Supported platforms: CODESYS 2.3, CODESYS 3.5

 

SCD_KTYSensor (FB)

Description

SCD_KTYSensor FB scales the ADC value to temperature (°C). This function block uses a built-in calibration base curve (in SCD_SetKTYScale (FB))  for KTY sensors which can be adjusted with two input variables.

 

KTY sensor type can be selected with i_ResAt25degC input. This input defines the sensor’s typical resistance in 25°C temperature and shifts the calibration curve accordingly. (The typical resistance in 25°C is told in the sensor’s data sheet).

 

However, there are some differences in individual sensors and therefore it might be necessary to fine tune the calibration curve for better accuracy. For that purpose there is i_CalibrationOffset input. i_CalibrationOffset shifts the calibration curve, keeping the curve shape. Shift amount is given in Ohms at 25°C. The ideal value for calibration offset is normally found only by testing.

 

Reference voltage level (V)

Connection type

CalibrationOffset (Ohm@25°C)

+10V

Voltage input (type 2)

30

+5V

Voltage input (type 2)

5

+10V

Current input (type 1)

out of spec

+5V

Current input (type 1)

70

Example values for Infineon KTY sensor (1000Ohm@25°C).

 

 

The FB also calculates the sensor’s resistance for diagnostics.

 

The sensor’s nominal calibration curve is only valid with a certain supply current, therefore the curve may also need fine tuning because of differences in supply current in different type of connections. Also, the reference voltage (sensor supply voltage) level affects the calibration offset. (Supply current is much bigger when using current input i.e. 220ohm pull-down resistor.)

 

 

Sensor connected to voltage input (type 2) with internal pull-up resistor.  

 

 

 

Sensor connected to current input (type 1) with internal pull-down resistor.

 

Limitations

This function block can be used only with KTY temperature sensors.

 

This sensor type will work only when connected either to voltage input with 2k2ohm pull-up resistor, (or to current input with 220ohm pull-down resistor).

 

This function block can be used only for measuring temperatures between -50°C and 150°C because of fixed base curve calibration points. Degrees of Celsius is used in calculation, therefore the return value is always °C.

 

Preferred connection type for KTY sensor is  voltage input (type 2) with internal pull-up resistor.

 

When i_Enable changes to FALSE, outputs stay unchanged until i_Enable changes back to TRUE.

 

Output resistance and temperature are always calculated, despite of diagnosed value errors and warnings.

 

Inputs

CODESYS 2.3CODESYS 2.3

Input variable name

Data type

Range

Description

i_Enable

BOOL

TRUE/FALSE

Enables calculation of outputs

i_SensorAIValue

WORD

hardware specific

AD converter value from sensor

i_SensorAIType

BYTE

0..G_ADScaleArrMax

Defines the AI type (mA or V) and range

i_ResAt25degC

INT

0..5000 Ohm

Sensor’s typical resistance in Ohm value at 25°C

i_CalibrationOffset

INT

-200..200 Ohm

Resistance offset value in Ohm at 25°C for fine tuning calibration curve.

i_SensorValueErrorLimitHigh

WORD

0..5000 Ohm

High error limit for sensor resistance value in Ohms

i_SensorValueErrorLimitLow

WORD

0..5000 Ohm

Low error limit for sensor resistance value in Ohms

i_CalibratedValueAlarmLimitHigh

INT

-50..150°C

High alarm limit for temperature output value in °C

i_CalibratedValueWarningLimitHigh

INT

-50..150°C

High warning limit for temperature output value in °C

i_CalibratedValueWarningLimitLow

INT

-50..150°C

Low warning limit for temperature output value in °C

i_CalibratedValueAlarmLimitLow

INT

-50..150°C

Low alarm limit for temperature output value in °C

i_ReferenceAIValue

WORD

hardware specific

AD converter value of the reference voltage that is used to supply the sensor.

i_ReferenceAIType

BYTE

0..G_ADScaleArrMax

 

Defines the AI range of reference measurement

i_EnableCalibratedValueOutput

BOOL

TRUE/FALSE

Enables temperature calculation, when false temperature output value is 0°C.

i_EnableSensorValueErrors

BOOL

TRUE/FALSE

Enables sensor resistance value diagnostics

i_EnableCalibratedValueHighAlarm

BOOL

TRUE/FALSE

Enables temperature high alarm

i_EnableCalibratedValueHighWarning

BOOL

TRUE/FALSE

Enables temperature high warning

i_EnableCalibratedValueLowWarning

BOOL

TRUE/FALSE

Enables temperature low warning

i_EnableCalibratedValueLowAlarm

BOOL

TRUE/FALSE

Enables temperature low alarm

i_ErrorDelay

UINT

0..65535 ms

Error delay in milliseconds

 

