Supported platforms: CODESYS 2.3
This function block monitors voltages, temperatures and the program cycle time of the control unit. All the voltages and temperatures have high and low limits, both signaled with a boolean output when exceeded. Each measurement limit has it's own parameter. Only the high limit of the program cycle time can be set and monitored.
|
The low and high limit parameters for supply voltage must be set within the specified voltage range of the control unit.
|
Input variable name |
Data type |
Range |
Description |
i_SupplyVoltage1 |
UINT |
|
Supply voltage 1 measured value. |
i_SupplyVoltage2 |
UINT |
|
Supply voltage 2 measured value. |
i_SupplyVoltage3 |
UINT |
|
Supply voltage 3 measured value. |
i_Ref5V |
UINT |
|
Reference 5V measured value. |
i_Ref10V |
UINT |
|
Reference 10V measured value. |
i_PullUp10V |
UINT |
|
Pull-up 10V measured value. |
i_RefADC |
UINT |
|
ADC reference measured value. |
i_Temperature1 |
UINT |
|
Temperature 1 measured value. |
i_Temperature2 |
UINT |
|
Temperature 2 measured value. |
i_SupplyVoltageHighLimit |
UINT |
|
High limit of supply voltage. 100 = 1.00 volts. |
i_SupplyVoltageLowLimit |
UINT |
|
Low limit of supply voltage. 100 = 1.00 volts. |
i_Ref5VHighLimit |
UINT |
|
High limit of 5V reference voltage. 100 = 1.00 volts. |
i_Ref5VLowLimit |
UINT |
|
Low limit of 5V reference voltage. 100 = 1.00 volts. |
i_Ref10VHighLimit |
UINT |
|
High limit of 10V reference voltage. 100 = 1.00 volts. |
i_Ref10VLowLimit |
UINT |
|
Low limit of 10V reference voltage. 100 = 1.00 volts. |
i_PullUp10VHighLimit |
UINT |
|
High limit of 10V pull-up voltage. 100 = 1.00 volts. |
i_PullUp10VLowLimit |
UINT |
|
Low limit of 10V pull-up voltage. 100 = 1.00 volts. |
i_RefADCVHighLimit |
UINT |
|
High limit of ADC reference voltage. 100 = 1.00 volts. |
i_RefADCVLowLimit |
UINT |
|
Low limit of ADC reference voltage. 100 = 1.00 volts. |
i_TempHighLimit |
INT |
|
High limit of temperature 1. 10 = 1 °C. |
i_TempLowLimit |
INT |
|
Low limit of temperature 1. 10 = 1 °C. |
i_CycleTimeHighLimit |
UINT |
|
High limit of application cycle time in milliseconds. |
Output variable name |
Data type |
Range |
Description |
o_SupplyVoltage1 |
UINT |
|
Scaled value of module supply voltage. 100 = 1.00 volts.. |
o_SupplyVoltage2 |
UINT |
|
Scaled value of module power 1 voltage. 100 = 1.00 volts.. |
o_SupplyVoltage3 |
UINT |
|
Scaled value of module power 2 voltage. 100 = 1.00 volts.. |
o_Ref5V |
UINT |
|
Scaled value of 5 volt reference voltage. 100 = 1.00 volts. |
o_Ref10V |
UINT |
|
Scaled value of 10 volt reference voltage. 100 = 1.00 volts. |
o_Temperature1 |
INT |
|
Calculated value of temperature 1. 10 = 1 °C |
o_Temperature2 |
INT |
|
Calculated value of temperature 2. 10 = 1 °C |
o_CycleTime |
UINT |
|
Latest application cycle time in milliseconds |
o_CycleTimeAverage |
UINT |
|
Average application cycle time in milliseconds. |
o_SupplyVoltage1High |
BOOL |
|
TRUE if supply voltage is higher than limit |
o_SupplyVoltage1Low |
BOOL |
|
TRUE if supply voltage is lower than limit |
o_SupplyVoltage2High |
BOOL |
|
TRUE if supply voltage is higher than limit |
o_SupplyVoltage2Low |
BOOL |
|
TRUE if supply voltage is lower than limit |
o_SupplyVoltage3High |
BOOL |
|
TRUE if supply voltage is higher than limit |
o_SupplyVoltage3Low |
BOOL |
|
TRUE if supply voltage is lower than limit |
o_Ref5VHigh |
BOOL |
|
TRUE if 5V reference voltage is higher than limit |
o_Ref5VLow |
BOOL |
|
TRUE if 5V reference voltage is lower than limit |
o_Ref10VHigh |
BOOL |
|
TRUE if 10V reference voltage is higher than limit |
o_Ref10VLow |
BOOL |
|
TRUE if 10V reference voltage is lower than limit |
o_PullUp10VHigh |
BOOL |
|
TRUE if 10V pull-up voltage is higher than limit |
o_PullUp10VLow |
BOOL |
|
TRUE if 10V pull-up voltage is lower than limit |
o_RefADCVHigh |
BOOL |
|
TRUE if ADC reference voltage is higher than limit |
o_RefADCVLow |
BOOL |
|
TRUE if ADC reference voltage is lower than limit |
o_Temperature1High |
BOOL |
|
TRUE if temperature 1 is higher than limit |
o_Temperature1Low |
BOOL |
|
TRUE if temperature 1 is lower than limit |
o_Temperature2High |
BOOL |
|
TRUE if temperature 2 is higher than limit |
o_Temperature2Low |
BOOL |
|
TRUE if temperature 2 is lower than limit |
o_CycleTimeHigh |
BOOL |
|
TRUE if application cycle time is higher than limit |

This example is from Epec 5050 control unit. Measured analog inputs may vary in different hardware.
-