with two decimals, range depend of used hardware type, with this value function return max control signal value (32767)

i_CalibratedMin

UINT

hardware specific

Min calibration voltage value, value given in voltage with two decimals, range depend of used hardware type, with this value function return min control signal value (0)

i_Deadband

BYTE

0..100%

Defines the dead band, value given in percentage of max-min range.  

 

 

CODESYS 3.5CODESYS 3.5

Input variable name

Data type

Range

Description

i_AISignal

UINT

hardware specific

Analog input signal

i_AIType

ADData

G_AIType struct

Analog input type and range

i_CalibratedMax

UINT

hardware specific

Max calibration voltage value, value given in voltage with two decimals, range depend of used hardware type, with this value function return max control signal value (32767)

i_CalibratedMin

UINT

hardware specific

Min calibration voltage value, value given in voltage with two decimals, range depend of used hardware type, with this value function return min control signal value (0)

i_Deadband

BYTE

0..100%

Defines the dead band, value given in percentage of max-min range.  

 

 

Return value

Return value

Data type

Range

Description

 

INT

0...32767

Calibrated control signal value

 

See also

 