Supported platforms: CODESYS 2.3, CODESYS 3.5
Data Types CODESYS 2.3Data Types CODESYS 2.3
Name of the Member |
Data Type |
Default value |
Description |
NodeID |
BYTE |
1 |
Node ID of device to monitor/manage. |
KeepAlive |
BOOL |
TRUE |
When set, the node is started when it enters pre-operational state. |
Reset |
BOOL |
TRUE |
When set, the node is reset when it is missing from CAN bus. |
Mandatory |
BOOL |
TRUE |
When set, the node state affects o_BusOk output of NetworkManager FB. |
ConsumerTime |
UINT |
600 |
Maximum heartbeat interval before node is considered missing. |
State |
SINT |
-1 |
Current state of the node. -1 means node is missing, others are NMT states. |
TimeSinceLastHeartbeat |
UINT |
0 |
Number of milliseconds since last heartbeat message from the node. |
SlaveConfiguration |
POINTER TO NM_ConfigureSlave |
|
Pointer to function block instance to configure slave OD, TPDOs and RPDOs |
Name of the Member |
Data Type |
Default value |
Description |
Index |
WORD |
0 |
OD index |
SubIndex |
BYTE |
0 |
OD subindex |
NewValue |
DWORD |
0 |
Value to be written to the index/subindex, or pointer to the value, if larger than 4 bytes |
Size |
BYTE |
0 |
Size of the value to write (number of bytes) . |
State |
BYTE |
0 |
State of the index/subindex: 0 = Not written, 1 = Written, 2 = Fault |
Name of the Member |
Data Type |
Default value |
Description |
COBID |
DWORD |
0 |
COBID of the PDO |
TransmissionType |
BYTE |
0 |
Transmission type of the PDO |
InhibitTime |
WORD |
0 |
Inhibit time of the PDO |
EventTime |
WORD |
0 |
Event time of the PDO |
State |
BYTE |
0 |
State of the PDO configuration: 0 = Not written, 1 = Written, 2 = Fault |
ConfigureInhibitTime |
BOOL |
TRUE |
TRUE = TPDO inhibit time is configured. FALSE = TPDO inhibit time is not configured. |
ConfigureEventTime |
BOOL |
TRUE |
TRUE = TPDO event time is configured. FALSE = TPDO event time is not configured. |
ConfigureMappings |
BOOL |
TRUE |
If TRUE PDO mappings are configured to slave unit |
PDONumber |
WORD |
1..512 |
Communication and mapping indexes are determined by PDO number |
Data Types CODESYS 3.5Data Types CODESYS 3.5
Name of the Member |
Data Type |
Default value |
Description |
NodeID |
BYTE |
1 |
Node ID of device to monitor/manage. |
KeepAlive |
BOOL |
TRUE |
When set, the node is started when it enters pre-operational state. |
Reset |
BOOL |
TRUE |
When set, the node is reset when it is missing from CAN bus. |
Mandatory |
BOOL |
TRUE |
When set, the node state affects o_BusOk output of NetworkManager FB. |
ConsumerTime |
UINT |
600 |
Maximum heartbeat interval before node is considered missing. |
State |
SINT |
-1 |
Current state of the node. -1 means node is missing, others are NMT states. |
TimeSinceLastHeartbeat |
UINT |
0 |
Number of milliseconds since last heartbeat message from the node. |
SlaveConfiguration |
POINTER TO NM_ConfigureSlave |
|
Pointer to function block instance to configure slave OD, TPDOs and RPDOs |
Name of the Member |
Data Type |
Default value |
Description |
NewValue |
DWORD |
|
Value to be written to the index/subindex; Used when size of value is 4 bytes or less. |
pNewValue |
POINTER TO ANY |
|
Pointer to the value, if larger than 4 bytes. |
Name of the Member |
Data Type |
Default value |
Description |
Index |
WORD |
0 |
OD index |
SubIndex |
BYTE |
0 |
OD subindex |
NewValue |
NM_SDOArg |
0 |
Value to be written to the index/subindex, or pointer to the value, if larger than 4 bytes |
Size |
BYTE |
0 |
Size of the value to write (number of bytes) . |
State |
BYTE |
0 |
State of the index/subindex: 0 = Not written, 1 = Written, 2 = Fault |
Name of the Member |
Data Type |
Default value |
Description |
COBID |
DWORD |
0 |
COBID of the PDO |
TransmissionType |
BYTE |
0 |
Transmission type of the PDO |
InhibitTime |
WORD |
0 |
Inhibit time of the PDO |
EventTime |
WORD |
0 |
Event time of the PDO |
State |
BYTE |
0 |
State of the PDO configuration: 0 = Not written, 1 = Written, 2 = Fault |
ConfigureInhibitTime |
BOOL |
TRUE |
TRUE = TPDO inhibit time is configured. FALSE = TPDO inhibit time is not configured. |
ConfigureEventTime |
BOOL |
TRUE |
TRUE = TPDO event time is configured. FALSE = TPDO event time is not configured. |
ConfigureMappings |
BOOL |
TRUE |
If TRUE PDO mappings are configured to slave unit |
PDONumber |
WORD |
1..512 |
Communication and mapping indexes are determined by PDO number |
Name of the Member |
Data Type |
Default value |
Description |
G_NM_ST_BOOTUP |
BYTE |
0 |
Node state is bootup. |
G_NM_ST_STOPPED |
BYTE |
4 |
Node state is stopped. |
G_NM_ST_OPERATIONAL |
BYTE |
5 |
Node state is operational. |
G_NM_ST_PREOPERATIONAL |
BYTE |
127 |
Node state is preoperational. |
G_NM_CMD_START |
BYTE |
1 |
NMT command start node. |
G_NM_CMD_STOP |
BYTE |
2 |
NMT command stop node. |
G_NM_CMD_ENTERPREOPERATIONAL |
BYTE |
128 |
NMT command enter to preoperational. |
G_NM_CMD_RESET |
BYTE |
129 |
NMT command rese node. |
G_NM_CMD_RESETCOMMUNICATION |
BYTE |
130 |
NMT command reset communication. |
G_NM_SlaveConfigForceTimeDelay |
DWORD |
200 |
Delay (ms) of forced slave configuration when slave is not preoperational. |
G_NM_SlaveConfigFast |
BOOL |
FALSE |
When TRUE, two configurations are made in one program cycle. Otherwise only one configuration per program cycle. |
G_NM_SlaveConfigRestartDelay |
DWORD |
50 |
Inhibit time of slave re-configuration (ms). |
Name of the Member |
Data Type |
Default value |
Description |
G_NM_Counter |
WORD |
0 |
Number of configurations done. |
Source file Topic000236.htm