 

CODESYS 3.5CODESYS 3.5

Input variable name

Data type

Range

Description

i_Enable

BOOL

TRUE/FALSE

Enables calculation of outputs

i_SensorAIValue

WORD

hardware specific

AD converter value from sensor

i_SensorAIType

ADData

G_AIType struct

Defines the AI type (mA or V) and range

i_ResAt25degC

INT

0..5000 Ohm

Sensor’s typical resistance in Ohm value at 25°C

i_CalibrationOffset

INT

-200..200 Ohm

Resistance offset value in Ohm at 25°C for fine tuning calibration curve.

i_SensorValueErrorLimitHigh

WORD

0..5000 Ohm

High error limit for sensor resistance value in Ohms

i_SensorValueErrorLimitLow

WORD

0..5000 Ohm

Low error limit for sensor resistance value in Ohms

i_CalibratedValueAlarmLimitHigh

INT

-50..150°C

High alarm limit for temperature output value in °C

i_CalibratedValueWarningLimitHigh

INT

-50..150°C

High warning limit for temperature output value in °C

i_CalibratedValueWarningLimitLow

INT

-50..150°C

Low warning limit for temperature output value in °C

i_CalibratedValueAlarmLimitLow

INT

-50..150°C

Low alarm limit for temperature output value in °C

i_ReferenceAIValue

WORD

hardware specific

AD converter value of the reference voltage that is used to supply the sensor.

i_ReferenceAIType

ADData

G_AIType struct

 

Defines the AI range of reference measurement

i_EnableCalibratedValueOutput

BOOL

TRUE/FALSE

Enables temperature calculation, when false temperature output value is 0°C.

i_EnableSensorValueErrors

BOOL

TRUE/FALSE

Enables sensor resistance value diagnostics

i_EnableCalibratedValueHighAlarm

BOOL

TRUE/FALSE

Enables temperature high alarm

i_EnableCalibratedValueHighWarning

BOOL

TRUE/FALSE

Enables temperature high warning

i_EnableCalibratedValueLowWarning

BOOL

TRUE/FALSE

Enables temperature low warning

i_EnableCalibratedValueLowAlarm

BOOL

TRUE/FALSE

Enables temperature low alarm

i_ErrorDelay

UINT

0..65535 ms

Error delay in milliseconds

 

 

Outputs

CODESYS 2.3CODESYS 2.3

Output variable name

Data type

Range

Description

o_SensorValue

INT

0..5000 Ohm

Sensor resistance value in Ohm, calculated from sensor ADC value.

o_CalibratedValue

INT

-50..150°C

Temperature value based on calibration

o_ParameterError

BOOL

TRUE/FALSE

Always FALSE. Included in the block for compatibility reasons

o_SensorValueErrorHigh

BOOL

TRUE/FALSE

Sensor value too high

o_SensorValueErrorLow

BOOL

TRUE/FALSE

Sensor value too low

o_CalibratedValueHighAlarm

BOOL

TRUE/FALSE

Temperature over the high alarm limit

o_CalibratedValueHighWarning

BOOL

TRUE/FALSE

Temperature over the high warning limit

o_CalibratedValueLowWarning

BOOL

TRUE/FALSE

Temperature below the low warning limit

o_CalibratedValueLowAlarm

BOOL

TRUE/FALSE

Temperature below the low alarm limit

 

 

CODESYS 3.5CODESYS 3.5

Output variable name

Data type

Range

Description

o_SensorValue

INT

0..5000 Ohm

Sensor resistance value in Ohm, calculated from sensor ADC value.

o_CalibratedValue

INT

-50..150°C

Temperature value based on calibration

o_SensorValueErrorHigh

BOOL

TRUE/FALSE

Sensor value too high

o_SensorValueErrorLow

BOOL

TRUE/FALSE

Sensor value too low

o_CalibratedValueHighAlarm

BOOL

TRUE/FALSE

Temperature over the high alarm limit

o_CalibratedValueHighWarning

BOOL

TRUE/FALSE

Temperature over the high warning limit

o_CalibratedValueLowWarning

BOOL

TRUE/FALSE

Temperature below the low warning limit

o_CalibratedValueLowAlarm

BOOL

TRUE/FALSE

Temperature below the low alarm limit

 

Example code

See also

 

Source file Topic000251.htm

Last updated 26-Aug-2026